Can someone please tell me if the regs have changed ? I thought to install a boiler in the loft it had tobe boarded fixed light a loft ladder and a guard rail ? Now I'm being told it has to me a min distance away from the hatch ? Can't find thus info anywhere
Here it is:
From current
BS 6798:2009
Specification for installation and maintenance of gas-fired boilers of rated input not exceeding 70 kW net
5.3 Installation and location
5.3.8 Roof space installation
5.3.8.1 Roof spaces incorporating boiler installations shall conform to the requirements listed below.
a) For an open system, vertical clearances shall be provided so that the static head requirement of 5.7.2.1 is met.
b) Flooring area sufficient to allow access for normal use and servicing shall be provided under and around the boiler. The boiler support shall be capable of supporting the load of the water-filled boiler, associated pipework and equipment.
COMMENTARY AND RECOMMENDATIONS ON 5.3.8.1b)
Where the floor is of combustible material and supports the boiler, a non-combustible insulating base at least 12 mm thick should be provided directly under the boiler.
c) A purpose-designed means of access to the boiler installation shall be provided.
COMMENTARY AND RECOMMENDATIONS ON 5.3.8.1c)
A permanently fixed retractable roof ladder is considered to satisfy the requirement for a purpose-designed means of access. A safety guard should be provided around the roof space access opening.
d) Fixed lighting for the boiler installation and the access shall be provided.
e) A guard shall be provided to prevent contact between stored articles and the boiler, its associated pipework and chimney.
5.3.8.2 When a boiler is connected to an existing brick chimney at a level higher than the connection for a previous installation, the lower section of the chimney shall not be used. The unused lower portion of the chimney shall be
sealed from the used portion by means of a plate inserted below the boiler connection to the chimney but ensuring that other flues in the same chimney stack are not sealed off. Where the chimney is unlined, the plate shall be inserted to form a void extending approximately 250 mm below the boiler connection to the chimney.
COMMENTARY AND RECOMMENDATIONS ON 5.3.8.2
Consideration should be given to providing access to the void immediately below the boiler connection to the chimney. Any openings into the lower portion of an internal flue, i.e. the sealed-off section, should be permanently closed off. For a chimney with at least one external face, the lower disused section should be ventilated to the external air at high and low level to prevent damp penetration.
That's all it is to it. Hope it helps.