doh😱!i agree that vents are important, but so is careful calculations!!!!!!
20/1.1-7*5= 56cm2, but this isnt accurate, as i said earlier it depends on what fire front is fitted, guys we are trying to advise the OP here and now confusing ourselves, a 45/4E with a PW5 fire needs 82cm2, but if it has a LFE5 fire it needs 86.68cm2 lets get it right or the poor OP is going to rip it all out an get an electric boiler fitted
i agree that vents are important, but so is careful calculations!!!!!!
20/1.1-7*5= 56cm2,* but this isnt accurate, as i said earlier it depends on what fire front is fitted, guys we are trying to advise the OP here and now confusing ourselves, a 45/4E with a PW5 fire needs 82cm2, but if it has a LFE5 fire it needs 86.68cm2 lets get it right or the poor OP is going to rip it all out an get an electric boiler fitted
*Gross input
* net input.like somone has just said vent size (cm2) = (maximum net input in kw-7kw) x 5.*
so if you gas fired back boiler is 20kw:
20kw-7kw =14kw
14x5=70 cm2
a 70cm2 vent is about 100mmx100mm in size, get the correct one from a plumbers merchant.
if the air brick in the kitchen is the correct size needed and of the correct type (any old "hole" wont do) then you only need to put a vent in between the room with the boiler and the room with the air brick, (of 70cm2) if there is three or more vents in series then each vent needs to be increased to be 50% increments ie if you vented from the boiler room into the lounge then into the kitchen which has the outside vents.
Ventilation is very important, dont think that just because it "works" and "has done for years" that it will be ok, it wont one day.