Installing a boiler in the loft | Boilers | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Installing a boiler in the loft in the Boilers area at Plumbers Forums

Status
Not open for further replies.
P

plumbdoctor

Can someone please tell me if the regs have changed ? I thought to install a boiler in the loft it had tobe boarded fixed light a loft ladder and a guard rail ? Now I'm being told it has to me a min distance away from the hatch ? Can't find thus info anywhere
 
Thanks that really helps, some boiler manufac round there under warranty refused to work on it cos of no hand rail not a problem I can sort that but was telling the customer it should be at least a metre from the hatch and reckons they should be asking for compensation ! I'm not happy any advice is welcomed, the guy I installed it for was gonna do the rail but he has now sold it and new owner is making a fuss
 
Do like what a lot of installers have done in the past, that I have had the pleasure to repair in the past!!!!!!

Dont bother with a loft ladder,
Dont bother with a light,
Dont bother with a walkway or handrail around loft opening,

ETC ETC

And best of all, stick the boiler in the loft, without all of the above for a pensioner who can't get into loft in the 1st place!!
 
new owner is making a fuss? your customer was the old owner, its there problem tbh.
 
As far as i remember there is no minimum distance required in the british standard so was there a minimum distance specified in the MI?

You say you are being told that who by? the customer? And if so where did they get that info?
 
Spoke to gas safe today and all the above is correct the 1m from hatch dimension seems to have been totally made up by either the custard or the lazy arse engineer from the manufac who obviously could not be bothered to fix the fault !
 
its building regs you are referring to and not gas regs. As such it was the original custards responsibility to see they were adhered to, and if you signed off a ticket to gas safe then you signed to say building regs were iaw the rules. As such you should have made sure it all complied, but your contract was with the old custard, the new lad was sold a seen and hasnt a leg to stand on, as long as the boiler meets all gsr requirements. All in all do you want to work for him any way, if not , stop answering your phone:)
 
Haha at the last post top notch ! Yeah I installed it and signed it off all to correct regs apart from a rail around hatch that custard didn't want ! Must admit I work on boilers all the time in lofts and am yet to see a rail round any loft hatch, this includes fixing boilers that major companies have Installed ! After all your help I'm no longer bothered what the new custard is kicking and screaming about and won't be installing that brand of boiler again if they are gonna cause agg with my custards !
 
So which manufacturer was it?, I had a recent one where the Manufacturers engineer said he cant work more than 2 steps high on a ladder! That was Worcester, so keep your Worcester boilers below 2 steps lads! ha
 
So which manufacturer was it?, I had a recent one where the Manufacturers engineer said he cant work more than 2 steps high on a ladder! That was Worcester, so keep your Worcester boilers below 2 steps lads! ha
There was a story about someone who fell off the bottom rung and died - I can't remember more! It was on some health and safety working with ladders site.
 
I worked on a site any thing above two steps had to have hand rail no working off ladders.it was a scaffolders dream.

life on the job as it should be today, best thing I ever saw was a roofer trotting backwards, tape in hand, straight off the flat roof!! Luckily for him he landed in some of that prickly cotoneaster (cant do plants) bush and really winded himself. His face looked a mess, but once we realised he'd live we all cracked up.
 
It was potterton I suppose if you install a budget boiler you get a budget engineer !
 
Can someone please tell me if the regs have changed ? I thought to install a boiler in the loft it had tobe boarded fixed light a loft ladder and a guard rail ? Now I'm being told it has to me a min distance away from the hatch ? Can't find thus info anywhere


Here it is:
From current BS 6798:2009
Specification for installation and maintenance of gas-fired boilers of rated input not exceeding 70 kW net

5.3 Installation and location

5.3.8 Roof space installation

5.3.8.1
Roof spaces incorporating boiler installations shall conform to the requirements listed below.

a) For an open system, vertical clearances shall be provided so that the static head requirement of 5.7.2.1 is met.

b) Flooring area sufficient to allow access for normal use and servicing shall be provided under and around the boiler. The boiler support shall be capable of supporting the load of the water-filled boiler, associated pipework and equipment.

COMMENTARY AND RECOMMENDATIONS ON 5.3.8.1b)
Where the floor is of combustible material and supports the boiler, a non-combustible insulating base at least 12 mm thick should be provided directly under the boiler.

c) A purpose-designed means of access to the boiler installation shall be provided.

