Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Yes, the curve supplied by the OP is for the weather compensator.I'm mixed up I think, the curve you gave is for the outside temp compensation? so can you provide the boiler curve or its basis for changing the SP?
I had a similar problem, for me it was the flow rate sensor, and this was with 100w as well.
I've been working on the 24 hr log you sent me. I have converted it to an Excel file to make analysis easier.There was not a single short cycle after disconnecting outside temperature sensor for more than 2 weeks.
I had a similar problem, for me it was the flow rate sensor, and this was with 100w as well.
If the temperature rises too quickly then cuts burner out it sounds like the plate heat exchanger is blocked in turn locking out as it’s overheating. Had this recently on the same boiler.Hi,
I have noticed my boiler Viessmann Vitodens 100-W(B1HC-26) makes a series of short cycling before starting to heat. Boiler is controlled by Baxi uSense room thermostat connected via Opentherm. I installed some monitoring equipment to get the better understanding of the problem. Bellow is the illustration of the problem:
View attachment 42946
I will explain the graph from the top to bottom:
The graph reveals that it took 10 times for the boiler to fire up until it started to run. Water temperature inside the boiler reaches ~40 degrees very quickly after boiler fires up and then it switches off.
- Green bar indicates heating pump is on
- Red bar indicates flame is on
- Black line indicates max relative modulation level (%)
- Orange line indicates DWH temperature (Celsius) (not relevant in this problem )
- Red line indicates boiler water temperature (Celsius)
- Grey line indicates setpoint temperature (Celsius)
I would appreciate any ideas of how to solve the short cycling.
The OP hasn't replied for five months, so his problem has probably been solved. In any case, he has a system boiler, not a combi, so there is no plate hex.If the temperature rises too quickly then cuts burner out it sounds like the plate heat exchanger is blocked in turn locking out as it’s overheating. Had this recently on the same boiler.