Dannyparty92

On a y plan system on heating only Does the three port have a live grey wire from the programmer?
 
My wiring knowledge is pants :)

but if you've got an iPhone then download the Honeywell wiring app. It's amazing and helped me loads.
 
Yes the grey will be live on ch only.
 
I have said application haha. Thank you whn1. So could you please explain to me why there's a HW off and HW on but only a CH on and not a CH off? Why does the valve have to have a live when from HW off?
 
Because the resting position of the valve is hw fully open. So the spring pulls it back
 
Yes otherwise how would the boiler know when to fire? Or when would the valve know when to hold the mid position.
 
book yourself on the honeywell course and life will be simpler
 
How good is the honeywell course, worth the money? Does the training they provide come in handy often? for different situations eg fault finding and wiring new systems or adding new components such as a new programmer?
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Its a very ingenious but devilishly cunning...
2
Replies
25
Views
3K
  • Question
Thanks for the replies, turns out it was a...
Replies
6
Views
1K
S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
194
S
  • Question
3 port could be on its way out?
Replies
3
Views
2K
Deleted member 120897
D
Finally got an update from him. He cant do the...
Replies
2
Views
841
Back
Top