COMMENTARY AND RECOMMENDATIONS ON 5.3.8.1c)
A permanently fixed retractable roof ladder is considered to satisfy the requirement for a purpose-designed means of access. A safety guard should be provided around the roof space access opening.

d) Fixed lighting for the boiler installation and the access shall be provided.

e) A guard shall be provided to prevent contact between stored articles and the boiler, its associated pipework and chimney.

5.3.8.2 When a boiler is connected to an existing brick chimney at a level higher than the connection for a previous installation, the lower section of the chimney shall not be used. The unused lower portion of the chimney shall be
sealed from the used portion by means of a plate inserted below the boiler connection to the chimney but ensuring that other flues in the same chimney stack are not sealed off. Where the chimney is unlined, the plate shall be inserted to form a void extending approximately 250 mm below the boiler connection to the chimney.

COMMENTARY AND RECOMMENDATIONS ON 5.3.8.2
Consideration should be given to providing access to the void immediately below the boiler connection to the chimney. Any openings into the lower portion of an internal flue, i.e. the sealed-off section, should be permanently closed off. For a chimney with at least one external face, the lower disused section should be ventilated to the external air at high and low level to prevent damp penetration.

That's all it is to it. Hope it helps.
 
Last edited:
Am I reading it wrong but other than the flooring the rest say recommendations ? Does that mean there not a must ? Just a thought
 
How the hell can you fall off the first rung and die, that is one unlucky chap, or lady.

Wonder why they never just stepped off it?
 
Am I reading it wrong but other than the flooring the rest say recommendations ? Does that mean there not a must ? Just a thought

From the same BS:

Foreword

Presentational conventions

The provisions of this standard are presented in roman (i.e. upright)type. Its requirements are expressed in sentences in which the principal auxiliary verb is “shall”.

Commentary, explanation and general informative material is presented in smaller italic type, and does not constitute a normative element.

 
I would have thought a loft hatch is a purpose designed means of access, flooring to the boiler from the hatch and a light in the attic, and have installed as such, the rest of it is just recomendations, Im not a chippy so im not installing a ladder or a guard rail.
 
Get the customer to get the roof space work done before you fit the boiler. You need a ladder, light and floor to work with to install the boiler in the first place, or am I idealistic?
 
From current BS 6798:2009
Specification for installation and maintenance of gas-fired boilers of rated input not exceeding 70 kW net

5.3 Installation and location

5.3.8 Roof space installation

5.3.8.1 Roof spaces incorporating boiler installations shall conform to the requirements listed below.

a) For an open system, vertical clearances shall be provided so that the static head requirement of 5.7.2.1 is met.

b) Flooring area sufficient to allow access for normal use and servicing shall be provided under and around the boiler. The boiler support shall be capable of supporting the load of the water-filled boiler, associated pipework and equipment.

c) A purpose-designed means of access to the boiler installation shall be provided.

d) Fixed lighting for the boiler installation and the access shall be provided.

e) A guard shall be provided to prevent contact between stored articles and the boiler, its associated pipework and chimney.

5.3.8.2 When a boiler is connected to an existing brick chimney at a level higher than the connection for a previous installation, the lower section of the chimney shall not be used. The unused lower portion of the chimney shall be
sealed from the used portion by means of a plate inserted below the boiler connection to the chimney but ensuring that other flues in the same chimney stack are not sealed off. Where the chimney is unlined, the plate shall be inserted to form a void extending approximately 250 mm below the boiler connection to the chimney.

The above are required. the comments and recommendations are how you meet the requirements.
But you might meet these requirement using different methods.
 
I would have thought a loft hatch is a purpose designed means of access, flooring to the boiler from the hatch and a light in the attic, and have installed as such, the rest of it is just recomendations, Im not a chippy so im not installing a ladder or a guard rail.

just see if buildings control would accept that, give them a call to find out, as if you sign off the boiler and complete the self certification you might just get a call back in the future to remedy some work if your on a new build or notifiable extension.
 
Status
Not open for further replies.

Similar plumbing topics

You need a new service engineer not a new...
Replies
3
Views
936
I would suggest a Grant registered engineer to...
Replies
10
Views
2K
Hi appreciate and thanks to all that replied...
Replies
11
Views
1K
I think a lot of us suspect your cylinder is...
Replies
12
Views
2K
Back
Top