Just fitted K3 radaitor and the centre front panel won’t heat up | UK Plumbers Forums | Page 2 | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Just fitted K3 radaitor and the centre front panel won’t heat up in the UK Plumbers Forums area at Plumbers Forums

Messages
21
I have started fitting new radiators in my house. The lounge kitchen gets very cold in the winter and is a big room that has previously had an extension put on it and is 19.5 metres by 6.5 metres with a 2.25metre high ceiling.

I started by replacing an old radaitor with a 1200x 600mm K2. Which heats up and works fine, great heat by Stelrad. I have this weekend fitted a K3 1800x700mm. I have this Radaitor hot but the lower centre front panels I can’t get hot. It does feel like the lower half of the radaitor (especially the front panel as that’s what I can get my hand too) isn’t burning hot like the K2. I have tried almost everything apart from actual changing components; I have bled the rads, shut the system down to one rad, balanced the system, the central heating pump is on max.

This Radaitor is working and convecting but not as hot as it should be.


Grundfos UPS 2-50/60
System / non Combi
4rads upstairs 2 hand towel rails
7 rads downstairs one towel rails
25kw boiler

Has anyone else experience this with k3 / triple panel Radaitors. Not a lot of posts online about triple panel radaitors. Some more posts and specifics about K3 issues would be helpful.
 
The boiler is an alpha 24r. I have been working on having another go at any airlocks in the system tonight as I work in the day. Heating system on and drainage out the front door

The boiler is alpha 24r.

I have done some more testing and airlock freeing over the last couple of days. I have managed to clear the airlocks I think. I drained the water of the drain away Radaitor (and out the front door) and ran the heating system at the same time.Also when shutting down to the one radaitor.

The result is shut down all the radaitors and four down stairs radaitors open (3 of them the cast iron former lounge Radaitors) The Radaitor heats to a satisfactory standard. Both the in flow and outflow pipes are hot of the K3. Once I attempt to balance the system the K3 half heats.

What I’m thinking and I am going to do anyway because the house needs it; is the following. But this is a summer project. So won’t be immediate. In the former lounge it has three old cast iron double panel Radaitors, these can struggle to heat along with the K3 in similar manner (often only one struggling to heat) This room I’m going to change to one rad and get just as much heat but a type 22. Then get the other two removed and pipework tapped off. The hallway I have a cast iron rad which again I’m going to change (this is the drain away rad) to a type 22. Then I have two different bedrooms with cast iron rads. These I’m going to change for modern Radaitors one probably a type 22 and the other needs a single panel with fins.

This should create enough flow through the system by making it more efficient removing 2 rads and swapping the others for more efficient rads and probably slightly smaller as I’m swapping from imperial. I’m on 14 rads and 3 towel rails. My system should power 10-15 rads. Removing the (very old) cast iron (all) double panel rads and replacing them should make a difference.

What are your thoughts? Really interested of any opinions.
I should mention the 14 rads in total include 3 towel rails as rads
 
I had thought you had said that the K3s return temperature was only lukw warm even when on its own, the minimum output of your boiler is 6.5kw, if/when you run the K3 on its own does the boiler cycle on/off fairly rapidly, and same for other 3 in the former lounge if you just run those together.
 
I had thought you had said that the K3s return temperature was only lukw warm even when on its own, the minimum output of your boiler is 6.5kw, if/when you run the K3 on its own does the boiler cycle on/off fairly rapidly, and same for other 3 in the former lounge if you just run those together.
When I just run the K3; the boiler stays on all the time. When running the boiler with the K3 and the 3 in the former lounge then it also doesn’t cycle and just stays in all the time. I haven’t ran the 3 in the lounge by themselves.

Initially when I ran the K3 by itself and the outflow to the K3 pipe was Luke warm, the boiler would cycle off and then back on.
 
There's also a fairly high pressure drop through even the clean boiler Hx, if you wanted say 20kw output at a dT of 15C, (1146LPH) (to achieve reasonably high radiator outputs then the Hx pressure drop alone is almost 3M so doesn't leave much remaining head available to circulate the system if a LLH isn't installed.

1683796067873.png
 
There's also a fairly high pressure drop through even the clean boiler Hx, if you wanted say 20kw output at a dT of 15C, (1146LPH) (to achieve reasonably high radiator outputs then the Hx pressure drop alone is almost 3M so doesn't leave much remaining head available to circulate the system if a LLH isn't installed.

View attachment 83378

1.6m John 857lph at 20kw
 
But boiler will want dt20 and will cycle to demand that system may be designed at dt15 but boiler will regulate itself at dt20 by cycling
 
I thought the 20C dT was a sort of standard to compare different boilers but didn't know that the boiler would try and maintain this but difficult on a heat only boiler since it doesnt contol the circ pump. Some Vaillants have return temperature control but I rarely see it mentioned.
 
I thought the 20C dT was a sort of standard to compare different boilers but didn't know that the boiler would try and maintain this but difficult on a heat only boiler since it doesnt contol the circ pump. Some Vaillants have return temperature control but I rarely see it mentioned.

