HRM Wallstar Oil Boiler - Advice please | Boilers | Page 4 | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss HRM Wallstar Oil Boiler - Advice please in the Boilers area at Plumbers Forums

1F1920A6-AD6B-406B-981D-D79062BF675C.png


Above is a screen shot of what the electrode dimensions should be. Also note the burner head dimensions of 3-5mm. Like I said I haven’t touched a sterling burner in some time so would have to re familiarise myself. The Alan key you were turning under black cover might be the adjuster for nozzle assembly position, again I can’t remember off the top of my head so apologise if it’s not. Both are extremely important to ensure safe and non delayed ignition.
Check those out if you feel compelled but the rest leave to the engineer, I know you have a background in engineering and more importantly that you know your limits. The attending engineer should take the time to check everything.
 
View attachment 42437

Above is a screen shot of what the electrode dimensions should be. Also note the burner head dimensions of 3-5mm. Like I said I haven’t touched a sterling burner in some time so would have to re familiarise myself. The Alan key you were turning under black cover might be the adjuster for nozzle assembly position, again I can’t remember off the top of my head so apologise if it’s not. Both are extremely important to ensure safe and non delayed ignition.
Check those out if you feel compelled but the rest leave to the engineer, I know you have a background in engineering and more importantly that you know your limits. The attending engineer should take the time to check everything.
Cheers mate, much appreciated with your help and guidance. Best hunt out my feelers to check gap. Must remember to disconnect boiler from power supply, don’t want boiler starting up while I’m checking electrodes lol.
 
Cheers mate, much appreciated with your help and guidance. Best hunt out my feelers to check gap. Must remember to disconnect boiler from power supply, don’t want boiler starting up while I’m checking electrodes lol.

Yes isolate power to system at switched fused spur and shut oil off, take solenoid off as well if really worried. Didn’t say this because it’s obvious lol.
Like I said whoever attends needs to check everything from start to finish, explain to the engineer that sometimes it starts and you lose flame during safety time then lock out and other times it won’t even start, tell them what parts have already been replaced randomly (which is not a sign of a good engineer) and hopefully they’ll get to the bottom of it. From the video I took pre purge, ignition, then loss of flame, cell senses that, I heard the solenoid close and then thermomechanical switch cause lockout. However that doesn’t explain why sometimes it won’t even start, so couple issues might be found.
 
Yes isolate power to system at switched fused spur and shut oil off, take solenoid off as well if really worried. Didn’t say this because it’s obvious lol.
Like I said whoever attends needs to check everything from start to finish, explain to the engineer that sometimes it starts and you lose flame during safety time then lock out and other times it won’t even start, tell them what parts have already been replaced randomly (which is not a sign of a good engineer) and hopefully they’ll get to the bottom of it. From the video I took pre purge, ignition, then loss of flame, cell senses that, I heard the solenoid close and then thermomechanical switch cause lockout. However that doesn’t explain why sometimes it won’t even start, so couple issues might be found.

Who ever I get to come look at boiler I’ll be keeping closer eye on, I think after chatting to you guys on here with the advice you have all given me I think I have a decent understanding on how it all works and what to look for.
I’ll have look at electrodes 1st then get someone to look at it.
 
Adjusting the air is for your oil service person to do using an analyser.
I would say excess air is fine. The CO2 reading is good and reducing the air will begin to increase the CO2.
You tried putting your hand partly over air intake and it didn’t help, so leave air settings untouched.
Hiya,
Ive no intention of adjusting any settings as although the burner is pain in backside sometimes, the majority of time it’s ok so I’d rather it be like that until it’s sorted out properly.
[automerge]1580920862[/automerge]
View attachment 42437

Above is a screen shot of what the electrode dimensions should be. Also note the burner head dimensions of 3-5mm. Like I said I haven’t touched a sterling burner in some time so would have to re familiarise myself. The Alan key you were turning under black cover might be the adjuster for nozzle assembly position, again I can’t remember off the top of my head so apologise if it’s not. Both are extremely important to ensure safe and non delayed ignition.
Check those out if you feel compelled but the rest leave to the engineer, I know you have a background in engineering and more importantly that you know your limits. The attending engineer should take the time to check everything.
I had chance today when I got home from work to check electrodes. I unhooked burner unit like I had the other day and got my trusty set of feelers out. The electrodes appear to be within the specified tolerance of the the screenshot page.
I did take blast tube off and give the fins at the nozzle end a good clean, I’m assuming the fin that has corner bent over is for the photocell to detect flame? I made sure it was clean.
Also had quick look at the pump, took cover off and then undid the 3 Allen head screws, pump gears looked clean, couldn’t see anything obvious. Without fully stripping pump down and measuring components it’s hard to tell if parts are worn. Once bled air out of pump it started up 1st time.
I’ve been quoted about £125 + vat to have new pump fitted.
 
