Radiator banging / clicking - possible reaction to F1 protector? | UK Plumbers Forums | Page 2 | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Radiator banging / clicking - possible reaction to F1 protector? in the UK Plumbers Forums area at Plumbers Forums

Messages
32
Hi.

We’ve had rather a lot of noise issues with our radiators since we had a new boiler installed. Our radiators other than 2 more recent ones are all over 30 years old.

When the boiler got installed in the middle of 2020, after the first few days, we had several loud airlocks each day. Probably up to 10 times in total until we got the plumbers round to sort it out. I can’t remember exactly what they did, but the air locks stopped occurring then. But what then was the case was that whenever the heating was on, the main radiator that must remain on all the time seemed to have a sound similar to a cold tap permanently running. That sound was amplified to the room above, unless the TRV on this radiator was either on 5 or totally off.

We got the plumbers back, and they then drained the system (not a blast out though) and added some Fernox F1 Protector.

This seemed to remove the issue I described with the sound like a tap was running, but introduced a whole load more.

The system clicks and bangs occur very regularly when the heating is on. It however is much more noticeable in my bedroom, but the noise is very similar in many other places in the house. It is not coming from the radiators, but they are what makes it more audible as upstairs all the pipes are under the floorboards. The F1 Protector I’m guessing caused some sort of chemical reaction. Every single day, loads of air / gas was generated and the radiators could be bled very frequently with more build up of whatever this was. The water was also very dark grey and smelt strong. We kept dealing with this throughout the winter ourselves and although the noise remained, the issue with the gas does seem to have gone now, probably because the radiators hadn’t been used this last summer.


Now, the clicking decreases when the heating is off at the boiler, but it still clicks or bangs randomly usually at least once an hour through the night. Sometimes it can be incredibly loud.



From what I’ve read, this now could be many things:


Boiler kettling – It seemed that F1 protector it supposed to help with this, but it seemed putting that in caused trapped air and other nasty reactions.

Expanding / shrinking pipes – This sounds like it could indeed be the case. As I can lift and move my radiator slightly and feel it rubbing in the hole in the floorboards, and I can almost create the identical sounds myself by doing this. However, the radiators and pipes have not changed since our boiler got replaced, so as that is the case, I can’t understand why this should be related. Our heating with our old boiler just bade a very quiet and consistent tinkling while on, and no noise when off.

Dirty pipes – While we had the F1 protector put in supposedly to clean the system, given the reaction it caused, it probably has made it worse. We don’t have air / gas in the system now and the water seems clean, but I obviously can’t tell what the pipes are like. I don’t believe it is related to the radiators now, as I can turn them off at both the TRV and other valve and the noise still occurs from the pipes.


As it is a new boiler with very old pipes and radiators, it is hard to know if a full system flush will solve this issue. I know that these radiators and pipes can be quiet, and nothing physically should have changed about them. Just likely to be something in them.



This clicking / banging has been irritating me so much that I’ve done rather a lot of recordings of it. So I can explain what it is better.



This first link below is actually from last year. This was during the day when I was at my desk. The microphone easily picks up me pressing a few buttons on my keyboard, but then it just sounds like a hard metal object hits the radiator hard. The radiator is nowhere close to my microphone, which just shows how loud it can be. This is a good example of what can occur in the night.



This next clip is close up to the pipe when there was an obvious reaction of some sort. You can hear what sound like fragments rolling around in the pipes, spitting, gurgling and then this clicking and banging begins. The gurgling has long since stopped, but the banging and clicking remains.



Number 6 was only from a few days ago when the boiler was on, but my radiator off. I’ve edited the recording and joined many of the sounds closer together. They sound similar, but can vary a lot regarding how far apart they are.






This is an awful lot of information, but I’m really stuck with what this is most likely to be, and what sort of people would know most about it and be able to sort it.







Many thanks.
 
The higher the pressure (head) the greater the circulation flow, some systems depending on number of rads length and diameter of pipework etc will require higher pump heads than others, that's why you have multiple choices of pump heads. Pump head (differential pressure) is normally expressed in meters M, M/10 = bar so 6m=0.6bar, 5M=0.5bar, etc,
 
Thanks, this hopefully will make more sense to me eventually.

