Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Timer replacement on a y plan system in the Plumbing Jobs | The Job-board area at Plumbers Forums

jaydebruyne

Plumbers Arms member
Plumber
Gas Engineer
Messages
2,718
So went to a job today, replaced an old Randall 130 mechanical timer with a Honeywell st9400c on a y-plan system.

Water channel fine. Heating channel was fine in that it sent a signal (if the room stat was calling) to the 3 port, but nothing on SL. Figured a faulty head. Replaced the head and same thing. So took off the head and manually moved the paddle and seems free as a bird.

I’ve said to the custard I need to drain down and replace the entire valve as I don’t think it’s pushing far enough to make the connection.

Thing is, when demand is on heating and the actuator kicks in, I can hear the micro switch click at the end (unless it’s the spring I can hear but I doubt it), but still nothing on SL.

Am I missing something obvious here? (Can you hear the 2nd guessing???)
 
so you have 240 on heating calling and hot water (seperately) ?
 
I have 240 coming from the thermostat to the white on the 3 port when heating is in demand, nothing on water if not in demand.

Same with water and nothing on the heating ?
 
Same with water and nothing on the heating ?
But if I’m getting 240 on the white and the actuators moving over why wouldn’t that send 240 to SL (orange)? Unless the paddle isn’t moving over enough to make the connection..
 
Last edited:
Correct doesn't need much for it to not contact
 
But if I’m getting 240 on the white and the actuators moving over why wouldn’t that send 240 to SL (orange)?
If you are talking about CH only, there needs to be 240V on the grey wire (from HW thermostat Sat/Programmer HW Off) as well as 240V on the white wire from room stat.

In mid-position (CH and HW) the boiler gets its SL directly from the HW thermostat, not via the orange wire.
 
If you are talking about CH only, there needs to be 240V on the grey wire (from HW thermostat Sat/Programmer HW Off) as well as 240V on the white wire from room stat.

In mid-position (CH and HW) the boiler gets its SL directly from the HW thermostat, not via the orange wire.
Stupid f***ing 3 ports :D I wondered if that was needed but thought if the actuator was in operation after getting 240 on the white it would make the connection..
 

Similar plumbing topics

  • Question
Its a very ingenious but devilishly cunning...
2
Replies
25
Views
3K
John Thank you for all your help, changed the...
Replies
13
Views
2K
  • Question
Here's an attachment of the PDF if people are...
Replies
1
Views
3K
Thanks, will drop that one out when doing the...
Replies
7
Views
2K
Ok thanks, doubt it’s that then. I think I...
Replies
11
Views
1K
Back
Top