Alex100
Hi all
I had a complete new CH system installed a few months back. I did some research, got multiple quotes, went with a guy with a few good references and checked he was Gas safe registered. He did work very fast though. Perhaps too fast.
It runs 9 radiators from a Greenstar 38 Cdi combi. It's a two storey end terrace house, with about 120 square metres of floor space. The carcass is 22mm copper, with 15mm branches to compact Stelrad radiators. The boiler is upstairs at the back of the house. Another plumber already told me the boiler is too big for this house and so inefficient - I did ask for good water heating power, so maybe that's why he chose that one.
Questions:
1. From installation I thought the rads are small, but the plumber told me that's because they are compact. Anyway, sure enough, it takes about 45-60 minutes per degree of room temp rise in the two living rooms, from when the radiators are really hot on a night, when outside is below about 7 degrees, and this is with the boiler at maximum CH heat setting. I think this is unacceptably slow, as if the heating comes on when the room is 16 degrees, takes 15 minutes to heat the rads, then I'm looking at 5 hours to get to 21 degrees, which is mad (and bedtime). I have checked this with an independent thermometer and it agrees with the thermostat on the rate of heating up the room. Needless to say, we're quite chilly with our brand new system.
The plumber is arguing that he's never had a problem with his BTU calculator and wants us to pay for the bigger radiators we need. I don't care about BTU calcs, as every house is unique and they are only a guide. I want to be sure this is an under-powered set of rads, based on how long it takes to heat up, before putting my foot down on who pays. Underpowered?
2. THE BIGGER QUESTION
With the above and other teething issues, it got me thinking to take a look at the piping. Now I realise that rather than take the flow and return to the front of the house upstairs, for the front and middle bedrooms (which are the lion's share of the upstairs floor space), he has instead taken a long two-pipe branch from the flow and return in the study at the back of house, where the boiler is, all the way to the farthest front room (8-10 metre), and also teed off this for the middle room. So two pipes emerge from study and run 8-10 metres along corridor into the master bedroom, one pipe into one end of a rad and one into the other. Near their beginning, outside the study, a tee is taken from each pipe to go 2-3 metres into and out of the middle bedroom's radiator. The pipework starts as 22mm and reduces to 15mm about 1metre from each radiator.
Is this just lazy but no great issue (the rads do heat up). I do have an attic conversion above the front bedroom, and the plumber knows I want to put a rad in there one day, but that means teeing off what is already an 8 metre branch.
3. The system used to creak terribly and woke us up in morning and kept us awake until fully cooled down at night. It's clearly the pipes touching joists and boards. We did manage to get the plumber back, grumbling somewhat that we're fussy, to put felting in the worst places. He said he's never had to put felt around joist notches for anyone before, but I find that odd, having read how common it is. Am I fussy or is felting standard? (better still, he could have cut floorboards so his pipes aren't touching them where they emerge). It still creaks a lot downstairs.
4. I don't know much about heating systems (obvious huh?). However, does the above indicate I should get a different plumber out to check the system?
If so, what are my rights? I paid about £7k for the system (No VAT, as he's not VAT registered).
Many thanks for any input.
Alex
I had a complete new CH system installed a few months back. I did some research, got multiple quotes, went with a guy with a few good references and checked he was Gas safe registered. He did work very fast though. Perhaps too fast.
It runs 9 radiators from a Greenstar 38 Cdi combi. It's a two storey end terrace house, with about 120 square metres of floor space. The carcass is 22mm copper, with 15mm branches to compact Stelrad radiators. The boiler is upstairs at the back of the house. Another plumber already told me the boiler is too big for this house and so inefficient - I did ask for good water heating power, so maybe that's why he chose that one.
Questions:
1. From installation I thought the rads are small, but the plumber told me that's because they are compact. Anyway, sure enough, it takes about 45-60 minutes per degree of room temp rise in the two living rooms, from when the radiators are really hot on a night, when outside is below about 7 degrees, and this is with the boiler at maximum CH heat setting. I think this is unacceptably slow, as if the heating comes on when the room is 16 degrees, takes 15 minutes to heat the rads, then I'm looking at 5 hours to get to 21 degrees, which is mad (and bedtime). I have checked this with an independent thermometer and it agrees with the thermostat on the rate of heating up the room. Needless to say, we're quite chilly with our brand new system.
The plumber is arguing that he's never had a problem with his BTU calculator and wants us to pay for the bigger radiators we need. I don't care about BTU calcs, as every house is unique and they are only a guide. I want to be sure this is an under-powered set of rads, based on how long it takes to heat up, before putting my foot down on who pays. Underpowered?
2. THE BIGGER QUESTION
With the above and other teething issues, it got me thinking to take a look at the piping. Now I realise that rather than take the flow and return to the front of the house upstairs, for the front and middle bedrooms (which are the lion's share of the upstairs floor space), he has instead taken a long two-pipe branch from the flow and return in the study at the back of house, where the boiler is, all the way to the farthest front room (8-10 metre), and also teed off this for the middle room. So two pipes emerge from study and run 8-10 metres along corridor into the master bedroom, one pipe into one end of a rad and one into the other. Near their beginning, outside the study, a tee is taken from each pipe to go 2-3 metres into and out of the middle bedroom's radiator. The pipework starts as 22mm and reduces to 15mm about 1metre from each radiator.
Is this just lazy but no great issue (the rads do heat up). I do have an attic conversion above the front bedroom, and the plumber knows I want to put a rad in there one day, but that means teeing off what is already an 8 metre branch.
3. The system used to creak terribly and woke us up in morning and kept us awake until fully cooled down at night. It's clearly the pipes touching joists and boards. We did manage to get the plumber back, grumbling somewhat that we're fussy, to put felting in the worst places. He said he's never had to put felt around joist notches for anyone before, but I find that odd, having read how common it is. Am I fussy or is felting standard? (better still, he could have cut floorboards so his pipes aren't touching them where they emerge). It still creaks a lot downstairs.
4. I don't know much about heating systems (obvious huh?). However, does the above indicate I should get a different plumber out to check the system?
If so, what are my rights? I paid about £7k for the system (No VAT, as he's not VAT registered).
Many thanks for any input.
Alex