As for price, I would pay £300 a tube for something that was always 100% reliable. £500 if it was overseas work :eek:

Our work goes into TV & film studios with 400v power cables strewn across the floor, £200k per day downtime costs etc.. threaded fitting are not the most popular subject in our workshop..

Try calling the Henkel/Loctite Technical hotline:

Contact & Services - Loctite

I've never called them myself, but they're a serious outfit so I'd expect them to know their stuff.
 
Try calling the Henkel/Loctite Technical hotline:

Contact & Services - Loctite

I've never called them myself, but they're a serious outfit so I'd expect them to know their stuff.

I did just before posting on here - they transferred me to the right department and all I got was a voice recording saying technical services were down due to a technical fault haha!!!

But yes, given their prominence (and prices) I'm sure on a normal day their tech support is first rate.
 
I can't fathom how you are having so many problems with threaded fittings.
You are obviously having major problems, hence coming on here.

Are you putting the tape on the correct way?
Is the tape not gripping to the plastic fittings and spinning / slipping.
Try roughing the threads up a little, so the PTFE grips to the thread.

We did some waterlines recently that were between 1400kPa & 1600kPa, used PTFE tape on all the threaded fittings and didn't have one drip. The largest fittings were 50mm
 
Hi all, just joined to try and get a definitive answer on this!

When connecting threaded fittings, metal of plastic, what single application thread seal product works best?

We have tried:
  • PTFE + silicone. Virtually always seals but will seep if agitated after cured.
  • PTFE with Fernox general purpose thread sealant, still sometimes seeps on larger threads 1" or over, and can also fail if agitated after cured.
And also just silicone on some ABS/PVC threaded fitting, as advised by the manufacturer (PTFE can react apparently).

We have to quite often adjust the layout of the kit we assemble and we need to be able to make and break threaded connections relatively quickly, cleanly.

Many thanks in advance

David


The equipment itself is mostly pool filters/pumps. Which are normally all done with solvent weld. But we have to make the kit modular, mobile and very tough[/QUOTE]

Pool pumps & filters are quite low pressure things even on 2" so don`t see why you struggle.
You tried these?
Mega Union coupler | Bosta UK Ltd
Come threaded for plastic or metal pipes or solvent weld
 
Pool pumps & filters are quite low pressure things even on 2" so don`t see why you struggle.
You tried these?
Mega Union coupler | Bosta UK Ltd
Come threaded for plastic or metal pipes or solvent weld

Yes we use hundreds of those a year. Fantastic as the seal is perfect each time and allows components to be switched out in moments, tool free. But sadly the pump/filter ports themselves are threaded, so threaded seal connections still exist in the system. We don't struggle so much with the pool kit really though. But when we have 3000 solenoids all with threads going into a single distribution manifold, all of which have to be (and remain) leak free, even a 99% success rate would mean 3 leaks per assembly. So that's why we're looking for quick and foolproof sealants to use.
 
I can't fathom how you are having so many problems with threaded fittings.
You are obviously having major problems, hence coming on here.

Are you putting the tape on the correct way?
Is the tape not gripping to the plastic fittings and spinning / slipping.
Try roughing the threads up a little, so the PTFE grips to the thread.

We did some waterlines recently that were between 1400kPa & 1600kPa, used PTFE tape on all the threaded fittings and didn't have one drip. The largest fittings were 50mm

Not major problems, it's just the sheer number of connections and importance of zero drips that makes me seek the ultimate product/method.

But what you have said is quite concerning. PTFE is not generally good for plastic threads. It increases the internal pressure on the female fitting, which combined with a medium to long term reactions with certain plastics can cause the fitting to split. We have had that happen. As your lines were 14bar pressure any such additional pressure on the fitting could be critical.

The thing is, I agree PTFE does work very well on plastic fittings. Initially. But it's a thread lubricant, sot sealant. Any future agitation and drips tend to start. And over time as the tape shifts and compresses the same can happen. But the worse thing is, the reason it works so well on plastic is it allows you overtighten the fittings - causing a fantastic seal initially but at the expense of over-stressing the female fitting.

It does depend entirely on the type of plastic fitting of course. If it were a GF reinforced PP fitting, as many pressure fittings are, then no problem. That stuff's near indestructible. But ABS and especially PVC, teflon tape is really not correct.

We genuinely have had quite a few 1.5-2" PVC threaded fittings split due to the use of PTFE. None were above 3bar pressure. And none split due to water pressure, it was the non-design force from the PTFE that did it. Most common when we combined PTFE with silicone as this made over-tightening very easy by even the most sensitive of hands. That was in the early days and not used PTFE of plastic since.
 
How many wraps do you do with PTFE tape on each size of fitting?

If someone asked me for a quick and fool proof method of sealing a threaded joint - I would reply PTFE tape.

For pool equipment under minimal pressure, I wouldn't consider using anything else on any size of fitting
 
My post may seem not to answer the question - we were posting at the same time.

If you are having fitting split after a while due to stress on the fitting due to PTFE tape, I would find another type of fitting.
I would put that down to the quality of the plastic in the fitting not the jointing method
 
How many wraps do you do with PTFE tape on each size of fitting?

If someone asked me for a quick and fool proof method of sealing a threaded joint - I would reply PTFE tape.

For pool equipment under minimal pressure, I wouldn't consider using anything else on any size of fitting

It really depends on the exact scenario and fittings to hand. Generally 3-4. That doesn't remove the issue of extra pressure on the female fitting though as you don't know whether or not the tape shift/creases/folds as it's tightened. 4 wraps could in one spot be the equivalent of 7 wraps.

You're outside of most manufacturers advice when it comes to the use of PTFE on plastic. Although, if you're not willing to consider anything else, I guess you have no option!

