GrahamM

Plumbers Arms member
Plumber
Gas Engineer
Messages
2,044
Called to an 18 month old Vision 30C earlier with poor hot water. Hot water luke warm at best showing a max of 35 deg on boiler display. If slow tap to little more than a trickle the temp gets up around 60 deg eventually. No issues with heating.
Boiler fitted to an old back boiler heating system and central heating water appears clean.
To rule out div valve I isolated flow/return. Gas rate, combustion etc is spot on.
Was thinking towards a blockage of some sort.
Boiler is in warranty and will be passed to Vokera anyway.
Any thought?
 
What's the flow rate through the tap your testing the temp at and what is the incoming cold main temp?
 
Restricted it down to 10 L/min flow and it is tepid water. Turn tap down to about 2 L/min and it is hot.
 
could be debris in plate exchanger resulting in v. slow transfer of heat.
could be super fast forming scale in plate exchanger.
could be divertor valve not operating properly.
check ch flow pipe while hot water running if its really hot that would indicate a faulty divertor
 
Status
Not open for further replies.

Similar plumbing topics

B
  • Question
I’m not familiar with this boiler, but if you...
Replies
1
Views
474
Deleted member 120897
D
M
Hello, We’ve recently moved into a fairly old...
Replies
0
Views
631
MartinPod81
M
Yeah it does mate but probably wasn’t flushed...
Replies
17
Views
326
Replies
25
Views
6K
Called Keston/ Ideal to see if they do fixed...
Replies
5
Views
132
Back
Top