Last edited:
Yes there should be no obstruction so the cell can detect light, if there was the burner would ignite then go to lock out due to no flame sensing.
I mentioned the pump gear set, drive key and coupling but did not say have a look yourself lol. I know you have a back ground in engineering but I only ever opened up a pump if I had spare seals and pump at hand and after I was confident there was a problem with it. What was the drive key and pump coupling like? These pumps should all be put back together with a certain torque as we discussed above.
 
Combustion is most likely then poor if flame isn’t partly being obscured from photocell view.
But can have one of many causes.
Nozzle could be faulty, or air setting wrong or burner drawing in flue gases, or oil pump pressure is set wrong, are some possibilities.
Current heating engineer has replaced nozzle at every service.

Pump pressure recored at the last service in 2019 was same as service in 2016 by different company and is correct to what the specification of burner

How would the burner draw in flue gases? Wouldn’t that be picked up on flue gas analysis?

If air setting was wrong wouldn’t that affect co and flue temp etc?
[automerge]1580922432[/automerge]
Yes there should be no obstruction so the cell can detect light, if there was the burner would ignite then go to lock out due to no flame sensing.
I mentioned the pump gear set, drive key and coupling but did not say have a look yourself lol. I know you have a back ground in engineering but I only ever opened up a pump if I had spare seals and pump at hand and after I was confident there was a problem with it. What was the drive key and pump coupling like? These pumps should all be put back together with a certain torque as we discussed above.
From what I could see and feel, there was a bit of play in the gear wheel against the drive key but without knowing what is acceptable it’s hard to judge.

Had the seal on the external case needed replacing I have numerous o rings and could have temp fixed. The main body of pump is metal on metal so gave it a clean prior to reassembly.

I found data sheet for the Danfoss BFP11 pump and no torque settings shown on it, so a gentle nip or as we call it a British Standard Nip.
 
Last edited:
I cant remember the correct torque setting, I'm sure I saw it on a danfoss bfp pump YouTube video.
The drive key should be solid in its groove with no play, if there was it could cause your issue and eventually shear completely and you would have no pressure or ignition. A photo would of been nice but I'm not suggesting open up again. A dodgy pump coupling could also cause the same.

The burner could draw in flue gases if the flue seals had failed or burner flange gasket was faulty, or anywhere else that could allow products of combustion to escape inside the casing. You could detect these products with a FGA yes.

Just out of curiosity have you ever dipped the tank for traces of water with detection paste? I'm sure this isn't the problem due to what I've seen but thought I'd ask.

With regards to the quote for changing the pump I'm not so sure if that will help now based on what you've said today but without seeing the gear set, drive key or coupling I cant say for sure.
 
I cant remember the correct torque setting, I'm sure I saw it on a danfoss bfp pump YouTube video.
The drive key should be solid in its groove with no play, if there was it could cause your issue and eventually shear completely and you would have no pressure or ignition. A photo would of been nice but I'm not suggesting open up again. A dodgy pump coupling could also cause the same.

The burner could draw in flue gases if the flue seals had failed or burner flange gasket was faulty, or anywhere else that could allow products of combustion to escape inside the casing. You could detect these products with a FGA yes.

Just out of curiosity have you ever dipped the tank for traces of water with detection paste? I'm sure this isn't the problem due to what I've seen but thought I'd ask.

With regards to the quote for changing the pump I'm not so sure if that will help now based on what you've said today but without seeing the gear set, drive key or coupling I cant say for sure.
I would have hoped current heating engineering would recognise fault if flue gases was being drawn back in.

I’ll have another look at the pump sometime this week and take photo. Im not sure if it was the shaft rotating of if it was the gear wheel on the drive key/ drive key in shaft.
I know when we had new oil tank in 2017 there was no mention of water in the oil when the existing oil was pumped out, also the pump showed no signs of water being sucked through.
 
If there was emulsified oil you would have seen a white gooey paste like substance. I was almost certain this wasnt the case but thought I'd ask.
 
I cant remember the correct torque setting, I'm sure I saw it on a danfoss bfp pump YouTube video.
The drive key should be solid in its groove with no play, if there was it could cause your issue and eventually shear completely and you would have no pressure or ignition. A photo would of been nice but I'm not suggesting open up again. A dodgy pump coupling could also cause the same.

The burner could draw in flue gases if the flue seals had failed or burner flange gasket was faulty, or anywhere else that could allow products of combustion to escape inside the casing. You could detect these products with a FGA yes.

Just out of curiosity have you ever dipped the tank for traces of water with detection paste? I'm sure this isn't the problem due to what I've seen but thought I'd ask.

