Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss how to set bypass (the old, red gate valve type) in the Plumbing Jobs | The Job-board area at Plumbers Forums

Jennie

Gas Engineer
Messages
283
Hi all,
My customer has a gatevalve/bypass off the primary flow into his cylinder.
He has fiddled with it (I think he was trying to turn off the water, and got the wrong valve).
How best to set it up?
I'll have to check to see if the system is on a three-port or two-port valves (if it's relevant).
Thanks all,
Jennie
IMG_0271.JPG
 
Hi Jennie,
This is an ‘old school’ method of regulating the
flow of water through the cylinder heat exchanger
(Coil) although usually fitted on primary return.
The idea is by reducing the flow, the coil will remain hotter longer. Thus heating the water quicker.
Nothing to do with modern pressure differential by-passes.
So the answer you seek, is by trial and error.
Crank it about two full turns from fully open and see how it goes.
 
Hi Jennie,
This is an ‘old school’ method of regulating the
flow of water through the cylinder heat exchanger
(Coil) although usually fitted on primary return.
The idea is by reducing the flow, the coil will remain hotter longer. Thus heating the water quicker.
Nothing to do with modern pressure differential by-passes.
So the answer you seek, is by trial and error.
Crank it about two full turns from fully open and see how it goes.
Given the position of the gate valve it's clearly acting as a bypass and in no way will affect the flow rate of water through the cylinder coil. I'd agree with Riley with fitting an auto bypass but would first check whether it's actually required. If the system is on a 3 way valve then I would just remove it.
 
In the photo, you can’t make out where it’s teed from.
I assumed it was directly from either a zone or mid-position valve. However, after reading your reply Craig and looking at the photo again.
I now feel you are right and I’m mistaken
It does look too low down to be the flow??
 
Yeah the photo looks to me like it's at the base of the cylinder and the gate valve is is tee'd into the top of the cylinder return pipe
 
Hi all,

Thanks so much for your comments. I'll have to go back and check out the surrounding pipework/zone valves/etc.

I'm a bit confused about the three-way valve versus the two zone valves. Surely both shut water off to the hot water and central heating circuits. So why isn't a bypass needed on the three way valve?
 
Hi all,

Thanks so much for your comments. I'll have to go back and check out the surrounding pipework/zone valves/etc.

I'm a bit confused about the three-way valve versus the two zone valves. Surely both shut water off to the hot water and central heating circuits. So why isn't a bypass needed on the three way valve?
A 3 port valve always keeps a circuit open so a bypass isn't required
 

Similar plumbing topics

Yes - the recommendation above is accurate for...
Replies
3
Views
2K
I should have said "S-plan plus", of course!