The best route forward is to remove and rebuild the burner system, checking each of the key points - very often with atmospheric burners, the issue is more than the resolution one specific problem.
As Brambles has said Issac your best bet would be to strip and start again checking all points.
Thanks guys, for such an exhaustive list. It'll be a few weeks before I can get round to such a large job, but I think I might have to give up (again) and call in a third engineer. The trouble is, I don't know what I'm looking for, nor how to stop these problems from recurring. You see, I've done most of the tings on your lists already. Some i do as part of the service (the very thing which started this whole problem), some I've done in response to the problem (I've effectively re-serviced it five times now since this problem began, with no long-term effect on smooth running).
If I go through the list I don't think I'm really going to be any the wiser, nor be in any position to prevent this from happening again.
Wrongly positioned wick - I've replace the wick five times in this whole saga to no effect, plus the latest problem simply occurred out of the blue one day, so - a) I'm suddenly putting the wicks in wrong after six years of doing it right - in which case I need to know what I'm doing wrong, and b) how do I tell I've put then in right when the burner runs fine for weeks before going wrong?
Not enough primary air - I've no idea what I'd be looking for here, nothing about my kitchen ventilation, nor the chamber inlet has changed to my eyes. I have a ventilation grill in the wall next to the burner (which isn't blocked and is never closed) and the inlet is always fully open and never blocked (I don't have pets), so - again I don't know what I'm looking for if this could still be a problem.
Too much secondary air - Not sure what this is.
Insufficient flue pull - I've had the flue swept, and the restrictor plate is the same one that's been in place for the last six years. So, again, if a set up that's worked for six years can suddenly not work, I kind of need to know why that might happen and prevent it, otherwise I might fiddle with the restrictor plate, only to have it go wrong again in a month's time. Or, if there's more to flue pull than just the restrictor plate and the flue being swept, then I need to know what I'm looking for.
Vaporiser not properly seated / sealed - as with the wicks, the vapouriser has always been fine, it's been out cleaned re-seated and replace five times to no avail. If it's broken beyond repair then there's no point in me getting it ourt and putting it back a sixth time without changing anything, but at nearly £500 to replace It would be really great if I had some kind of sign that it was broken, something I could see had snapped/cracked/bent whatever. same with sealing the plug - why would it need sealing now,, all of a sudden There's no sign of wear that I can see. If I get a replacement, how do I know the same thing won't just happen again in a month if I don't know what caused it to happen this time?
Additionally flue downdraft/Anti down draft cowl.- Nothing has changed in my flue set up, so what would I be looking for if flue downdraft were a problem, presumably something which used to stop it all the last six years of perfect running has broken, but I don't know what I'm looking for - the restrictor plate is the same, the flue is the same and the flue cowl is the same - are there any other components?
Oil feed is being heated before it enters the burner - same as the others. How do I prevent this from happening again if I don't know what caused it to suddenly start happening now? It's obviously not been heating the oil feed for the last six years. It wasn't heating the oil feed a few weeks ago (before this crackling noise started). If it now is suddenly, without me touching it, heating the oil feed, I need to know what might have caused it to do that so that I can stop it from happening again, yes?
Oil depth - I check the oil depth at service and it's been fine for the last six years, so - either my checks are suddenly inadequate (does the right oil depth change over time?) or something has happened after service which has disrupted the oil depth - in which case I need to know what that thing might be, so I can stop it from just happening again a few weeks after I've done all this work.
I really am at the point of giving up and ripping the whole thing out. You guys have shown more technical know-how in your posts than all the engineers I've had out put together despite them being able to look at the thing directly, but no-one seems to be able to pin down the crucial question - why has this suddenly started happening now? What did I do in that service (and fail to fix in subsequent five re-services) which caused things to go so irreparably wrong? What suddenly happened a few weeks ago that turned a fairly functioning burner into a non-functioning one despite nothing visible having changed?
I really appreciate all your help, but I'm at the end of my tether and the thought of doing another full service, just like I've done five times before, and it having no effect (again!) is not one I savour, nor is the thought of paying someone, to fail to fix it (again!). Still - it doesn't sound like I have a choice, so maybe in a few weeks I'll be back here badgering you again after another failed service!