Hi All,
I am having a few problems with my radiator system, I have had a new boiler fitted earlier this year and I have also fitted an additional radiator as well as rerouting the pipework to another radiator, this was all earlier in the year, but it's not until now the temperature has dropped that I jhave noticed the problem.
My problem is that one room isn't getting to temperature, I have one radiator which is noticeably cooler than all the others on one that is slightly cooler than the others, both are new and in the same room, they are fed from above indipendanly tee'd into a 22mm pipe with 15mm pipe (Close together).
The area that I think is the problem has 4 radiators Tee'd off in a close location to each other, probably they all Tee off within a 500mm area of the 22mm main pipe, could this cause one radiator to be bypassed by the main flow and just receiving a trickle from the Flow.
I have tried various things like turning radiators off and balancing the system which has improved things but not solved them, any thoughts?
The system is:-
I am having a few problems with my radiator system, I have had a new boiler fitted earlier this year and I have also fitted an additional radiator as well as rerouting the pipework to another radiator, this was all earlier in the year, but it's not until now the temperature has dropped that I jhave noticed the problem.
My problem is that one room isn't getting to temperature, I have one radiator which is noticeably cooler than all the others on one that is slightly cooler than the others, both are new and in the same room, they are fed from above indipendanly tee'd into a 22mm pipe with 15mm pipe (Close together).
The area that I think is the problem has 4 radiators Tee'd off in a close location to each other, probably they all Tee off within a 500mm area of the 22mm main pipe, could this cause one radiator to be bypassed by the main flow and just receiving a trickle from the Flow.
I have tried various things like turning radiators off and balancing the system which has improved things but not solved them, any thoughts?
The system is:-
- Combi Boiler "Potterton Titanium 33"
22mm pipework for Flow and Return
15mm Branch pipes to each radiator
underfloor heating system
It has been Flushed
all radiators have been balanced to 1/2 turn on lockshield
15 Radiator system
Mainly all TRV's