Guys,
I am just changing my own heating system to a sealed system (not the hot water, just heating) because I added a circuit and needed to move the pump, now the Vent and F and E tank are on the pumped side of the pump.
Expansion vessel sized and fitted, and open vent sealed off with a bottle air vent, (or will be) but I have 2 questions...
1, can I use the F and E tank as a "top up bottle" instead of using a mains filling loop? Checking my understanding...I think I can, so long as I can fill the system, then seal it, I don't see an issue.
2, If so, can I simply use it manually, with a gate valve or do I need to fit a non-return valve and have automatic top-up, is this the best of both worlds, or does it just mask leaks? I think I can do either.
Two advantages as I see it...
1, minimum pressure, as only enough to fill the system is needed.
2, less work!! never a bad thing!
Thank you.
I am just changing my own heating system to a sealed system (not the hot water, just heating) because I added a circuit and needed to move the pump, now the Vent and F and E tank are on the pumped side of the pump.
Expansion vessel sized and fitted, and open vent sealed off with a bottle air vent, (or will be) but I have 2 questions...
1, can I use the F and E tank as a "top up bottle" instead of using a mains filling loop? Checking my understanding...I think I can, so long as I can fill the system, then seal it, I don't see an issue.
2, If so, can I simply use it manually, with a gate valve or do I need to fit a non-return valve and have automatic top-up, is this the best of both worlds, or does it just mask leaks? I think I can do either.
Two advantages as I see it...
1, minimum pressure, as only enough to fill the system is needed.
2, less work!! never a bad thing!
Thank you.