The only manufacturer I have spoken to that does say teflon tape is ok is spears. But even they stipulate no more than two tooled turns of the threads beyond finger tight. Effectively leaving at least half the thread exposed in most cases. And in any case, they like others prefer the use of sealant in general.

It also has little to do with line pressure. Yes swimming pool kit is relatively low pressure. But I have seen pvc fittings split due to PTFE use on drained systems sat in storage.
 
My post may seem not to answer the question - we were posting at the same time.

If you are having fitting split after a while due to stress on the fitting due to PTFE tape, I would find another type of fitting.
I would put that down to the quality of the plastic in the fitting not the jointing method

We do keep crossing posts but all useful stuff!

Yes I agree. and per my last post, this may well be why Spears are OK with PTFE tape. The quality and conformity of their fittings is above average imo. Perhaps the worse fittings we have come across are the 'mega' fittings range. We once had a union roll off onto the workshop floor and split. We ripped it apart for a closer look and there were voids in the PVC wall!! I would think that more premium fittings are weighed during production for conformity.


But still the fact remains - PTFE can apply spot pressure to the female fitting which increases failure potential. And it will often drip if agitated after an initially successful seal. It's a common enough problem and if you google it, it's not hard to find examples and various experts explaining at length the reasons why it's not ideal.
 
So.. the 5776 arrived this morning. I grabbed a couple of old 1.5" fittings, one brass, one stainless and applied to product to the male thread, and finger tightened. I left it about an hour and noticed the product was still fully liquid, I had expected it to gel over at least. But anyway, it said it would work after a few minutes so I hooked it up to a pressure tank we have and then wound the pressure up to 3 bar. That was 2 hours ago and no drips. Not bad for old fittings, finger tight and no real care in the application of the product.

So I'm very happy so far! It still hasn't 'cured' in any way. I'm not sure if it will - but clearly whatever it's doing inside the threads in working. It's also locked the two fittings together very well. I'm sure I could break them apart if I tried but already better than PTFE when it comes to resisting movement.

When i've broken the fittings apart I'll repeat the test, this time applying pressure after just a few minutes. I have a feeling it'll still work fine.

I haven't had chance to try the plastic thread sealant yet, but I'm optimistic based on how well the metal thread sealant works.

So thankyou to all who contributed to this thread - I'm very grateful! :)
 
It won't cure for a long time you can wipe it away once you've finished tightening to make it look neat
 
It won't cure for a long time you can wipe it away once you've finished tightening to make it look neat

Good to know. And yes it's certainly neater than general sealants we have bought over the counter in the past. This is far better. Even at the price, which is irrelevant really if it works this reliably.
 
5776 is an 'anaerobic cure' adhesive. For it to cure it requires (a) absence of air (oxygen in fact) and (b) the presence of metal. See here for details:

Thread Sealant | Thread Sealing | LOCTITE® - Henkel Adhesives North America

So, the reason your excess doesn't cure is that it is in contact with air. Clever stuff.

Indeed. I had assumed it would cure due to moisture in the air as many other products do. Far cleverer this way though - gives me a virtually instant seal yet overspill can be easily cleaned no matter how long it's left.

It's exactly the type of high tech solution I was hoping to find. Bit neater than the old fashioned way too haha!

plumber-putting-hemp-fibers-thread-closeup-61335192.jpg
 
Hope that is a left handed thread in the picture.

Good spot! I was about to say maybe the image is reversed but looking closely I can see the direction of the thread :D

And that image was from some sort of guide/tutorial I think!
 
Good spot! I was about to say maybe the image is reversed but looking closely I can see the direction of the thread :D

And that image was from some sort of guide/tutorial I think!
TBH, anyone copying that would end up having the problems you experienced and some of the things you said about PTFE tape and fittings, lubricant, sealing and split fittings :eek:
I`ve never had any of the issues you talk of in 40yrs.
 
I`ve never had any of the issues you talk of in 40yrs.

You've never used just PTFE on threads and had a drip occur? That's very good going! I'd say we get a drip/seep per 50 or so connections. But that's critical for us. We have to make hundreds in a single assembly sometimes and all extremely tight and hard to access. Also, we can't pressure test as the systems are not closed, or closeable. We really just needed a virtually impossible to fail solution - which it seems we have now.
 
Oh I`ve had drips and seepages which I nip up or add a smear of something on top of the PTFE, even binned fittings if in doubt but the other stuff you talk of, no never! Perhaps it is the quality of the tape and fittings or the experience of how tight is tight that makes the difference.
 
Oh I`ve had drips and seepages which I nip up or add a smear of something on top of the PTFE, even binned fittings if in doubt but the other stuff you talk of, no never! Perhaps it is the quality of the tape and fittings or the experience of how tight is tight that makes the difference.
Failure to make a perfect seal is the only problem we have that is frequent enough to cause an issue. The splitting fittings was from a long time ago and due to PTFE combined with silicone. Which does make a perfect seal everytime, but also makes it extremely easy to over-tighten.

Sadly we just don't have the time to cope with little drips. If it was plumbing in my house I'd just sigh and do the connection again. But commercially, If I have 300 threaded fittings built into a slim case that requires makes access almost impossible without disassembly, then I stand to lose a lot of time for the sake of just one failed connection.
 
Status
Not open for further replies.

Similar plumbing topics

I've tidied up this thread and banned a user...
Replies
2
Views
1K
I used a Loctite 577 and the activator in the...
Replies
12
Views
5K
  • Question
I think it's likely you want to use a 3/4" BSP...
Replies
9
Views
2K
  • Locked
Whatever you use, pressure test before tiling.
Replies
3
Views
3K
If you ask a question on site looking to learn...
Replies
4
Views
3K
Back
Top