- Messages
- 2,558
Ok. First and foremost isolate electrics and fuel near the burner, remove the coil and to make sure theres no accident due to a faulty stem (I'm not saying there is) remove the flexi going into pump and let any fuel drip into a container (pump will need to be bled afterwards). Now remove the burner from centre long bolt to expose nozzle assembly and electrodes. Now when sure no fuel can be delivered bring the power to burner on and with burner pointing into combustion chamber you are looking for good quality spark between electrodes, if it looks weak or sparking elsewhere or no spark at all then we're in the right area, I would bring the boiler off and on again a dozen times checking the spark each time, if its intermittent then a dozen times should catch it (do not run the pump without oil for too long because you risk damaging it. The boiler then needs to be reassembled and bleed the pump. DO NOT adjust oil pressure or air intake as the burner will need to be set up again using smoke pump and FGA.
The DKO does things differently in lockout. When you interrupt the burner feed and reinstate it the motor runs for 2-3 seconds and then locks out, pressing reset button will then go through sequence to lockout on last fault.
The DKO does things differently in lockout. When you interrupt the burner feed and reinstate it the motor runs for 2-3 seconds and then locks out, pressing reset button will then go through sequence to lockout on last fault.