Have 7 yr Vailliant ecotec plus 937, serviced yearly. Boiler after 45 mins reaching 2.7 bar I then turn it off! It then takes 3 hrs to return to 1.2. Any ideas what’s going on?
 
I'd assume insufficient pressure in the expansion vessel and would want to verify. Should be much the same as (some say slightly above) the pressure of your primary water circuit. BUT to check you need the primary water circuit to be void of pressure. I would hope the installer checked, with an accurate tyre pressure gauge or similar device, that the vessel was pre-charged to 1.2 bar (if that's your primary water pressure when dead cold) when he installed it. Did he, or did he just assume the pre-charge was correct?
 
18 Rads, 8 double
You probably have a 10 litre EV.
If prefilled to 0.75bar and filled to 1.2bar then it would require a system contents of 170 litres to rise the pressure to 2.7bar with average of flow/return temps of 65C, unlikely that your system is this big, if say 140 litres max then the final pressure above for the same conditions will be 2.25bar. If pre/filling of 1.0/1.2bar, final pressure, 2.06 bar.

But if the prefill has fallen to 0.4bar then a fill pressure of 1.2bar will result in a final pressure of 2.7bar.
 

Similar plumbing topics

  • Question
Use the search box on the top right of the...
Replies
2
Views
1K
  • Question
Just to add, I’ve notice the pressure gauge...
Replies
3
Views
1K
  • Question
1 is filling loop passing. 2 if it’s a combi...
Replies
1
Views
528
  • Question
And it's fixed! Had someone move the EV from...
2
Replies
27
Views
3K
  • Question
You can, as suggested, top up at night/very...
Replies
18
Views
984
Back
Top