hi lads,
Just called out today for a low water pressure issue.
Customer had a diyer according to the install without certification for the unvented cylinder which is just 6months old.
However, Thames water checked outside 25lpm and 1.8bar pressure
Inside 10lpm and 1bar pressure static
Operating is below 0.4bar
which indicates that there is an issue with the supply to the cylinder or am I wrong here?
What can be done to solve the issue ?
Partly lead pipe ( outside to inside celler )
The cylinder won’t functioning with such a pressure or flow rates.
I am also wondering if the flue is correcr installed whoch doesnt seem to me as they used the plume or waste pipe to extend it
Any help or guidance would be appreciate it
Thanks guys