diamondgas
Hi bigrinks .... soz about the few replies been walking in the Lake District across the weekend 🙂
Regards the circulation issue please do not rule out the primaries but from the info you've given they are less likely! If the boiler is cutting out then the heat build up is enough to trip the overheat usually around 90C+ ... That points to circulation if you know the flow is getting that high at some time. The conclusion would be; heat not being removed quickly enough or a dodgy o-heat!
Regards the fault being in the return, you just do not know? If it's effecting ALL radiators then it's either the heating primary flow or return. Either one will cause grief 🙂
Here's a question I haven't asked as yet; Does the boiler cut out on hot water only at all? Coz if it's cutting out on both hot water and heating circuits then it'll deffo point toward the boiler/pump/or primary circulation pipework! 🙂
Regards the circulation issue please do not rule out the primaries but from the info you've given they are less likely! If the boiler is cutting out then the heat build up is enough to trip the overheat usually around 90C+ ... That points to circulation if you know the flow is getting that high at some time. The conclusion would be; heat not being removed quickly enough or a dodgy o-heat!
Regards the fault being in the return, you just do not know? If it's effecting ALL radiators then it's either the heating primary flow or return. Either one will cause grief 🙂
Here's a question I haven't asked as yet; Does the boiler cut out on hot water only at all? Coz if it's cutting out on both hot water and heating circuits then it'll deffo point toward the boiler/pump/or primary circulation pipework! 🙂