Agreed, my scheme does not allow independent control of the HW & CH, it behaves as system W. If going for PDHW I assume that’s the main intention.Using the contactor will allow your customer to still have independant control of the HW & CH
I never saw much advantage in Y or S-plan. I had W-plan in 70s/80s, with 3 young kids and an h&c fill washing machine so plenty of HW demand, and didn’t have any problem. And that was with a pretty basic HW cylinder. With a modern cylinder like your 15kW coil even less problem. I estimate my current cylinder, probably well scaled up, transfers about 3kW (30 mins recovery time) and it isn’t a problem, though I do live on my own now.
With PDHW it seems things have gone full circle. And necessary if weather compensation is used, as discussed.
If I understand you right, putting the (NC) switch there, when opened closes the relay contacts allowing CH, but stops HW. I would put a NO switch in parallel with the relay contacts.If you like you can add in a switch between the Cylinder Stat and the contactor so the HW Priority can be turned on and off as required.
With my scheme you can add extra roomstats and zone valves (not limited to 2 total). Updated sketch attached.SP or DP Contactors are fine. You will require DP (Or referred to as a 2 Pole contactor) if you have more than one heating Circuit - for instance upstairs and Downstairs.
Agreed, comments above.Coming back to your solution - The two issues here are one; You have to have HW & CH 'ON' together.
Agreed, it depends on the programmer. I have a programmer leaflet which shows both HW and CH with volt-free DT contacts, so OK for my scheme. If on a new installation need to use that type or similar (DT not required). If an existing installation and it’s not that type, it’s clearly easier and cheaper to do it your way than change the programmer.Secondly; On your diagram you have the Cylinder Stat '2' port coming back to the clock and the clock switching this live feed. The issue here is that on most Two Channel Programmers the Live to the CH 'ON' on the back plate is supplied by the clock and not by a link. So the only way to turn the CH off would be turning the Roomstat down.
Interesting discussion, we may have kicked this to death. Have a good day!