Yes vaillants and gloworms are the worst for it viessmann also cycle a bit if dt is low

It’s more down to pcb logic and estimates it’s take x to heat from this to this so flow rate is y etc
 
This shows perhaps why a K3's front panel doesn't heat up as much as the others and should also be filled very slowly?.
I have quite a few old double panel type 22s, these have only two little manifolds on the bottom connecting the two panels, nothing on the top except two bracing strips of welded on steel plate but both panels have separate air vents which makes them very easy to refill and get rid of the air.

1683844716197.png
 
This shows perhaps why a K3's front panel doesn't heat up as much as the others and should also be filled very slowly?.
I have quite a few old double panel type 22s, these have only two little manifolds on the bottom connecting the two panels, nothing on the top except two bracing strips of welded on steel plate but both panels have separate air vents which makes them very easy to refill and get rid of the air.

View attachment 83388
Hello John,
I have been sick and holiday so very distracted and haven’t got back to my thread.
But yes I do agree, I think at least with large Radaitors a heating system with excellent circulation/ pressure or at least where the K3 is fitted (such as upstairs next to the boiler). Would really help the front panel heat up, but yes the front panel does tend to be diverted around slightly.

Ben
 
Glad to hear, Ben, that you are back in form again,

Regarding that pesky K3, Renewing the cast iron rads should help but I feel that installing a UPS3 pump would improve the flow considerably as you have established that the rad does, more or less, emit its rated output when running on its own since the boiler doesn't cycle on/off.
The UPS3 is a giant of a pump even though a "6M"(6.4) pump like the UPS2, (6.2M) see below.
The other alternative is to install a low loss header, LLH, where one pump deals with the boiler heat exchanger pressure loss and the other pump deals with the rads/system losses.

1685730229372.png



1685730015027.png
 
Glad to hear, Ben, that you are back in form again,

Regarding that pesky K3, Renewing the cast iron rads should help but I feel that installing a UPS3 pump would improve the flow considerably as you have established that the rad does, more or less, emit its rated output when running on its own since the boiler doesn't cycle on/off.
The UPS3 is a giant of a pump even though a "6M"(6.4) pump like the UPS2, (6.2M) see below.
The other alternative is to install a low loss header, LLH, where one pump deals with the boiler heat exchanger pressure loss and the other pump deals with the rads/system losses.

View attachment 83652


View attachment 83651
Hello John

Thank you, the long run on the K3 I think is contributing. It has the longest run in the house. There’s at least a 4 and half metre run just in the room before it even gets out of the lounge/extension. I think the UPS3 pump will help and I will fit this over the summer when I change the Radaitors. Thank you for the technical details I was earlier considering a bigger pump but this more advance pump looks an easier option. I was looking at this link which while slightly off topic explains Pressure drops and flow rates – John Cantor Heat Pumps - https://heatpumps.co.uk/technical/pressure-drops-flow-rates/

Thank you for everyone’s help!

Ben
 
Glad to hear, Ben, that you are back in form again,

Regarding that pesky K3, Renewing the cast iron rads should help but I feel that installing a UPS3 pump would improve the flow considerably as you have established that the rad does, more or less, emit its rated output when running on its own since the boiler doesn't cycle on/off.
The UPS3 is a giant of a pump even though a "6M"(6.4) pump like the UPS2, (6.2M) see below.
The other alternative is to install a low loss header, LLH, where one pump deals with the boiler heat exchanger pressure loss and the other pump deals with the rads/system losses.

View attachment 83652


View attachment 83651
Hello John,

This weekend I done some of the work as planned. Fitted a radiator in the downstairs hallway from a cast iron double panel to a type 22 and changed the central heating pump to the UPS 3. The K3 now heats up properly and think the downstairs lounge kitchen diner now will be warm this winter. So problems solved I think.

Ben
 
Excellent news, what mode and setting are you running the UPS3 at?
Hello John
I tried 2 constant to start with but it didn’t rid the air from the system. Changed it to 3 constant and it heats the K3 (slowly, which I have been told is normal). The old pump ups2 15 50/60 was on 3 constant and failed to heat all the Radaitors. So 3 constant is what I would expect for the UPS 3.

Ben
 
The UPS3 is now probably pumping at it full 6.4M head (speed 3) so next time its running have a look, or get someone to have a look in the attic, and hold a "glass" of water under the vent pipe with the end of the pipe immersed in the glass and see does the level remain the same, you don't want any air ingress through the vent, also, if possible watch the vent when someone stops/starts the pump and see if any spurt of water.
 
The UPS3 is now probably pumping at it full 6.4M head (speed 3) so next time its running have a look, or get someone to have a look in the attic, and hold a "glass" of water under the vent pipe with the end of the pipe immersed in the glass and see does the level remain the same, you don't want any air ingress through the vent, also, if possible watch the vent when someone stops/starts the pump and see if any spurt of water.
Hello John

I can check this in the near future. But I assume this won’t cause any flooding issues from the loft tank if it is to higher head? I can’t hear any air in the system and the pump is running quiet, indicating no air in the system.

Ben
 

Similar plumbing topics

J
  • Question
Take a look at Viessmann boilers and controls...
Replies
2
Views
2K
  • Question
Well done for sorting it. Waggling the trv pin...
Replies
7
Views
863
  • Question
How did you go about heating the extension in...
Replies
10
Views
3K
  • Question
(Just bumping a few older threads, they will...
Replies
12
Views
5K
Back
Top