HRM Wallstar Oil Boiler - Advice please | Boilers | Page 3 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss HRM Wallstar Oil Boiler - Advice please in the Boilers area at Plumbers Forums

Fool the photocell into seeing light once burner fires and see if burner continues to fire while photocell out. Handy on Sterling burners.
That will prove flame is poor for some reason or photocell had obstructed view.
Does sound like flame burn is barely making it
 
Fool the photocell into seeing light once burner fires and see if burner continues to fire while photocell out. Handy on Sterling burners.
That will prove flame is poor for some reason or photocell had obstructed view.
Does sound like flame burn is barely making it
Boiler started up 1st attempt this morning.......

I did try this awhile ago. I think when I removed photocell burner continued running but when I covered photocell it shutdown if my memory serves me correctly.
[automerge]1580746973[/automerge]
Took burner unit off and had a look. I’ve attached photos. Tip of nozzle is damp with oil.
Any suggestions?
 

Attachments

  • 8365299F-E148-4661-B898-EDBFE74587C6.jpeg
    8365299F-E148-4661-B898-EDBFE74587C6.jpeg
    85.7 KB · Views: 42
  • 26955CB1-FDE4-4290-8B4B-A3ACEBE49685.jpeg
    26955CB1-FDE4-4290-8B4B-A3ACEBE49685.jpeg
    121.1 KB · Views: 42
Last edited:
Boiler started up 1st attempt this morning...

I did try this awhile ago. I think when I removed photocell burner continued running but when I covered photocell it shutdown if my memory serves me correctly.

Combustion is most likely then poor if flame isn’t partly being obscured from photocell view.
But can have one of many causes.
Nozzle could be faulty, or air setting wrong or burner drawing in flue gases, or oil pump pressure is set wrong, are some possibilities.
 
Nozzle being damp is fine. Dont like the position of the electrodes though.
Just a quick question, the capscrew that is in the main body of the burner just below the black plastic cover for the photo cell etc is that what is undone when boiler serviced? If so should the gasket be replaced?
[automerge]1580748488[/automerge]
could the electrode be causing the issue of lockout? If it’s not positioned correctly could the photocell fail to detect it sometimes?

is the blast tube ok or should that be cleaner?
 
The Alan key under the black cover is used to undo and remove the burner, you've detached the whole thing. The electrodes don't look right in terms of position and could be part of the reason it doesn't light sometimes, it doesn't explain why it sometimes ignites and then loses flame during 5 second safety time though.
 
The Alan key under the black cover is used to undo and remove the burner, you've detached the whole thing. The electrodes don't look right in terms of position and could be part of the reason it doesn't light sometimes, it doesn't explain why it sometimes ignites and then loses flame during 5 second safety time though.
That capscrew is seriously tight, should the gasket be replaced when burner is split?

wish id paid more attention to what he was doing when he serviced it.
[automerge]1580750082[/automerge]
I’ve contacted a 3 local heating engineers, 1 said he would go with pump bring issue. 1 said possibly pump but wouldn’t be sure and the other said it’s the control box.
 
That capscrew is seriously tight, should the gasket be replaced when burner is split?

wish id paid more attention to what he was doing when he serviced it.
[automerge]1580750082[/automerge]
I’ve contacted a 3 local heating engineers, 1 said he would go with pump bring issue. 1 said possibly pump but wouldn’t be sure and the other said it’s the control box.

When you split the burner any gaskets need to be replaced if not In good reusable condition. I've not experienced on this burner but have on a Riello where the seal had perished causing it to draw more air which was extinguishing the flame like you're experiencing at times.
I did not say for sure it was the pump, only suspicious and I based that on what I've seen heard and read, like I said I cant be sure without checking a couple things. Control box can cause this issue yes and the DKO does things slightly different in lockout mode but again it's hard to say without being there.
 
As far as I’m aware the only parts that have been replaced during service are the filter and the nozzle, no mention of replacing gasket.

should that capscrew be stupidly tight to undo?

with regards to blast tube does that look in good condition?
 