We have 7 radiators. 5 being pretty large and the bathroom and my bedroom (both small rooms) have smaller ones. The hallway is the only one without a TRV as that is the main one (not sure the name for it).

Two of our radiators are newer than the others, but still over 15 years old rather than well over 30, but the pipework could well be a similar age to the house which was built in the 60s.

One example of the sounds in the night is below. I had my microphone recording it the whole night, and joined several of the sounds together. Typically, the really loud band was not there this time. The best example of what they can be like was in the first clip in my first post.


Our heating comes on soon, so I will make sure i check the pipes first, then let you know. They I will try changing some of the things you have suggested.
 
right, when the heating first came on, it was the pipe at the top right that first started to build up heat. After a few minutes, the other one got warm, but didn't seem to quickly get hot like the other. As the water was going along the pipes here, I could hear what sounded like fragments rolling around in the pipes above the boiler - a similar sound to what I had in my bedroom pipes a while ago.

Now the heating is on, despite my radiator being off off, the pipes are clicking and ticking away many times a minute, and while I know it can be normal for it to do this more quietly when the heating first comes on, it is the fact that it keeps stopping and starting these intervals of many clicks while the heating is still turned on.

I'm unsure on how to change the pressure gauge though.


By the way, I have also checked the pump. As is has an LED when it is on, I know that it must have been off when I last checked it later in the evening the other day when the heating was off, as the LED was off. It turns out it is on speed 1. My dad told me he had put it to 2, but it may be too long ago to remember exactly. Let me know what other mode to try now.


Thanks.
 
Open the black arrowed valve 90 deg anti clockwise and increase whatever pressure its showing now by 0.3 bar but no more, reclose valve.

Flow pipe on boiler seems correct.
Will revert later re pump.
 

Attachments

  • Pressure Gauge 2.JPG
    Pressure Gauge 2.JPG
    511.5 KB · Views: 40
To select CP1, press the setting button for 3 sec, then single presses until 1 flashing green at one end and 1 flashing yellow at the other, CP1 is now selected with a constant pump head of 3M.

1635615025862.png
 
Open the black arrowed valve 90 deg anti clockwise and increase whatever pressure its showing now by 0.3 bar but no more, reclose valve.

Flow pipe on boiler seems correct.
Will revert later re pump.
I've changed the pump mode / speed to CP1.

I just need to fully understand that valve does, and make sure that it isn't easily possible to go wrong in a way that matters in the long term. As usually, I don't do any of this stuff myself.
 
You cant go wrong, that valve allows mains water into the system/E.vessel and even if you forgot to close it the red topped safety (PRV) valve on the boiler top will open at 3 bar.
So just open it slowly, you should hear water passing through it and the pressure gauge should start rising slowly, reclose the valve when the pressure has increased by 0.3 bar.
 
Done that now. Got the valve to be showing a fraction over 1.2. Still hearing the clicking, but possibly should give it time and wait for the heating to go off and give it another cycle.

The last 2 things done by plumbers did make a significant change to the sound but not making it quieter!

I almost wish I had left it as it was (as in not have the plumbers drain it again) as although that was still annoying, it was nothing like as bad as this. Before the time they emptied it for the 2nd time, it sounded like a cold tap was running (not sure, but I notice virtually everywhere seems to have a louder cold tap than the hot one) You could only solve this by making sure all of the TRVs were on maximum, so it was an issure if you wanted good control of the temperature. But at least that was totally consistent and predictable, and only the case when the heating was on. This clicking and other stuff only seems to have been an issue since the system was last refilled with the f1 protector added (it didn't have a power flush at any point)

So if what you have suggested and I have now done doesn't work, I'm wondering if a power flush may be the next option, though it obviously will cost and we can't be sure it will work.
 
Last edited:
I wouldn't be holding my breath re the above steps.

Are you getting any air/gas when you vent now (cold).?.

There should really be a air vent right on top of the boiler or on the flow pipe as it leaves the boiler, the boiler probably has a internal one but this is generally shut off after commissioning.
I suppose any air should really gather somewhere else where you can vent it.

I honestly can't suggest any other options, a power flush may work as you say?.

The only thing that I am not 100% sure about is the boiler flow being on the right hand side, the eManual doesn't specifically say so but the schematics of different pipe layouts suggests that it is.
You might check that out with Ideal Logic or some installer here might inform.

