In brief
Customer calls with luke warm hot water
Ran the tap and hot water was going down the flow pipe, i changed the diverter valve.
hot water stops going down the flow pipe, but still luke warm hot water
changed the domestic heat exchanger and flow switch, still no change
thermistors are fine
burner pressure is fine
no under gassing
flow rate is 9.5lm
any ideas?