Logic Combi ESP1 35 always showing demand for Central heating | Central Heating Forum | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Logic Combi ESP1 35 always showing demand for Central heating in the Central Heating Forum area at Plumbers Forums

Messages
19
Hi folks,

I've got a potential problem with my Logic Combi ESP1 35. When the boiler is set to Central Heating and Hot water mode, the boiler indicates that there is a constant Demand for Central heating.

When the thermostats (TP5000 Si) are turned off (both pulled from the wall and also simply by turning off the heating either via temperature or timer) boiler continues to fire. The boiler indicates that the temperature of the system is always around the 50c mark and as soon as the temperature drops, the boiler kicks in and heats the water again.

I have a dual zone system with some form of valve system which is controlled successfully via the thermostats (photo attached) and as the radiators do not get hot unless triggered by one of the two thermostats i can only assume that it is working as expected.

Initially I believed that this was by design, however after finding a similar post on this site, I'm now not too sure.

I suppose my question is this; when the two thermostats are set to off, should the boiler be continuing to heat that water system or should it go into standby mode and allow the temperature of the system to drop until the thermostat kicks in to show a demand for central heating?

I've also included a picture of the thermostat wiring, which I believe to have been correctly wired.

Thanks in advance for any advice.

Shaun
 

Attachments

  • download.png
    download.png
    597.2 KB · Views: 79
  • download (1).png
    download (1).png
    769.2 KB · Views: 48
  • download (2).png
    download (2).png
    934.7 KB · Views: 47
Zone valves normally give the run signal to the boiler via auxiliary (end) contacts which switch a permanent live to fire it, the motorized valves are closing but one of the contacts may still be closed, the boiler will then continue to fire controlled by its own thermostat.
 
Morning folks,

Thanks for the quick replies; its appreciated.

OK, so the boiler shouldn't be be receiving the demand for heating call until the thermostats kick in. At least I now know that its not wired correctly.

I can see that the zone valves have a wire which drops through the floor and I believe to the boiler, so this may be where the problem is as John.g mentions. I'll open the floor plate (white box near the valves) later to see if I can spot the problem.

As for the age of the house; its just over 2.5 years old and has just left the warranty period. I have dropped the builders a mail about this as if the system has been wired incorrectly, it should be covered by them, either as a good will gesture or perhaps via the 10 year NHBC building cover.
 
It could still be wired correctly but one of the zone valves may be faulty and not opening it's end switch when it closes, tne HW will still work as it takes priority over the CH.
If it's always behaved this way then probably wiring problem.
 
Should be relatively easy to check out at the junction box in front of the two zone valves. Each valve actuator will have 4 or 5 (if earth wired).
Brown&blue and grey&orange. (+yellow/green earth wire).
The brown wire is live from the room stat etc with call for heat and opens the valve via the motor and the blue neutral.
The grey wire is always (permanently) live and the end switch connects this supply to the orange wire and on to the boiler when the valve opens.
With motorized valve de energised (Shut) there should still be 230V at the grey wire but nothing at the orange wire, a multimeter can easily check this out.
 
Hi folks,

Attached is a picture of my floor junction box.

John.g - to perform the test you mentioned above, I believe I need to connect the multi-meter (also shown in a picture) to 3rd and 4th points in the connector block when both of the thermostats are powered off?

If the wiring is correct (which it looks like it is), I should get a 0 reading?

Thanks again

Shaun
 

Attachments

  • download (3).png
    download (3).png
    1.1 MB · Views: 48
  • download (4).png
    download (4).png
    970 KB · Views: 43
You currently have your multimeter set to Amps, and more specifically microamps, this could damage your meter. Select Voltage which is the V~ and use the 600 setting (600 is more than 230/240 vac). Yes the reading should be zero Volts, testing between the orange and blue.
 
I'm a bit slow electrically so can someone point out the actual colour codes from the (any) zone valve and point out clearly which are the permanently wired ones for supply to the microswitch and also the wires connected to each microswitch out, both orange wires appear to be connected together in one connector block, I can see the two brown wires separately connected into the blocks so presume that they are via the roomstats and drive the motors?.
 
Just opened the boiler front up and I've found that the room stat link is still hooked in using the standard pre-installed wire, so it's always going to be on regardless of what the rest of the system is doing.

I see that there's a connector block in the local fused spur which is connecting the black wire from the thermostat circuit to the wire connected to the boiler. This black wire is taped off at the boiler end. Do I simply need to connect this wire to the room stat connector using another piece of wire and a connector block to make the circuit?

Cheers

Shaun
 

Attachments

  • download (6).png
    download (6).png
    752.9 KB · Views: 40
  • download (7).png
    download (7).png
    782.9 KB · Views: 41
Post #3 conclusive then? #smug I would be contact them to find out why the link was left in and room stats not connected , unless you know of any other reason?
 
Last edited by a moderator:
Just opened the boiler front up and I've found that the room stat link is still hooked in using the standard pre-installed wire, so it's always going to be on regardless of what the rest of the system is doing.

I see that there's a connector block in the local fused spur which is connecting the black wire from the thermostat circuit to the wire connected to the boiler. This black wire is taped off at the boiler end. Do I simply need to connect this wire to the room stat connector using another piece of wire and a connector block to make the circuit?

Cheers

Shaun
This "black wire from the thermostat circuit", is it live with either one of the stats calling and is it dead only when both switched out?.
 
I can confirm that the black wire is dead when there is no call for central heating and the goes live at 240V when the call for central heating is activated via the thermostats.

I'm assuming that I'm going to need some form of switch which is off when there's no power and switches on when there is power?
 
If the link is linking a permanent live to a boiler switched live, then if it is removed and if the 4th terminal from left is live and the third from left is dead that the black wire from the stats goes in here (third from left) but this is just my reading of it and may be incorrect so someone else on here may advise you.
 
The wire that I was referring to being being live is the one in the attached picture at the boiler end. So, I'm confident that the wires in the airing cupboard are correct and there's a live feed which activates when the thermostats trigger the call for central heating.

Is the solution to put a relay switch in the boiler with the following wiring?

Please forgive my diagram!
 

Attachments

  • edit1.png
    edit1.png
    745.9 KB · Views: 37

Similar plumbing topics

All sorted, I bled the radiators a little and...
Replies
3
Views
2K
Unfortunately most household insurance...
Replies
16
Views
2K
M
Hi, I noticed the pressure this morning on my...
Replies
0
Views
904
MrDave
M
I have a home with an oil boiler in a garage...
Replies
0
Views
634
This was indeed the case, picked up a new zone...
Replies
13
Views
2K
Back
Top