When the boiler is generating more heat than the water circulating in the system can remove and dump via the radiators the heat exchanger temperature rises and when it hits a preset limit shuts down the burners and waits for things to cool down before trying again.
Normally, WBs give a message that says something like '20x Anti-cycling mode' (I forget exactly what they say but that's the gist). I've not seen your particular message myself but I speculate that it may be essentially the same thing but instead of the trigger being flow '5°C above the set-point' it's 'HX temperature too high'.
This explanation is consistent with your observation that the HW system is working okay.
So if I were your engineer I'd want to check temperature sensor(s) for correct operation but once they're ruled out I'd expect the cause to be in this list: an ABV that is set incorrectly or faulty, inappropriate pump setting, undersized radiators, restricted circulation due to TRVs, lock shields set incorrectly, sludge, crushed section of pipe, incorrect pipework with a 'short circuit' between flow and return, etc.
If you post some more details about what the boiler flow temperature is doing before, during and after the boiler 'stalls' it may be possible to be more specific.
Hi and thanks for that. Yes, it is certainly an issue caused by the return temperature being too high and triggering the safety/cycling shut down mechanism. There are no actual error messages being returned on the screen, but if I press the Info button I get the 265 Status Code which I can then see in the manual.
The piping is mostly well over 35 years old (I bought the house in 1987), but I have always treated it with Fernox in my time, and it was given a good flush before this boiler was installed, but I don't know how well it is designed and what issues there may be hidden in there. I previously ran a similar power non-condensing WB combi (which I appreciate would be far less fussy) on this pipework for over 20 years with no obvious problems. All the rads, 9 in total, and valves have been replaced with modern Stelrads, some doubles some singles, which my installer says are more than adequate for a medium size semi. TRVs are Drayton 4s.
By trial and error I have discovered today that a constant higher pressure pump setting, rather than the "variable" setting, improves things when it is heating up from a large room temperature difference, but it starts cutting out again when it nears the target room stat temperature, and when trying to maintain it afterwards. I am however concerned that this is probably not the most economical setting for running the pump.
I also noticed today that when set-up with the constant higher pump pressure it heats the flow by 2 or 3 degrees above the set temperature, and then the Status Code (no Error Message) changes from 200 "System being heated" to 204 "System waiting, primary flow temperature above setpoint" and the pump keeps going rather than stopping, as I would expect, rather than a full stop. I am guessing this is because the Energy Transfer Limit has not been exceeded as in the 265 Status. After it cools for a bit it returns to 200 Status and carries on heating.
Regarding the Flow and Return temperatures, it doesn't seem to matter where the flow temperature is set, it always seems to stall with the 265 code when the difference between the two reduces to about 4 degrees C. This is what appears to be meant by the Energy Transfer Limit.
The WB engineers replaced the PCB and one of the sensors on their first visit (I think it may have been the Maximum Safety Sensor), which didn't make any difference. I have also tried reducing the heat in the system by turning the 24kw power output right down to the minimum of 7kw and running the pump at the minimum 60% with a flow of 50 degrees C, with all the TRVs and lockshields fully open, and although this did allow it to run for longer in between stalls, as you might expect it took even longer to get up to the set room temperature, and still kept cutting out, so not very satisfactory.
What is an ABV please?
Peter