A (if) CH system has a very high head loss due to improperly sized pipework and long runs and possibly partially blocked pipes and requires a UPS2 pump running at its 8M head to feed 21 rads with a theoretical output of 25kw at a 20C dT.
A fairly old Vaillant 438 boiler is being replaced, the boiler is range rated to 24kw so a 25kw replacement boiler should be adequate.
One choice is a 25kw system boiler but because of the very high head required which will still, more than likely be ~ 6M after the system is cleaned, then a LLH or CCts will be required as the max head after passing through the (system) boiler HEX will probely only be ~ 2M at its rated flow rate of 17.92LPM, 1075LPH, also the internal bypass has a maximum setting of 4M, (before the HEX).
The other choice is to install a 25kw heat only boiler and use the existing UPS2 pump and the existing ABV. Question is, assuming a 8M head is still required (even though unlikely) at the rated flow rate, does this cause any problems for the boiler HEX, etc?.
A fairly old Vaillant 438 boiler is being replaced, the boiler is range rated to 24kw so a 25kw replacement boiler should be adequate.
One choice is a 25kw system boiler but because of the very high head required which will still, more than likely be ~ 6M after the system is cleaned, then a LLH or CCts will be required as the max head after passing through the (system) boiler HEX will probely only be ~ 2M at its rated flow rate of 17.92LPM, 1075LPH, also the internal bypass has a maximum setting of 4M, (before the HEX).
The other choice is to install a 25kw heat only boiler and use the existing UPS2 pump and the existing ABV. Question is, assuming a 8M head is still required (even though unlikely) at the rated flow rate, does this cause any problems for the boiler HEX, etc?.