Viessmann Vitodens 222-F: short cycling on hot water call | Central Heating Forum | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Viessmann Vitodens 222-F: short cycling on hot water call in the Central Heating Forum area at Plumbers Forums

Messages
6
I have a Viessmann Vitodens 222-F FS2B 26kW Storage Gas Boiler installed in 2014.

The boiler has developed a problem recently where it short cycles but only when hot water is used.

When hot water is turned on (on any tap in the property) the boiler remains off for about 45 sec. At the beginning the water temp from the tap is very close to the set cylinder temperature of 50C. In about 45 sec the boiler fires up and runs up to 75C, turns off, goes down to 65C, turns on, runs up to 75C and so on. At the same time water temperature from the tap gradually goes down from 50C to about 35C over the course of 5mins (I haven't tested whether it goes further down after that). When the tap is closed the boiler continues the same short cycling pattern for 5-10 mins before going back to steady state where it runs continuously at the same lower temp. The boiler has two pumps - presumably separate pumps for CE and DHW.

What I've tested:

1) With hot water tap opened and the boiler firing I measured the difference between the temp of cold water inlet pipe and DHW outlet pipe and it was around 25C (hot water outlet at 36C and cold at 9C). I was hoping that this test will determine whether plate heat exchanger is free of any blockages. I believe delta T across incoming cold and outgoing hot terminals of the plat of 35C or more suggests the plate heat exchanger is not blocked, but I'm not an expert. In my case it is less than 30C so the result is not conclusive.

2) The secondary pump serving the cylinder seems to be fine - i.e. it has not seized or anything but I can't attest to how effective it is.

I'd appreciate any thoughts/pointers at potential culprits and ways to diagnose.

Thank you
 
Lower the HW cylinder temp and see if the same thing keeps happening.
Well, that's funny. I lowered the cylinder temp from 55 to 40C. The boiler kicked in, slowly climbed up to 69C and ran perfectly fine without any short cycling. But the most interesting thing is that I measured the tap water temp and it was 49-50C and stayed at that level... I'm not sure what to make of it
 
Well, that's funny. I lowered the cylinder temp from 55 to 40C. The boiler kicked in, slowly climbed up to 69C and ran perfectly fine without any short cycling. But the most interesting thing is that I measured the tap water temp and it was 49-50C and stayed at that level... I'm not sure what to make of it
It is possible of course that the reason why water temp was higher than the cylinder temp because the tap was still drawing from the cylinder and if I left it on for a bit longer it'd go down to 40C. So it may not be a significant observation but what is pretty interesting that there is no short cycling when the cylinder is at 40C.
 
I assume you're talking about flow temp which will naturally be higher than set water temp as it heats the store but now with a lower temp set at 40 it's heating the water to 50 deg C.

Time to get someone in, could be a sensor issue.
 

Similar plumbing topics

Thanks for the reply whats the best suggestion...
Replies
2
Views
1K
A gas safe engineer can do the works but they...
Replies
3
Views
1K
If the op has the newer colour display model...
Replies
5
Views
3K
It seems that the power/pump module has failed...
Replies
3
Views
1K
This sounds like a faulty venturi causing the...
2
Replies
29
Views
3K
Winnywood
W
Back
Top