Hi all,
I have a Wallstar Oil Boiler 12/15.
A few years ago, it developed a problem where it would fail and it required a manual reset on the boiler controller outside.
I didn't know much about oil boilers back then.
I have had a number of 'heating engineers' and so-called specialists to it but so far none have cured the problem.
I decided to figure out how these things work for myself to give me a greater understanding of what is going wrong.
So, this is what happens.
When there is demand for heat, the boiler from cold (in a none failed condition) fires up without the slightest problem.
It runs to get the water hot, shuts off, starts again as water cools etc... normal running.
Then, for no apparent reason, say after 30 mins or 1-hour etc, it will fail to ignite. This triggers the fail and requires a reset on the controller.
Sometimes the reset will work and the boiler will fire up and continue, sometimes it will just keep failing.
If I leave it to cool down for a few hours, it will generally fire up as normal (after clearing the fail with the reset).
It seems that when the boiler is very cold, there is no problem. If it is also very hot, it doesn't seem to be a problem, but in-between is where it fails.
The engineers etc have changed the nozzle, plastic pipe, solenoid, controller and filters and the problem persists.
Now then, things I have checked.
When starting, the pump runs (pulsing of the oil can be seen in the clear pipe). It does its 10-15 second purge then the solenoid clicks and the oil flows, boiler lights.
All good.
When it fails, it NEVER fails when running, only on re-starting during the normal heating cycle.
It goes through the normal procedure as above, solenoid clicks open, oil is seen to flow and then within about 3 seconds it shuts off with the fault.
Now, as I can see the oil moving, it isn't the solenoid, it’s not air as I can see the oil in the line, it’s not a blockage as again I can see the oil moving in the line.
It seems to be the igniter.
I have had it apart, cleaned the electrodes, checked the gap 3mm+-0.5mm and level with the top of the nozzle.
It's not the flame detector because when it fires up, you can hear it ignite and it doesn't get that far.
Does anyone have any experience with this same fault and how was it cured?
Could it be the transformer (that creates the spark), the leads to the electrodes or the electrodes themselves.
Puzzling as it only fails when the boiler has been running. The temperature in the burner cabinet is always quite cool, but the fault is definitely heat related!
This must be a known problem, on my street 12 houses, we all have the same boiler and 7 of them have the exact same problem.
Surely someone must know what the problem is.
Oh, the boiler is about 12 years old.
Thanks.
Martin
I have a Wallstar Oil Boiler 12/15.
A few years ago, it developed a problem where it would fail and it required a manual reset on the boiler controller outside.
I didn't know much about oil boilers back then.
I have had a number of 'heating engineers' and so-called specialists to it but so far none have cured the problem.
I decided to figure out how these things work for myself to give me a greater understanding of what is going wrong.
So, this is what happens.
When there is demand for heat, the boiler from cold (in a none failed condition) fires up without the slightest problem.
It runs to get the water hot, shuts off, starts again as water cools etc... normal running.
Then, for no apparent reason, say after 30 mins or 1-hour etc, it will fail to ignite. This triggers the fail and requires a reset on the controller.
Sometimes the reset will work and the boiler will fire up and continue, sometimes it will just keep failing.
If I leave it to cool down for a few hours, it will generally fire up as normal (after clearing the fail with the reset).
It seems that when the boiler is very cold, there is no problem. If it is also very hot, it doesn't seem to be a problem, but in-between is where it fails.
The engineers etc have changed the nozzle, plastic pipe, solenoid, controller and filters and the problem persists.
Now then, things I have checked.
When starting, the pump runs (pulsing of the oil can be seen in the clear pipe). It does its 10-15 second purge then the solenoid clicks and the oil flows, boiler lights.
All good.
When it fails, it NEVER fails when running, only on re-starting during the normal heating cycle.
It goes through the normal procedure as above, solenoid clicks open, oil is seen to flow and then within about 3 seconds it shuts off with the fault.
Now, as I can see the oil moving, it isn't the solenoid, it’s not air as I can see the oil in the line, it’s not a blockage as again I can see the oil moving in the line.
It seems to be the igniter.
I have had it apart, cleaned the electrodes, checked the gap 3mm+-0.5mm and level with the top of the nozzle.
It's not the flame detector because when it fires up, you can hear it ignite and it doesn't get that far.
Does anyone have any experience with this same fault and how was it cured?
Could it be the transformer (that creates the spark), the leads to the electrodes or the electrodes themselves.
Puzzling as it only fails when the boiler has been running. The temperature in the burner cabinet is always quite cool, but the fault is definitely heat related!
This must be a known problem, on my street 12 houses, we all have the same boiler and 7 of them have the exact same problem.
Surely someone must know what the problem is.
Oh, the boiler is about 12 years old.
Thanks.
Martin