054510D3-CD29-4345-95AA-754F1818A6AA.png


Image from manual to show the long bolt you should be removing. Blast tube looked ok, usual wear and tear but overall in acceptable condition. Couldn’t see if there were any obstructions to the cell though
 
These things do quite often have torque settings yes. Alan key below on burner casing looks like the one going by image. Been a while for me on this burner lol
 
The large Allen bolt is used for to split the burner (main part from part that also has blast tube and flange on it.
Removing the entire burner is fine if you make sure the seal at flange to boiler is still okay and the bolts are holding burner in firm.
No need to over tighten
 
When was this last record dated? Smoke level fine, CO2 is about right depending on when it was serviced, excess air maybe a little too high. Pump pressure is looking good from my calculations.
 
Looks good readings to me, but I never just assume they are accurate or honest and do my own test results
 
That was July 2019 that it was serviced.
How is excess air reduced?

Adjusting the air is for your oil service person to do using an analyser.
I would say excess air is fine. The CO2 reading is good and reducing the air will begin to increase the CO2.
You tried putting your hand partly over air intake and it didn’t help, so leave air settings untouched.
 
This needs to be done in conjunction with a FGA (flue gas analyser) and I shouldn’t tell you because randomly adjusting can through all other readings out. Ideally you want maximum combustion and CO2 with no excess air, this however is not practical in the modern world and you will always have a lower CO2 and certain amount of excess air, this is down to the fact increasing CO2 also increases smoke and soot emissions. Again CO2 is set depending on ambient air temperature and density. If excess air was too high it can force heat up through the flue and reduce efficiency, it can also cool the combustion process and increase CO ppm as well as extinguish flame, the data sheet suggests your efficiency and CO are good, certainly for a non condensing boiler.
 
This needs to be done in conjunction with a FGA (flue gas analyser) and I shouldn’t tell you because randomly adjusting can through all other readings out. Ideally you want maximum combustion and CO2 with no excess air, this however is not practical in the modern world and you will always have a lower CO2 and certain amount of excess air, this is down to the fact increasing CO2 also increases smoke and soot emissions. Again CO2 is set depending on ambient air temperature and density. If excess air was too high it can force heat up through the flue and reduce efficiency, it can also cool the combustion process and increase CO ppm as well as extinguish flame, the data sheet suggests your efficiency and CO are good, certainly for a non condensing boiler.
Thanks for that, I’ve no intention of adjusting settings I’ll leave that to experts with correct equipment.
2 Questions

1 - Would the excess air cause the burner to lockout?
2 - Could excess be caused if that gasket hasn’t been replaced?
 
Like I said I have known flames to extinguish due to faulty gaskets/seals, however I would expect it to happen constantly if these were a problem.
If there was a problem with gaskets/seals causing an excess of air but not enough to extinguish flame then I would expect to see other readings on my FGA out and the sheet you showed me looked like very good figures (providing they are similar now). I did say the excess air was a bit high yes but only a little to what one usually would see.
 
Like I said I have known flames to extinguish due to faulty gaskets/seals, however I would expect it to happen constantly if these were a problem.
If there was a problem with gaskets/seals causing an excess of air but not enough to extinguish flame then I would expect to see other readings on my FGA out and the sheet you showed me looked like very good figures (providing they are similar now). I did say the excess air was a bit high yes but only a little to what one usually would see.
Figures have been very similar on last few service record sheets, although the 1 from 2016 doesn’t show excess air.
Think I’ll give the electrode gap a check sometime this week.
 

Similar plumbing topics

Yes everything worked fine before. Is there a...
Replies
6
Views
977
Will try to upload pic again
Replies
4
Views
1K
L
With no pressure gauge or flue gas analyser...
Replies
3
Views
1K
External hounsfield heat only. If you really...
Replies
4
Views
1K
L
Camray 5 (90A) (20 year old) oil boiler, had a...
Replies
0
Views
1K
Lincoln22
L
Back
Top