I understand that its normal for output flow from a combi to reduce when the inlet cold water flow is reduced (when other outlets are opened) but is there a method/process/configuration that can be adopted to minimise the effect in the the drop in flow and in doing so, provide a priority flow?

It jumps to mind that having a storage tank to feed the combi would provide a solution but as I've never seen this in any property, I'm guessing its not an answer (but would love to know why)

If I replaced the 15mm cold feed to the combi with a 22mm pipe and then had a connection (tee) from this pipe to a 15mm take-off for all other outlets and positioned this tee as close as possible to the combi inlet, would this provide a priority flow rate of any discernible value?

How about reducing the flow in the existing take-offs, is this what you do? (and by how much to make a difference)

Or is there another option that my non expert mindset has yet to consider?
 
Installing a new bathroom has been on the cards for a while now so this is a good time to think bigger. I'm going to have a combi dedicated to each bathroom (2) (I have the space and gas pressure) so now the water flow becomes an accumulator issue (will be requiring good flow to each combi simultaneously) Do I push the water from the tank to the combis using a pump or do I pump into the tank to create internal pressure for the output? Does that make sense?
 
You can get instantaneous gas water heaters that might be a bit cheaper than a combi?

I'm not the person with the best experience to comment on your pumping issue.

My understanding, however, is that you can get an accumulator that recharges from the mains pressure, or a mains booster that is a storage cistern with incorporated pump.

You could also just have a cold water storage cistern and then a pump or pumps coming off that, which may be cheaper and easier to maintain than the previous suggestions. Not sure what the downside may be: may be worth a separate thread?
 
Funny you should suggest that. The combi manufacturer does a continuous flow water heater so I've ordered one of those. I replaced the old stopcock which was on the 25mm mains which then dropped to 15mm then back to 25mm. In doing so, the pressure has jumped 2 bar.
 

Attachments

  • IMG_20201024_103620.jpg
    IMG_20201024_103620.jpg
    417.2 KB · Views: 20
Definitely will help :) From the photo you post, that valve looks like it may be a pressure reducing valve, else I'm not sure why it would incorporate a pressure gauge. Such valves can become a slugish in action and unable to maintain a steady working pressure. If your standing pressure has increased, I'm thinking this was your case.

How's your shower now?
 
collected the data today. 8 bar static and 6.5 working. All outlets open, still 6.5 bar (how come?)
Method: 13l bucket to collect shower output to fill the bucket
Results:
no taps open, bucket fills in 1 min 20 seconds
1 tap open takes 1 min 22 seconds
2 taps open takes 1 min 24 seconds
More than 2 taps and it takes 1 min 26 seconds
So very little drop in flow or pressure which suggests I might get away with the supply being suitable for the additional continuous heater (which arrived today and is much smaller than I imagined it would be) and should be connected by early evening I'm told.
I'll then compare the two heaters outputs against time/temperature using the shower.
 

Similar plumbing topics

  • Question
Hi, I'd be grateful for some advice please...
Replies
0
Views
222
  • Question
Morning, he took it out from where it was...
Replies
11
Views
957
  • Question
There are float switches instead of mechanical...
Replies
2
Views
406
  • Question
Thanks all found these... So I'll fit an equal...
Replies
4
Views
1K
D
  • Question
No sorry if your combining two cwsc tanks they...
Replies
2
Views
686
Back
Top