Hi all,
Was wondering if someone with more experience than me with Y-plan wiring could jump in.
HW working fine, no problems at all. 230v at grey wire when HW is off, 230v at orange wire when HW is on. All good so far.
The problem is that CH will turn on but will not turn off again until the power to the heating controls is turned off at the fused spur. There appears to be a backfed voltage of 120v or so on the white wire. I have disconnected the white and orange wires from the wiring centre to make sure it's not a backfed voltage from the boiler/pump. This backfed voltage is present when HW is off, i.e. 230v on the grey wire. As I understand it, there should be no way that 230v on the grey can backfeed to the white wire.
The backfed voltage is also causing the cabling from the SL on the room thermostat to the wiring centre (linked to white wire on motorised valve) to vibrate when the thermostat is calling for heat.
Anyone come across this before? The motorised valve is only 2 months old and was replaced by the previous plumber who had taken to swapping bits in and out trying to resolve the problem without testing the system electrically, apparently.
The customer cannot say for sure whether the problem started or not when the motorised valve was replaced...
Was wondering if someone with more experience than me with Y-plan wiring could jump in.
HW working fine, no problems at all. 230v at grey wire when HW is off, 230v at orange wire when HW is on. All good so far.
The problem is that CH will turn on but will not turn off again until the power to the heating controls is turned off at the fused spur. There appears to be a backfed voltage of 120v or so on the white wire. I have disconnected the white and orange wires from the wiring centre to make sure it's not a backfed voltage from the boiler/pump. This backfed voltage is present when HW is off, i.e. 230v on the grey wire. As I understand it, there should be no way that 230v on the grey can backfeed to the white wire.
The backfed voltage is also causing the cabling from the SL on the room thermostat to the wiring centre (linked to white wire on motorised valve) to vibrate when the thermostat is calling for heat.
Anyone come across this before? The motorised valve is only 2 months old and was replaced by the previous plumber who had taken to swapping bits in and out trying to resolve the problem without testing the system electrically, apparently.
The customer cannot say for sure whether the problem started or not when the motorised valve was replaced...