Just one other thing, that pressure should rise and fall between a cold and hot system by maybe 0.5bar.
 
Last edited:
I wouldn't be holding my breath re the above steps.

Are you getting any air/gas when you vent now (cold).?.

There should really be a air vent right on top of the boiler or on the flow pipe as it leaves the boiler, the boiler probably has a internal one but this is generally shut off after commissioning.
I suppose any air should really gather somewhere else where you can vent it.

I honestly can't suggest any other options, a power flush may work as you say?.

The only thing that I am not 100% sure about is the boiler flow being on the right hand side, the eManual doesn't specifically say so but the schematics of different pipe layouts suggests that it is.
You might check that out with Ideal Logic or some installer here might inform.
At the stage we had large build ups of air or gas, it seemed that most days, virtually all the radiators in the house would get quite a lot of whatever this was in them. Some of them you could be bleeding for over 30 seconds with the water only spitting just slightly, with significantly more of whatever the air was. Presumably the reason why it was spitting liquid just slightly it was because there were a load of bubbles inside or something.

It is possible that what settled this was the summer and having no heating used at all for many months. This water was very mucky last winter when this reaction (to something) was occurring, so presumably although the water seems clean now and the air is gone, some of the muck build up must be somewhere and maybe it could be related to the noise continuing?

I've tried bleeding the radiators again and they all seem full up. Haven't noticed any air or gas in them since they have been off over summer.
 
I doubt the age of the radiators has ANY bearing to the noises. Until they leak radiators don't really change in behaviour. By age, I do literally mean any age. Two thirds of the radiators in the building where I am writing this from are 49 years old.
 
I doubt the age of the radiators has ANY bearing to the noises. Until they leak radiators don't really change in behaviour. By age, I do literally mean any age. Two thirds of the radiators in the building where I am writing this from are 49 years old.
We first thought that nothing should change with the radiators as the pipes hadn't been touched. But all the TRVs had been replaced as well as the boiler as it was that that had failed.
 
Did they get cleaned eg with an ADEY magna cleanse ?
 
Hasn't been 24 hours yet, but not sure if that makes a difference. But after the adjustments made to the pump (Speed 1 to CP1) and the increase of the pressure gauge to 1.2, neither seem to have made a difference, but were worth trying. Still getting the same clicking and occasional loud bangs in the night when the heating is off.

Did they get cleaned eg with an ADEY magna cleanse ?
As I know we haven't had a power flush at any point, I presume that was never used. We just had our system drained when we had our new boiler fitted, then drained again when we complained about airlocks and noises like a tap was permanently running. They then drained the system and refilled the system with F1 protector in October a year ago. It was just after this when we started using the heating more often that we seemed to get this reaction that caused dirty water and gas / air build up as well as a load of clicking and banging.

Over the summer, the air has gone and the dirt also, unless it has settled somewhere, but nothing has been done since we had this issue. Now it is winter again, the noise has come back. It is just so hard to diagnose what it is.
 
It could be something as simple as heat expansion due to the little plastic radiator clips breaking at the back where it goes onto the metal bracket
 
Boiler kettling – It seemed that F1 protector it supposed to help with this, but it seemed putting that in caused trapped air and other nasty reactions.

Expanding / shrinking pipes – This sounds like it could indeed be the case. As I can lift and move my radiator slightly and feel it rubbing in the hole in the floorboards, and I can almost create the identical sounds myself by doing this. However, the radiators and pipes have not changed since our boiler got replaced, so as that is the case, I can’t understand why this should be related. Our heating with our old boiler just bade a very quiet and consistent tinkling while on, and no noise when off.

Dirty pipes – While we had the F1 protector put in supposedly to clean the system, given the reaction it caused, it probably has made it worse. We don’t have air / gas in the system now and the water seems clean, but I obviously can’t tell what the pipes are like. I don’t believe it is related to the radiators now, as I can turn them off at both the TRV and other valve and the noise still occurs from the pipes.
It could be something as simple as heat expansion due to the little plastic radiator clips breaking at the back where it goes onto the metal bracket
I had said in my original post (sorry for the length of if) about me thinking it could be expanding pipes, although I thought several things me and others had discussed since sort of made this unlikely. As the pipes and radiators haven't changed since the new boiler got put in place. And this clicking and banging only got introduced when the radiators got refilled with F1 protector a year ago. Almost all the pipes seem to do this now (but vary in volume), when they didn't before the system got bled out.
 