With regards to the quote for changing the pump I'm not so sure if that will help now based on what you've said today but without seeing the gear set, drive key or coupling I cant say for sure.
Your correct about the YouTube video, 5Nm for external Allen screws and 3Nm for the 3 internal screws.
 
New heating engineer came and replaced the pump, after speaking to Danfoss they recommended fitting BFP21L3 instead of the BFP11L3, heating engineer set pump pressure at 120psi and used FGA to set burner up. All running spot on.
Next morning burner locked out.
Heating engineer been back and resealed all the joints in pipe work with oil seal.
Burner still locking out, but starting after reset.

This evening boiler won’t start.....

Could it be electrodes??
 
Christ that's virtually everything. Yes if the electrode gap is wrong or dirty electrodes it could fail to ignite. If it was arching elsewhere other than at electrode ends then the photocell will usually detect false light and not even open the solenoid for ignition and go straight to lockout. Has this been checked? When the pump was replaced was the coupling checked and/or replaced? You could still be experiencing an excess of air at times if seals were perished as we've discussed before. I have a feeling you might have more than one issue still but of course I could be wrong.
 
Christ that's virtually everything. Yes if the electrode gap is wrong or dirty electrodes it could fail to ignite. If it was arching elsewhere other than at electrode ends then the photocell will usually detect false light and not even open the solenoid for ignition and go straight to lockout. Has this been checked? When the pump was replaced was the coupling checked and/or replaced? You could still be experiencing an excess of air at times if seals were perished as we've discussed before. I have a feeling you might have more than one issue still but of course I could be wrong.
Yeah not much left to replace, the coupling was replaced with new pump.
New engineer says that the excess air amount that’s registering on FGA is ok.
He looked at electrodes when he had burner apart and said they look ok, couldn’t see any sign of arcing other than where should be.
 
Has he checked thoroughly though rather than just saying it looks ok? Someone I know had this recently where it was only intermittently arching elsewhere. You got fuel, you got new pump and coupling I know what I'd be looking at next.
 
So when it doesn't start at all the motor runs, you hear solenoid click and see fuel flow but it doesn't ignite at all? If that's the case I'd suspect its ignition related. Electrode gap wrong, dirty electrodes, weak HT leads, weak spark from ebi transformer or arching elsewhere, porcelain electrode covers need to be checked. Control box possibility as well
 
So when it doesn't start at all the motor runs, you hear solenoid click and see fuel flow but it doesn't ignite at all? If that's the case I'd suspect its ignition related. Electrode gap wrong, dirty electrodes, weak HT leads, weak spark from ebi transformer or arching elsewhere, porcelain electrode covers need to be checked. Control box possibility as well
Yeah motor runs.
Sometimes it runs perfectly other times it fails to ignite.
Electrode gap is ok, transformer replaced recently due to weak spark. Control box replaced 7 years ago.
 
It's one of those where theres only so much I can do through a phone for you. If I was the engineer attending and based on what you've said (assuming I haven't misread you) is I'd be looking at ignition first. I say that because motor is clearly running, you say you hear solenoid click and see good neat fuel flow, so saying that it's either an over aired problem (which by now we think not) blowing spark away from nozzle, a problem with the ignition, be it arching elsewhere etc, or a problem delivery the fuel. I've never experienced it but those that have taught me always consider a blocked HP line from pump to nozzle outlet as well.
I can tell you how to safely check spark function and quality but its probably best left to the engineer, I do not want to be responsible for something you got wrong.
 
It's one of those where theres only so much I can do through a phone for you. If I was the engineer attending and based on what you've said (assuming I haven't misread you) is I'd be looking at ignition first. I say that because motor is clearly running, you say you hear solenoid click and see good neat fuel flow, so saying that it's either an over aired problem (which by now we think not) blowing spark away from nozzle, a problem with the ignition, be it arching elsewhere etc, or a problem delivery the fuel. I've never experienced it but those that have taught me always consider a blocked HP line from pump to nozzle outlet as well.
I can tell you how to safely check spark function and quality but its probably best left to the engineer, I do not want to be responsible for something you got wrong.
It’s very frustrating with it being intermittent. The other half is getting annoyed and stressed with it.
Yeah that would be great if you could tell me how to check spark function and quality.
I work in engineering so have a good practical skills background but know my limit and when to get In professionals.
 

Similar plumbing topics

Yes everything worked fine before. Is there a...
Replies
6
Views
925
L
With no pressure gauge or flue gas analyser...
Replies
3
Views
1K
Will try to upload pic again
Replies
4
Views
902
L
Camray 5 (90A) (20 year old) oil boiler, had a...
Replies
0
Views
1K
Lincoln22
L
External hounsfield heat only. If you really...
Replies
4
Views
966
Back
Top