Technically if its a g4/U6 and pipework 28mm or under you don't need to bother working out the IV. The PV is 5 x cyclic volume (0.002) = 0.01
 
Every app you use will prob give different answer.
If you want accuracy you need go old school and work out using your fingers and toes with standardised formula.
I got 0.02934 volume for a G4 meter.

You've added 10% to the pipework before adding meter volume, right?
 
Technically if its a g4/U6 and pipework 28mm or under you don't need to bother working out the IV. The PV is 5 x cyclic volume (0.002) = 0.01

True, as that is minimum purge vol but I want to check whether I was taught wrong about the multiplying by 1.5?
 
Almost right. :yes:
Went wrong by adding the meter before adding your 10%.

Now that's a funny thing. When I first did ACS, I was taught to do your method. Subsequently I was taught to add meter volume first and then add 10%.
 
True, as that is minimum purge vol but I want to check whether I was taught wrong about the multiplying by 1.5?

No its right enough.
You would only bother working out the IV for a purge if there was > 28mm or a G10/U16 on it so it is irrelevant in this case anyway.
 
Now that's a funny thing. When I first did ACS, I was taught to do your method. Subsequently I was taught to add meter volume first and then add 10%.

Some acs centres have their heads up their rses.
Gimme a minute and i'll post a pic from UP1B.
 
Some acs centres have their heads up their rses.
Gimme a minute and i'll post a pic from UP1B.

Just checked the Construction Skills textbook. 10% added to pipework and then meter volume added. So yeah, the worksheet the assessment centre gave us was wrong!

Although, I noticed something else in the book - we've all been adding 0.008m3 as meter volume, but that is meter internal volume. Meter purge volume is given as 0.01m3 for U6/G4.

God, I'm sad...
 
according to this app (uk gas app) with a g4 meter with straight run of 35mx22mm pipe with no fittings comes to 0.0305m3 so a 30m run of 28mm and 10m of 22mm with 6 fittings cant equate to the same?
looking at same volume
 
Untitled.jpg
 
Just checked the Construction Skills textbook. 10% added to pipework and then meter volume added. So yeah, the worksheet the assessment centre gave us was wrong!

Although, I noticed something else in the book - we've all been adding 0.008m3 as meter volume, but that is meter internal volume. Meter purge volume is given as 0.01m3 for U6/G4.

God, I'm sad...

the inspectors will be busy next week.lol

i rely on my app's or last resorse get the book out of van.
did my resits last week and they said 'right get your prefered app ready for purging/pipes & vents.lol
 
Just checked the Construction Skills textbook. 10% added to pipework and then meter volume added. So yeah, the worksheet the assessment centre gave us was wrong!

Although, I noticed something else in the book - we've all been adding 0.008m3 as meter volume, but that is meter internal volume. Meter purge volume is given as 0.01m3 for U6/G4.

God, I'm sad...
Yip. For standard G4/E6 upto 28mm pipe the standard purge is 0.01.
Bigger meter and or greater than 28mm pipe then you need to calculate.
 
Wow.a lot of info in there guys. Thank you. So basically, all I need to do is purge 0.01 and all is well as no 35mm pipe or u16 meter.

So I am within scope.

I know some boilers have a purge setting on them so think I shall do it this way


Thanks for all the help guys. I appreciate it.
 
Just one more thing to clarify, it is the installation volume that makes it commercial and not the purge volume correct? Which is what tamz's diagrams explains
 
Wow.a lot of info in there guys. Thank you. So basically, all I need to do is purge 0.01 and all is well as no 35mm pipe or u16 meter.

So I am within scope.

I know some boilers have a purge setting on them so think I shall do it this way


Thanks for all the help guys. I appreciate it.

no!
the installation volume is>0.035 and by the book..its out of scope!
whether it matters could be debateable but you wouldnt do it near an inspector ;)
perhaps were all on a learning curve here, one for the acs reassesment center when tickets are due.haha

however, based on this there in scope and simular to what tam said, so 'grey area'?
http://shop.igem.org.uk/download/document/Pages from IGE-UP-1B Edition 2.pdf
http://shop.igem.org.uk/download/do...UP-1A Edition 2 (Reprint with amendments).pdf
 
no!
the installation volume is>0.035 and by the book..its out of scope!
whether it matters could be debateable but you wouldnt do it near an inspector ;)
perhaps were all on a learning curve here, one for the acs reassesment center when tickets are due.haha

however, based on this there in scope and simular to what tam said, so 'grey area'?
http://shop.igem.org.uk/download/document/Pages from IGE-UP-1B Edition 2.pdf
http://shop.igem.org.uk/download/do...UP-1A Edition 2 (Reprint with amendments).pdf

He's well within scope!

Scope refers to the installation volume, not the purge volume. Installation volume in this case is, as several have worked out, 0.030M3

The purge volume is 0.085m3 which, if you crack a joint under the boiler, will take 180 seconds to purge.

You'll have gas long before that but the 120 will definitely prevent any air pockets being left.
 
The volume is 0.2934 so its fine

I should reload again after going to the shop ;)
 
Last edited by a moderator:
He's well within scope!

Scope refers to the installation volume, not the purge volume. Installation volume in this case is, as several have worked out, 0.030M3

The purge volume is 0.085m3 which, if you crack a joint under the boiler, will take 180 seconds to purge.

You'll have gas long before that but the 120 will definitely prevent any air pockets being left.

Just wondering how you worked out the purge time. Is there a calculation you do to figure this rather than having to go to the meter to make sure you purge the correct amount?
 
Status
Not open for further replies.

Similar plumbing topics

Experience tells me 10mm won't be enough but...
Replies
5
Views
835
The date the inspection is let’s say 2 months...
Replies
13
Views
174
More than fine then in 11/5 tube should be...
Replies
3
Views
674
When they converted to northsea gas in the...
Replies
3
Views
598
Back
Top