Hi all. As most of you will know I've gone back on the cards now and am now fault-finding one of our commercial hot water systems in a 5,800sq.m building. It's a large building on a hospital site.
The hot water system is an old system! Heating is run from a steam feed from the main hospital and that heats the water in 2 very large calorifiers (3000 litres each). The water is heated to 65C in these and is then pulled around the system with the standard 2x pumps (one on, one standby) on the hot water return.
The hot water flow pipework is in 54mm and quickly splits off into 6x 35mm 'risers' feeding different parts of the building (6 branches really, all pipes run through between the 2 floors). The issue is that hot water return temperatures furthest from the boiler on some risers are down to 37-42C, and there is a legionella problem in the system. No shock there! When you open hot taps in the affected areas the temperature will then rise by up to 5C before dropping back as soon as the tap is closed. In the affected areas the water temperature doesn't even get up to 50C when running the hot tap.
From having inspected two risers (they are above suspended ceilings) I see no balancing/gate valves on the main return pipework. What I do find odd though is that every individual tap has it's own tee'd off hot water return pipework. The end result is there are loads of loops for the water to follow to get back to the calorifiers on each riser.
I suspect that the hot water is following the shortest routes back to the calorifiers and there are large stagnating areas where recirculation is not occurring. I don't see the point in the hot water return pipework to individual taps (they are all within 5m or so from the main pipework) and feel it complicates the system. My plan is to remove all of them and fit automatic balancing valves on the return leg of each riser in order to properly balance the system - something like the Honeywell Kombi 4.
All the schematics I see online show taps etc connected to the hot water flow pipework only, I'm assuming connecting them all to flow and return is wrong and is going to cause this issue I have surely?
Anyone else got any thoughts? Have spoken to our commercial plumber we contract in and he agrees with me but wanted to get other people's ideas before briefing management on Friday!
Thanks a lot in advance for all advice.
The hot water system is an old system! Heating is run from a steam feed from the main hospital and that heats the water in 2 very large calorifiers (3000 litres each). The water is heated to 65C in these and is then pulled around the system with the standard 2x pumps (one on, one standby) on the hot water return.
The hot water flow pipework is in 54mm and quickly splits off into 6x 35mm 'risers' feeding different parts of the building (6 branches really, all pipes run through between the 2 floors). The issue is that hot water return temperatures furthest from the boiler on some risers are down to 37-42C, and there is a legionella problem in the system. No shock there! When you open hot taps in the affected areas the temperature will then rise by up to 5C before dropping back as soon as the tap is closed. In the affected areas the water temperature doesn't even get up to 50C when running the hot tap.
From having inspected two risers (they are above suspended ceilings) I see no balancing/gate valves on the main return pipework. What I do find odd though is that every individual tap has it's own tee'd off hot water return pipework. The end result is there are loads of loops for the water to follow to get back to the calorifiers on each riser.
I suspect that the hot water is following the shortest routes back to the calorifiers and there are large stagnating areas where recirculation is not occurring. I don't see the point in the hot water return pipework to individual taps (they are all within 5m or so from the main pipework) and feel it complicates the system. My plan is to remove all of them and fit automatic balancing valves on the return leg of each riser in order to properly balance the system - something like the Honeywell Kombi 4.
All the schematics I see online show taps etc connected to the hot water flow pipework only, I'm assuming connecting them all to flow and return is wrong and is going to cause this issue I have surely?
Anyone else got any thoughts? Have spoken to our commercial plumber we contract in and he agrees with me but wanted to get other people's ideas before briefing management on Friday!
Thanks a lot in advance for all advice.