Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ideal isar 30he in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

lupieloo

Gas Engineer
Messages
37
Hi

Servicing this boiler and I have found the inlet working pressure is 12-13mbar when hot tap is running. At the meter is 24mbar working. 26mbar standing.

Would this be classed as At risk? Ideal has mentioned it would be as it would cause incomplete combustion. Anything below 14mbar isn't acceptable.

Also they have a gas hob too.

Kind Regards
 
yes it would
 
Status
Not open for further replies.

Similar plumbing topics

Thanks some good ideas. Just as an aside if we...
Replies
10
Views
2K
  • Locked
Diverter manifold replaced, you were right...
Replies
4
Views
123
Should have added in, naturally there will be...
Replies
3
Views
1K
the Same position for meter but riser outside...
Replies
3
Views
2K
Was re-checked and passed no ID. pressure 15.5mbar
2 3
Replies
57
Views
14K
Back
Top