Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss No-one can work out why our heating isn't working! in the Gaining Plumbing Experience area at Plumbers Forums

It wouldn't surprise me if they were fully qualified these days to be honest.
I went to a job not that long ago and the customer said I was the fifth!!!!
Ridiculous!
It was something that any Engineer worth his / her salt would have diagnosed within 5 min too. That is the largest procession of Plumbers I have heard of but it is by no means the only time I've heard it.
They even left tools!!!

The mind boggles.

Totally agree with what your saying I come across the same , simplest of jobs and they cant do it even basic plumbing tasks seem to be beyond them, and they seem to charge stupid amounts of money, and leave the problem worse than it was, God help this trade in 20 years, not that I'm bothered ! be long gone by then fixing the boilers down below
 
If upstairs rads get hot but downstairs rads dont, pump is literally first thing id be looking at. I would be pulling out the old trusted flathead screwdriver within minutes. My guess is they are 'plastic' plumbers and dont really have a clue. Saying that your system could be sludged leading to the failed 5 year old pump.
 
It could still be a goosed pump because of sludge but the problem as said above will likely be the pump in terms of no corculation
 
It sounds like a flow problem, as in the heat isn't getting pushed around the system. And i'd agree with everyone else and say the pump is probably the first place to look. I just wanted to add that it's possible for the pump to still be spinning making you think it's working, but on its way out and only pushing at half the power it should be, hence only heating half the system up (Y)
 
Hm. I realise this photo isn't exactly helpful. Our latest plumber has installed this yesterday- It's a Grundfos Type UPS 2 15-50/60 230V. Whatever any of that means. he's coming back on Tuesday and is working on the "try everything and see what works" principle. Which is going to turn out expensive I think. He's also flushed Sentinel X4oo in somewhere. And done lots of twiddling and frowning. They are now beard-stroking over the controller. Meanwhile I sit there (wrapped in blankets) saying nothing. Thank you for the facial hair jokes- I was about to make a joke about waxing, but thought it might steer this post in a dodgy direction.

IMG_5562.JPG
 
You say you have an immersion heater, so I'm guessing you are on an open vented old style system.
If upstairs works and downstairs doesn't then the first thing most plumbers would look at is the pump.
Your hot water cylinder will be upstairs so will get heat, but without the pump working it will take a lot longer than usual because the boiler will only be running in short bursts due to overheating as the pump isn't dispersing the heat.
All downstairs valves aren't going to block at the same time.
A system clean doesn't have to be done in the summer, whoever told you that was either lying or doesn't have a clue.
Where did you get your 'plumbers' from?
I would agree it's the pump ,and I'm no plumber ,it would benefit from a flush with fernox too ,you can check your pump operation by undoing the slot head bung at the front of the pump ,to see if it's moving ,also try turning the pump speed up ,you should have 2 or 3 speeds ..but if this doesn't improve things ,maybe the vaines in the pump are shot ,so new pump tine
 
I would agree it's the pump ,and I'm no plumber ,it would benefit from a flush with fernox too ,you can check your pump operation by undoing the slot head bung at the front of the pump ,to see if it's moving ,also try turning the pump speed up ,you should have 2 or 3 speeds ..but if this doesn't improve things ,maybe the vaines in the pump are shot ,so new pump tine
Looking at photo pump seems to be on max speed
 
To be honest though if a pump has only lasted 5 years there's probably another problem too, even if a new pump got it going. I had one recently where like yours, only some rads were heating up and they didn't have as much hot water as before. The pump was still spinning but with no real force, I put a new one in and it still didn't heat everything up, and the pump just didn't sound right. I spent ages trying to get air out but it ended up that the 30 odd year old boiler was so full of sludge that it was slowing everything down. A powerflush sorted it. My guess is just running a cleaner through and draining wouldn't have, you need the force of a powerflush to lift all the sludge out.
 
I’m suprised no one has suggested that the pump may have been fitted the wrong way around. Or that the flow and return might be plumbed the wrong way around onto the boiler. Or that the pump setting might be too low. Or that the system might not be correctly balanced. Or that the bypass might be wide open. Or that there might be air trapped in the System.
 
I’m suprised no one has suggested that the pump may have been fitted the wrong way around. Or that the flow and return might be plumbed the wrong way around onto the boiler. Or that the pump setting might be too low. Or that the system might not be correctly balanced. Or that the bypass might be wide open. Or that there might be air trapped in the System.
Come on Dan ! read all the replies I did ask if pump was the right way round, look at the photo pump is set to max speed
 
I am currently huddled by a fan heater. Our heating hasn't worked properly for over 3 weeks despite visits by 2 plumbers, a lot of beard-stroking and twiddling of valves.
The T37HW-3 Zone Programmer seems to be working fine. The boiler fires up enthusiastically when the timer clicks in, and there the problem starts.
The hot water DID heat up- this seems to have fizzled out in the past 2 days and we have to use the immersion heater. The upstairs radiators heat up, but the downstairs don't, UNLESS you turn off the upstairs radiators AND the hot water. Then you get adequate heat in one or two radiators, always in the same sequence. If the heating is boosted to stay on for about 4 hours, three and a half radiators will warm up eventually.
The Blokes have tried out unblocking radiator valves; have suggested the system needs flushing out (apparently can't be done till the summer?) Other than that, theres been a lot of shrugging.
It seems to me that somehow there's not enough pressure shoving the heat round the system. Could it be a pump? I have NO IDEA how any odd this works but I am sick of freezing and listening to said Blokes talking rubbish. I would LOVE to be able to tell plumber no 3 (coming on Friday) what the problem is!

Sorry , but Its The Pump.
 
Another thought- sent hours on simisim problpr, did flush but couldn't get good flow through system, found a y-filter covered by a more recent fitted kitchen cupboards where they had hidden pipework. Blocked solid and reverse flow of flushing had probably made it worse. Customer had mixed feelings about work to make good, which I understood but thought unfair on us. But piping hot system after clearing it. Suggested a magnaclean.
 
If that's a new pump, it would seem to be a reasonable assumption to make at this distance that the problem is not the pump. Unless the new one is also faulty, which is rather unlikely.

OP - Am I right to assume that the system worked well before 3 weeks ago?
 
I’m suprised no one has suggested that the pump may have been fitted the wrong way around. Or that the flow and return might be plumbed the wrong way around onto the boiler. Or that the pump setting might be too low. Or that the system might not be correctly balanced. Or that the bypass might be wide open. Or that there might be air trapped in the System.

Well given that the system has been working and has just stopped working without any plumbing work being undertaken would suggest that most if not all the things you are suggesting is unnessesary.
 

Similar plumbing topics

  • Question
Problem found, it was a blockage... mostly in...