at what point and in what system is that likely to happen?

It can and does happen at stagnation and the excess pressure taken up by the expansion vessel. But it all returns to liquid again as the collectors cool down.

Eco


Agree'd. Got called out to a system that had gone down. The customer had tried opening Auto Air Vent herself in the loft. The system must have been well stagnated because she still had burns from the steam all down her arm.
 
I did the solar course and then went to Alpha's product training. They were only concerned about the connections immediately off the panel and supplied fittings for that purpose. Manufacturers instructions prevail in my book that's what I go by same as gas appliances.

Clearly Alanka has not attended a solar course otherwise he would not be giving the wrong answer!

Thats the trouble with these internet forums with anonymous posters, you have no way of knowing if they are qualified or not!

At least Buster realises the temperatures can get very high and he knows that soldered connections are not permissable but he then suggests that plastic and pushfit connections are better! I am sure that on reflection he will realise that plastic fails just over 100° whereas soldered copper can stand 300° !

Solar panels should only be connected with compression joints! Silver soldered or brazed joints would also be acceptable but are not usually practiced for heating in the UK.

Tony

Mr Agile,

At what point did buster mention Plastic?
 
Last edited by a moderator:
I did the solar course and then went to Alpha's product training. They were only concerned about the connections immediately off the panel and supplied fittings for that purpose. Manufacturers instructions prevail in my book that's what I go by same as gas appliances.



Mr Agile,

At what point did buster mention Plastic?

So Alpha panels as long as you us their panel connectors you can then run in what?
Copper with soldered joints?
 
at what point and in what system is that likely to happen?

It can and does happen at stagnation and the excess pressure taken up by the expansion vessel. But it all returns to liquid again as the collectors cool down.

Eco


At what point does the system fluid expand 500 times it's volume? If tony could have explained he would have, perhaps you can tell us. This is a sealed system we're talking about with a cold pressure of perhaps 1-3bar, remember this is guage pressure so, atmospheric pressure?. I'm struggling with the idea of thousands of litres by volume being contained(no mention of the prv at this point. Not to mention the fact that when water(the major constituent of transfer fluid) flashs to steam it expands 1600 x it's volume.


Tony stone
 
Tony

The expansion of the HTF is taken up by the "expansion vessel" in normal circumstances, the PRV does is not normally operate only in extreme stagnation i.e power or pump failure at peak radiation. The vaporisation of the HTF only takes place in the collectors and a small portion of the pipe work so it is only that volume that expands. A correctly sized expansion vessel can take the increased volume without increasing system pressure. The higher the system running pressure the higher the boiling point of the HTF so the less chance of vaporisation.

Hope this helps.

Eco
 
So Alpha panels as long as you us their panel connectors you can then run in what?
Copper with soldered joints?

That is correct Ecowarm. I distinctly remeber the question in the little micky mouse test you get at the end like most manufaturers product courses. They were adamant about using the flexi-pipes supplied with compression fittings and from there you can go in copper.

just checked the Mis they actually state you must use copper tube & compression fittings between the collectors and the drainback unit.
 
Last edited by a moderator:
That is correct Ecowarm. I distinctly remeber the question in the little micky mouse test you get at the end like most manufaturers product courses. They were adamant about using the flexi-pipes supplied with compression fittings and from there you can go in copper.

Yes I agree but not with soft soldered joints?
 
Another person who needs to go on a Solar Course!

Its not a gas boiler! You cannot just turn off the sun when it gets too hot !

Steam can be at any temperature and expands by about 500 times the volume when opened to atmosphere from pressure.

Go on the course!

Tony

i work with steam and was taught it expanded 1600 times the volume when opened to atmosphere

sorry just noticed some1 else stated this
 
Last edited by a moderator:
Tony

The expansion of the HTF is taken up by the "expansion vessel" in normal circumstances, the PRV does is not normally operate only in extreme stagnation i.e power or pump failure at peak radiation. The vaporisation of the HTF only takes place in the collectors and a small portion of the pipe work so it is only that volume that expands. A correctly sized expansion vessel can take the increased volume without increasing system pressure. The higher the system running pressure the higher the boiling point of the HTF so the less chance of vaporisation.

Hope this helps.