But you changed boiler was the old one tanks in the loft and the new one pressure gauge ?
 
But you changed boiler was the old one tanks in the loft and the new one pressure gauge ?
We have a water tank in the airing cupboard as well as a boiler downstairs in our kitchen. Our old water tank was still working when our old boiler gave up, but wasn't very efficient so we got that replaced at the same time as the boiler. I'm unsure of the type as I know little about this stuff. So I may well keep naming the things incorrectly.

Well, it looks as if F1 started the noise so what about a drop of F2 into one of the rads to stop it?.
I notice that many retailers sell Fernox of all types. This does look like a cheap option to try, but isn't this something that I shouldn't really be doing myself?

Even so, i I had to get someone in to do it, it would be cheaper than getting a powerflush. That may be the last option if nothing else works. But yes, it does seem to be the addition of F1 protector that made a significant change to the sound, and nothing I've tried myself recently has changed it.
 
Sorry that’s the cylinder have you always had the pressure guage / filling loop in the airing cupboard
 
The pressure gauge got added when we had the expansion vessel put in above the airing cupboard in the loft. My dad tells me that was probably over 10 years ago, so well before out boiler failed. He said this used to reduce in pressure by itself, and since we got our new boiler, it has been better at maintaining the same pressure. But as was suggested by John, I've increased it just a fraction.
 
If you wish, you can quite easily put a can of that F2 into a rad, just post a photo of one of your newest rads showing the air vents and can show you then.
I will consider this then as it is easy to get hold of. It hopefully is one of these things that can me done by the inexperienced like myself and have little risk of causing any harm.

However, it does say it is intended for boiler noise, which isn't really the issue. I always hear the boiler come on and it is louder than our old one, but it just makes a noise that is only really noticeable in the kitchen or above in the bathroom and it seems a perfectly reasonable sound for what you should expect. The pipe noise surely won't be specifically boiler related will it? Especially when off.

I can't tell what is more likely to be the cause of this starting up. Not sure if emptying the system as well as adding the F1 protector was any more likely to trigger what happened rather than just adding the protector without bleeding the system.


This F2 protector doesn't cost much, but reading up about it, it still seems like it may not be the sort of thing that helps stop radiators and pipes banging / clicking. If it doesn't work, it likely will have to be will have to be wasted as the only other option i can see is the power flush.
 
If you wish, you can quite easily put a can of that F2 into a rad, just post a photo of one of your newest rads showing the air vents and can show you then.
I will get a picture when I get the chance. I just need to understand the exact location on the radiators you are on about. Is this where you bleed them? Even the newer radiators take the same key to bleed them so they likely have the same style vent.


Regarding the heating noise, this picture is quite good at showing what the sound is like over the whole period the heating is on from 06:00 until 08:30.
2021-11-03-101335_1920x1080_scrot.png


Virtually all of the lines are the clicks. I could understand more if it was when it was coming on and going off, but the fact that when it is on, the pipes randomly start doing these clicks so frequently seems odd. Just before an hour for example.
 
Was it making noises when (if) you tried it with both CH&HW off and the hot tap opened?.

This is the plug end you remove after opening the vent (screwdriver slot), you first (after first shutting valves at both ends of rad) open the vent to ensure no pressure, then remove that blank end, open the vent a few more turns, syphon off a litre or so of water and pour in the F1 via a plastic funnel or whatever, close up the rad, reopen valves top up pressure if required, flash up the boiler and wait for the silence!!.
 

Attachments

  • Vent End.JPG
    Vent End.JPG
    16.9 KB · Views: 34
  • Vent Plug.JPG
    Vent Plug.JPG
    8.5 KB · Views: 32

Similar plumbing topics

  • Question
Hi Kop, thanks for the reply. No water storage...
Replies
2
Views
1K
  • Question
I would of clipped the pipework but it is...
Replies
2
Views
239
R
  • Question
In the diagram below shows a typical S-plan...
Replies
3
Views
1K
Recently over the past 2 months, the boiler or...
Replies
0
Views
3K
  • Question
Oh nice one, that's really useful. Those look...
Replies
6
Views
1K
Back
Top