Myself and a gasfitter on these forums are off to look at a combi-boiler install tomorrow that I did last Christmas. All central heating pipework was pressure tested prior to fitting the boiler and passed a pressure test at 5 bars.
Since the boiler has been installed the pressure is dropping every day, usually by around 0.3 - 0.5 bars. I've checked everything I can think of and I'm still at a loss, especially as there are no signs of a leak and this sort of pressure drop equates to a loss of around 1 litre a day. This would certainly be noticeable.
FACTS SO FAR: -
The leak occurs whether or not the CH is on, we've left the heating off for a day and it still does it.
The PRV isn't leaking at all.
The expansion chamber is working fine, pressure rise on heating up is around 0.2-0.3 bar, pretty normal.
There are no signs of leaking from inside the boiler.
The pressure gauge definitely isn't faulty as the boiler is cutting out when it drops to 0.4 bar (the low pressure switch for this boiler - a Broag Avant Plus 39C combi). This is how we first found the problem.
I have been over all pipework in the house with an infrared camera. There are no signs of anything unusual, i.e. no black patches indicating damp.
All radiators downstairs are fed by microbore pipework inside dot and dabbed walls. There are no CH pipes running under the ground floor.
2 inaccessible dead legs (the old feed and expansion tank pipes) have been capped off with automatic air vents in the loft. Thermal imaging shows both of these pipes are full of water.
All radiators are full of water.
I'm at a complete loss, does anyone else have any ideas? If we can't sort it tomorrow we are looking at re-plumbing the whole system to stop the problem. Definitely not a cheap option for my customer.
Myself and a gasfitter on these forums are off to look at a combi-boiler install tomorrow that I did last Christmas. All central heating pipework was pressure tested prior to fitting the boiler and passed a pressure test at 5 bars.
Since the boiler has been installed the pressure is dropping every day, usually by around 0.3 - 0.5 bars. I've checked everything I can think of and I'm still at a loss, especially as there are no signs of a leak and this sort of pressure drop equates to a loss of around 1 litre a day. This would certainly be noticeable.
FACTS SO FAR: -
The leak occurs whether or not the CH is on, we've left the heating off for a day and it still does it.
The PRV isn't leaking at all.
The expansion chamber is working fine, pressure rise on heating up is around 0.2-0.3 bar, pretty normal.
There are no signs of leaking from inside the boiler.
The pressure gauge definitely isn't faulty as the boiler is cutting out when it drops to 0.4 bar (the low pressure switch for this boiler - a Broag Avant Plus 39C combi). This is how we first found the problem.
I have been over all pipework in the house with an infrared camera. There are no signs of anything unusual, i.e. no black patches indicating damp.
All radiators downstairs are fed by microbore pipework inside dot and dabbed walls. There are no CH pipes running under the ground floor.
2 inaccessible dead legs (the old feed and expansion tank pipes) have been capped off with automatic air vents in the loft. Thermal imaging shows both of these pipes are full of water.
All radiators are full of water.
I'm at a complete loss, does anyone else have any ideas? If we can't sort it tomorrow we are looking at re-plumbing the whole system to stop the problem. Definitely not a cheap option for my customer.