Hi Gents

I have problem with pressure in my house. Plumber advice my to read about cold water booster set, it is grate solution in that kind of situations i read. I think i will go for one of this device. My question is how do you sizing this to the property, what should i take into consideration. What is the best quality for money???
 
5. budget i don't know i would like to buy something right quality to money and install my self. I know how to hold spanners and pliers.
You do know of course that the installation of a booster pump drawing more than 12L/M is notifiable to your local Water Undertaker under the Water (supply & fittings) Regulations 1999?
You must give formal notice in writing before you start, it is likely that they will wish to inspect the installation upon completed.
 
You do know of course that the installation of a booster pump drawing more than 12L/M is notifiable to your local Water Undertaker under the Water (supply & fittings) Regulations 1999?
You must give formal notice in writing before you start, it is likely that they will wish to inspect the installation upon completed.
Hi Chris
Last time I rang the local council to notify. They put me through to building control, who said
“ don’t know what your on about?”
 
Chris that is only when the pump is directly connected/ fed from mains not when your feeding from a stored source
 
Hi Chris
Last time I rang the local council to notify. They put me through to building control, who said
“ don’t know what your on about?”
This is the Water Regs Chalked not the Building Regs so it falls to the Undertaker to administer & enforce.
Chris that is only when the pump is directly connected/ fed from mains not when your feeding from a stored source
Sorry Shaun but it isn't limited to directly connected pumps.
It makes it quite clear that it applies to pumps that are indirectly connected drawing more than 0.2Litres/second. see - Table 5 (1), sub-clause 4(d) and it provides a diagram R6.1b showing indirect connection break cistern.
 
This is the Water Regs Chalked not the Building Regs so it falls to the Undertaker to administer & enforce.
Sorry Shaun but it isn't limited to directly connected pumps.
It makes it quite clear that it applies to pumps that are indirectly connected drawing more than 0.2Litres/second. see - Table 5 (1), sub-clause 4(d) and it provides a diagram R6.1b showing indirect connection break cistern.

But it’s not drawing from the main it’s being fed from a tank

Why would they need to know you’ve connected a pump to a tank don’t have to let them know about shower pumps
 
But it’s not drawing from the main it’s being fed from a tank

Why would they need to know you’ve connected a pump to a tank don’t have to let them know about shower pumps
Full guidance is given in R6.1 but to answer your question installing a pump even if it is indirectly connected will increase the draw from that supply main (more water out = more water in) especially if the cistern is not sized correctly therefore they want to know about a risk that the main pressure could drop, leading to an increase risk of back siphonage in surrounding properties.
Them's the rules "you have to give notice before you start" They then have 10 working days to respond.
The Water Supply (Water Fittings) Regulations 1999
 
Last edited:
At the end of the day, increased usage by one property in a stress water supply area wether its pumps that suck, or push on stored water leads to the neighbours getting kicked they all install one and everbody is back to square one. Did one in Hightown a few years ago, Grunfos one, guess what we more or less worked our way round thus little cul de sac. and they are all back in same desert Happy Days Rob Foster aka centralheatking
 

Similar plumbing topics

  • Question
What type of cylinder do you have?
Replies
6
Views
1K
  • Question
IME Mira showers of that age are usually very...
Replies
1
Views
622
  • Question
hi have been a plumber for 50 years this month...
Replies
1
Views
842
  • Question
Yes or they do an extra tank so brings it upto...
Replies
3
Views
562
  • Question
Thanks. I'll try to find a hard copy as I...
Replies
3
Views
960
Back
Top