Eco

Eco,
I should apolagise to you as my previous post was really aimed at Agile who I didn't expect to reply as he never does when shown to be wrong (on any of the other forums we post on)

I have a few years real world experience of supplying and installing solar thermal systems so my views are at odds with the likes of Bpec and their qualified engineers such as Agile😉

The very first mistake made in the solder can/cant be used arguement is to lump all systems types and sizes together. So just to clarify my remarks below will refer to the average domestic system installed in the UK, not commercial or swimming pool systems that will need carefull installation design consideration.

I agree that all solar collectors should be connected to the system pipework with some form of Mechanical Fitting for a number of reasons. However, that does not mean you cannot use lead free solder on other joints in the system if using copper pipework.

If you were installling an heatpipe system I doubt there is a single collector out there that would lead to System stagnation as opposed to Collector stagnation temperatures that could melt lead free solder, if there is, then I've not come across it yet and doubt I ever will.

If you were installing a self limiting heatpipe system like the Thermomax HP200 or the Viessmann Vitosol 300-T or indeed the Narva heatpipe. All limited to around the 160c mark, why not use solder?

Direct flow systems are a different beast. the Thermomax DF100, AMK Solac or Ritter along with some of the better flatplate collector systems can and do stagnate at very high temperatures. If they vent they can produce large amounts of steam (they have to vent to produce large volumes) that can extend down as far as the cylinder coil where it will condense out. The steam zone when extending this far is likely to have passed into some of the system components none of which will be rated above 160c for brief periods. Many of the boiler manufactures re-baged kits come with Spirovent air scoops rated at 180c. On some systems they can allow a tremendous amounts of steam to escape, once that starts it will not stop until the system is vertually dry or the systems cools.

We repaired a Smart Energy AMK system last week that had around 1 litre left form a 12 litre fill. Having vented, it filled their airing cupboard and hallway with steam which scared the living daylights out of them. The only component changed was teh PRV fitted to teh collectors. Most of these types of systems are NOW installed using pre-insulated stainless flexi pipe the insulation is rated at 170c for brief periods. The insulation had not melted anywhere in that system.

I have said this before and it always causes a row. Solar thermal isn't new there has been a very small industry since the 70's when most systems were garage built flatplates or used the then NEW fangled Phillip's tubes and later the Thermomax tube systems. These were often installed using solder so whats changed? perhaps the noise😉


Let the games begin(again)😀

Tony Stone
 
Tony

Thanks for the apology
As for your dislike of bpec trained installers your web site I presume is Welcome to Solar Savings and do you or do you not advertise bpec trained installers for solar? [DLMURL="http://www.solarsavings.co.uk/article/show/18"]Solar Thermal Reapairs and Installation Service[/DLMURL] if this is not you then I also appologise


As for Smart energy ...... they put an spiro air vent on there systems and when stagnation takes place it thinks its air and vents glycol all over the airing cupboard.
 
Last edited by a moderator:
Tony

Thanks for the apology
As for your dislike of bpec trained installers your web site I presume is Welcome to Solar Savings and do you or do you not advertise bpec trained installers for solar? [DLMURL="http://www.solarsavings.co.uk/article/show/18"]Solar Thermal Reapairs and Installation Service[/DLMURL] if this is not you then I also appologise


As for Smart energy ...... they put an spiro air vent on there systems and when stagnation takes place it thinks its air and vents glycol all over the airing cupboard.

I do not have a dislike of Bpec "trained"😀 installers I know and work with lots them. Yes we have all had to sit the bpec SDHW I wouldn't be able to voice such strong opinions about it otherwise. We had to sit the assessment for the MCS and insurance purposes, something we were forced to do I wouldn't be able to voice such strong opinions about it otherwise. Incidentally, the first thing the guy taking the course said was "I know this is out of date" and went on to say how it was being updated at the moment. Strange then that it hasnt been in the last five years🙄 I don't agree with many of the things I'm forced to be a part of including the competent person scheme either, but at least they use current and relevant information.

As you are probably aware the MCS was set up by suits with vested interests to get control of the renewables market in much the same way they rob us in the gas industry too. However, the mcs is much much worse. They have been able to set up and run the scheme in such a way that most would think it wants to ailienate the small installation company, surely that wasnt their intention? make it so difficult that they would leave the market or use the klikes of WB with their MCS made easy. From next year even the book keeper/s employed by MCS approved companies will need to have sat an assessment.


You re-make the point i made about the spirovent😉
 
Last edited by a moderator: