Intelligent boilers. | Boilers | Plumbers Forums
Guest viewing is limited

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Intelligent boilers. in the Boilers area at Plumbers Forums

Status
Not open for further replies.

joni os

Plumbers Arms member
Plumber
Messages
1,495
Now we have modulating boilers, out side weather compensation, and apps to turn heating on as we drive home has anyone arranged variable flow temps. to match purpose. ie. >75 C when heating DHW and <65C for underfloor heating. The programme clearly defines the purpose but apart from viessmann 4 pipe setup I'm unaware of any regular boilers with this facility. 1 hour per day in non condensing mode DHW. to ensure boiler is fully condensing, heating, 23 hours seems a reasonable trade off.
 
Now we have modulating boilers, out side weather compensation, and apps to turn heating on as we drive home has anyone arranged variable flow temps. to match purpose. ie. >75 C when heating DHW and <65C for underfloor heating. The programme clearly defines the purpose but apart from viessmann 4 pipe setup I'm unaware of any regular boilers with this facility. 1 hour per day in non condensing mode DHW. to ensure boiler is fully condensing, heating, 23 hours seems a reasonable trade off.

Vaillants can be set up for different flow temps for different zones, if you use there weather comp it has to prioritise DHW because of this anyway as the DHW might want a flow temp of 75deg but the heating may want a much lower flow temp depending on outside temp and what the heating curve its set to.
 
WB system boilers with built in diverter can, Vaillant can, Ideal Vouge can, fairly certain you can with intergas also
 
A lot of boilers can, but the manufacturers are not pushing it too much. They don't want the boilers condensing most the time, as amazingly, that will reduce the boilers lifespan!
 
Status
Not open for further replies.

Similar plumbing topics

    • Like
Great summary and well done for getting it...
Replies
1
Views
2K
That looks like excessive wear on the housing...
2 3
Replies
57
Views
5K
Who said plastic 28/22mm copper tube and mlcp...
Replies
3
Views
828
That is manifold fo4 all rooms on 1st floor...
2 3
Replies
58
Views
6K
That's what I was hoping, looks like a good...
Replies
5
Views
986
Back
Top