Tundish leaking water.... advice sought | Bathroom Advice | Page 2 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Tundish leaking water.... advice sought in the Bathroom Advice area at Plumbers Forums

J

Jonna

Hi All,

First post...

I bought a new Bellway house last year and have had a few probs with it since moving in. After around 4 months (December 2010) I noticed damp in the kitchen ceiling below the cylinder. On inspection the water (cold) appeared to be leaking from the tundish, which tuned out to be the result of a frozen blow-off waste pipe outside. The plumber stopped the leak (no idea what work was carried out), and added lagging and a cover to the external pipe.

On Sunday, I noticed water dripping from the ceiling again in the kitchen... same issue as before, water appears to have been leaking from the tundish. No blockage in the external blow-off drain however, in fact there are signs that a large amount of water has been draining outside. Plumber came, but suggested he'd need to take the ceiling out in the kitchen to locate a fault in the blow-off drain - he advised he'd have to come back later.

Came in tonight and noticed more water in the ceiling and more outside. There's also evidence that water has been overflowing from the tundish...

I'm waiting for a call back from Bellway regarding the plumber, but was hoping you guys could clarify...

1. Why the tundish? This thing doesn't appear to be capable of managing a heavy flow of water, and when a heavy flow (i suspect) does ensue, water pours out, down the outside of the pipe onto my kitchen ceiling.

2. Any ideas what would cause a constant dripping of cold water through the tundish? (faulty blow-off valve perhaps, or too high pressure in the system?)

Thanks. :cry_smile:
 
can you show a photo of the 3rd pipe into the tundish

Here you go... pipework to the aquasystem pressure vessel.

Thanks for the assistance so far fellas. I'm somewhat concerned about comments form GrahamM, though like I say it appears to have been running okay since December.




photo.jpg
 
Thanks for pics

The discharge pipework and tundish is undersized,maybe leaking out from tundish as upper rim scaled as been leaking through a while,need to get a qualified plumber in to trace which safety valve is leaking,why,correct problem ,check installation ok and run correct sized discharge pipework

imho

The discharge pipe work starts at 22mm via compression fitting on tundish - must therefore be designed to take 22mm pipework? The 22mm goes more or less straight into 28mm via reducing coupler. Took the tundish out tonight and blew down the discharge pipe... apart from the odd bit of gurgling, it seemed fairly clear and certainly not full due to a blockage.

Thanks again for your advice so far.
 
The flexi is a standard on the OSO, well the ones I've seen anyway, and I don't agree with it as well, like you said should be copper.

With the extra 15mm going in, as said prob from htg prv, I would have increased d1 to 22mm before tundish and then used 22 - 28 tundish, must be a complicated or long discharge.

Must admit though that I haven't seen a discharging tundish that doesn't put water everywhere, even when everything is 100% to regs. Especially like it when the tundish is right next door to immersion fused spur. :)

As Gray0689 has said though needs pressure vessel and other safety devices checking out.

Make sure the plumber that comes out has his g3.


Plumber ought to have G3 - Bellway are sending the guy and as far as I know, he's from the same outfit that did the original install.

Perhaps you could help on the lingo?

htg prv? heating pressure releae valve?

I assume D1 / D2 relates to the pipework up to and beyond the tundish?
 
Plumber ought to have G3 - Bellway are sending the guy and as far as I know, he's from the same outfit that did the original install.

Perhaps you could help on the lingo?

htg prv? heating pressure releae valve?

I assume D1 / D2 relates to the pipework up to and beyond the tundish?

Spot on.
 
Plumber ought to have G3 - Bellway are sending the guy and as far as I know, he's from the same outfit that did the original install.

Perhaps you could help on the lingo?

htg prv? heating pressure releae valve?

I assume D1 / D2 relates to the pipework up to and beyond the tundish?

Htd prv is the valve with the red knob on top of the red expansion vessel (small red tank)
With pressure gage on it that looks like it has no pressure in it
Correct on D1/D2
Sounds like expansion vessel no pressure or diaphragm split
When heating on water temp rises water expands with heat no where to expand to with expansion vessel full of water then pressure rises and safety valve discharges exess pressure out vie safety valve
Hope this helps explain it to you
 
Hi Gray..

