Undertandable but you can improve heat up time for slow rads by ‘balancing’ them. Has reducing the pump speed affected water liss from the system?

There is a 15mm leg that runs down from upstairs, there are three reasonable size radiators on this. These are slow to warm up (lounge / dining room), I was trying to improve these.

The other radiators have the valve (not the TRV) adjusted to different positions to control how they warm up :)
 
There is a 15mm leg that runs down from upstairs, there are three reasonable size radiators on this. These are slow to warm up (lounge / dining room), I was trying to improve these.

The other radiators have the valve (not the TRV) adjusted to different positions to control how they warm up :)
Theres the issue for them rads not heating. 3 rads on one leg??
 
Hot water likes to go up. So upstairs rads often heat up easier than downstairs. For that reason you can balance all the upstairs ones by closing the lockshield entitely and then opening say 1/3 of a turn only. That shoukd not adversly affect the upstairs rads but the downstairs rads will now have more heat diverted to them.
 
Hot water likes to go up. So upstairs rads often heat up easier than downstairs. For that reason you can balance all the upstairs ones by closing the lockshield entitely and then opening say 1/3 of a turn only. That shoukd not adversly affect the upstairs rads but the downstairs rads will now have more heat diverted to them.

I didn't know about upstairs heating up quicker, thanks!
 
A common misconception is that rads dont need balancing as TRVs take care of that. They dont but modern systems can get away with it. Yours is an old type system and boiker and system will benefit from balancing
 
Me too. But there is a tendency to believe that because TRVs close rads down individually that balancing isnt as important as you and I both know that it actually is - hence my use of “misconception”
 
Ok, thanks. Ones I want to warm up slower are turned right down. I understand about the TRV's not making a difference to warm up speed.


Looking at the radiators, it's only 3 at the front of the house (on a 22mm leg to the first radiator) that are buried in concrete. One of these has never got hot just warm.
It would be fairly easy to put valves on this leg to prove if it is leaking into the ground.

In other news, new electric heaters are working well, but noisy! :p
 
Re-reading your posts about ‘a’ 22 mm pipe and then a rad on ‘a’ 22mm leg. Are you on a ‘One Pipe’ system? Does each rad have a separate flow pipe and a separate return pipe or are both the flow and return coming from the same ‘One’ pipe. As you say the downstairs rads pipes are in concrete you may have to look at the upstairs rads to decide. One pipe systems have their issues. A partial block in the same ‘one’ pipe going both into and out of the boiler will affect circulation easily leading to over pumping especially if pump set to highest speed.
 
Hi, by 'leg' I mean a flow and return. Definitely everything that isn't under concrete is like this. The first radiator from the under concrete pipes is T'd off from a flow and return, I imagine the other two on this leg are the same but can't be definite.

If something is blocked and it is overpumping then where would the water be going?

Thanks for your help :)
 
Hi, by 'leg' I mean a flow and return. Definitely everything that isn't under concrete is like this. The first radiator from the under concrete pipes is T'd off from a flow and return, I imagine the other two on this leg are the same but can't be definite.

If something is blocked and it is overpumping then where would the water be going?

Thanks for your help :)

Agree. The 4-5 min refill of water being lost each day must be going somewhere and since it is not going up the vent pipe that indicates a leak in the underfloor pipework. Hopefully the thermal imaging camera will locate it. Good luck.
 
Yes but I’ve not had it on since as the kids are in bed and the f&e tank filling and the air noise wakes them.

Forgot to say, someone is coming with a thermal imaging camera tomorrow.

A bit late in the day but have you checked if the F&E tank ball cock is still making up with boiler shut down, system cold and ALL the air vented from the rads, if it isn't then you haven't got a system leak .
Another long shot but costs nothing to check out, the F&E tank is mounted in the loft above the cold water supply tank?, if the cylinder coil is holed/split then the F&E tank would continue to make up but the water would be constantly overflowing from the cold water supply tank even with no usage.
 
Last edited:
Thanks for all the advice.

You know when you get a thread like this and the thread starter suddenly disappears because they are too embarrassed to admit what the problem was....

No one should feel embarrassed for asking advice on any problem, its a bit like apologizing for asking a stupid question, well as we all know or should know, there is no such thing as a stupid question but there can be plenty of stupid answers.
 
I'm joking.

I thought I'd check the where all the boiler pipes come up from the boiler into a crawlspace. I noticed that a motorised valve was open that shouldn't have been, it should have been closed. It is on a 22mm flow and return that goes to a heat exchanger at the bottom of the garden. This circuit hasn't been in use for maybe 8 years. I had checked for leaks at the heat exchanger late last night and walked along the pipe run. I knew that because of our water table being so high in the rear garden that any leak of this size would be clearly visible.
Anyway, looking along it today I lifted a section. A JG plastic connector had come apart, presumably in the recent very cold temperatures. Underneath the pipe was a hole that had channelled all the water under the fence into next doors 'garden'.

I think I must have knocked the valve when I put the christmas decorations away!


Thanks again for your help, your much more helpful / less rude than the people on the electrical forum :p
 
I'm joking.

I thought I'd check the where all the boiler pipes come up from the boiler into a crawlspace. I noticed that a motorised valve was open that shouldn't have been, it should have been closed. It is on a 22mm flow and return that goes to a heat exchanger at the bottom of the garden. This circuit hasn't been in use for maybe 8 years. I had checked for leaks at the heat exchanger late last night and walked along the pipe run. I knew that because of our water table being so high in the rear garden that any leak of this size would be clearly visible.
Anyway, looking along it today I lifted a section. A JG plastic connector had come apart, presumably in the recent very cold temperatures. Underneath the pipe was a hole that had channelled all the water under the fence into next doors 'garden'.

I think I must have knocked the valve when I put the christmas decorations away!


Thanks again for your help, your much more helpful / less rude than the people on the electrical forum :p

You are very welcome. So it was a leak in the end but one that was hidden. Glad you sorted it out.
 