Water pressure for block of flats | Plumbing Zone | All Other Country's | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Water pressure for block of flats in the Plumbing Zone | All Other Country's area at Plumbers Forums

Messages
8
Hi,

I will try to explain best I can, please bare in mind I am currently in a learning stage so just trying to understand the process behind things.

A building with three floors and 69 rooms. How do you work out the pressure needed on the hot water system? I’m sure there is a calculation to work out the flow rate and pressure. Sometimes the top floor experience low pressure on the hot water, I believe it is currently supplied at 2.5 bar.

I would like to try and do the calculations to work out the correct pressure setting.

appreciate any help or advice given.

Thank you.
 
There’s a difference between pressure and flow rate, and there’s a calculation used for working out which each floor needs by a way of working out what is needed to be fed on those floors. More experienced engineers than me might say an accumulator could be used?
 
Upvote 0
There’s a difference between pressure and flow rate, and there’s a calculation used for working out which each floor needs by a way of working out what is needed to be fed on those floors. More experienced engineers than me might say an accumulator could

Thank you for the reply. Do you know the formula for the calculation please? I would quite like to work out the pressure per floor. A hot water expansion vessel is used on the system which is set at 2.5 bar unsure if this is correct or how to work out the correct pressure.
 
Upvote 0
Thank you for the reply. Do you know the formula for the calculation please? I would quite like to work out the pressure per floor. A hot water expansion vessel is used on the system which is set at 2.5 bar unsure if this is correct or how to work out the correct pressure.

2.5 bar cold so let’s say 3 bar per flat and 20lpm how many floors ?
 
Upvote 0

So let’s take 2.6m to allow for dropped ceilings etc that gives you 10.4m need to pump so adds 1.04 bar ontop of your outlet pressure requirement so 4.04 bar required to give you 3 bar 4 floors up

Working on the 70% rule that’s 50 flats needing water at the same time so that’s 1000lpm eg 20lpm for each flat

So 4.1 bar and 1000lpm is your duty cycle
 
Upvote 0

Similar plumbing topics

  • Question
If you are capping off something temporarily...
Replies
2
Views
409
  • Question
I would suggest getting a G3 plumber in to...
Replies
9
Views
592
  • Question
I don't see your comments?
Replies
8
Views
831
  • Question
The problem is likely something blocking the...
Replies
15
Views
2K
  • Question
How high is the hill 40m as that will add 4...
Replies
2
Views
505
Back
Top