Yeah, this was spotted by the plumber on Sunday. He did recharge it, but whatever caused the loss of pressure initially has since happened again...

Still waiting on a visit from the plumber.
 
Thanks for your input all...

Has anyone seen a 15 into 28 tundish? might stick one in myself or request that the plumber do this when he turns up. A larger diameter might cope with the flow better?

Was also thinking of sticking a hosepipe down the D2 pipework to see how well it handles the flow... if it overspills, I'd at least have justification in requesting the plumber to check it out.

Where exactly is the diaphragm that's been mentioned? I'd imagine the first thing for the plumber to look at would be the prv on the pressure vessel. Then again the water that's dripping through the tundish seems to be cold, and I'd assume it would be hot if coming from the heating prv? - could just be coolling by the time it reaches the tuncdish though.

Thanks again.
 
Thanks for your input all...

Has anyone seen a 15 into 28 tundish? might stick one in myself or request that the plumber do this when he turns up. A larger diameter might cope with the flow better?

Was also thinking of sticking a hosepipe down the D2 pipework to see how well it handles the flow... if it overspills, I'd at least have justification in requesting the plumber to check it out.

Where exactly is the diaphragm that's been mentioned? I'd imagine the first thing for the plumber to look at would be the prv on the pressure vessel. Then again the water that's dripping through the tundish seems to be cold, and I'd assume it would be hot if coming from the heating prv? - could just be coolling by the time it reaches the tuncdish though.

Thanks again.

You can get 22 to 28 mm tundish. All you would need is a 22/15 reducer and job done on that point. I've not read the rest of the thread so excuse me if I missed the point.
 
One use of the tundish is to provide an air gap to allow the discharge to drain freely and safely away without any vacuum resisting the flow.. I was concerned when you mentioned this splashing water. The tundish is an open vessel and to a degree there will be some spillage, but if this spillage is excessive it is incorrectly fitted as far as I am concerned and I have marked a number of installations as 'At risk' because of this in past. At the end of the day this must be capable of handling a stream of high pressure ￾￾water at temperatures as high as 95°C safely. If this is splashing excessively-it is not safe. I check a few of these every week and the vast majority operate safely as they have been designed/fitted so.
Looking at your pics there is what appears to be a horizontal run of 15mm pipe from the temp/pressure relief valve. This is not ideal to start with. This should ideally terminate vertically and run directly into the tundish and should fall continuously to a safe termination in the correctly sized D2 pipework.

I am not aware if you can get a 15 to 28mm tundish but what you may do is fit a 22 to 28mm one and tee into the top in 22mm. This may or may not help the issue. As I mentioned, only someone competent in fitting/inspecting unvented cylinders can advise.
 
Ptfe wrapped round the tundish? Looks like possibly leaking from where the two halfs of the tundish join, pipework could be under tension causing tundish to split, so when valve letting by leaking from this point, seen it before, making a mess of the ceiling below. Still need to suss why a valve is dripping but also replace tundish i would think.
 
I've read all these posts and noticed a couple of things. As you are in Glasgow the pressure will probably be very high in the water main in the area, possibly up to 14bar. The water board will have a PRV fitted to reduce this.
1. Is your incoming main excessively high? If so, then contact them.
2. The tundish looks as if it's been repaired.
3. The tundish should be no more than 500mm from any temp or pressure relief valves. The D1 from your heating looks to be more than a meter.
4. Three D1's should connect to tundish in 22mm.
5. You mentioned gurgling when you blew down D2. This means that water is lying in D2. There should be no water in D2 as there must be a continuous fall. Water lying in D2 could cause an airlock in the pipe and allow it to back up through the tundish.
 
Just thought of something. Your house is 1 year old! I take it you have a HE System Boiler. Why do you have an expansion vessel on your heating? Can you show a pic of the whole cylinder cupboard and pipework?
 

Similar plumbing topics

  • Question
There are 2 ways to know a pump has failed. 1/...
Replies
3
Views
651
G
Just discovered water is constantly dripping...
Replies
0
Views
878
GrahamSE1
G
  • Question
I am glad that you got rid of the smell :)
Replies
4
Views
785
  • Question
Those float valves are easily serviceable and...
Replies
1
Views
803
Replies
2
Views
777
Back
Top