Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss What needs to be updated when a boiler is replaced in the Boilers area at Plumbers Forums

Status
Not open for further replies.

Worcester

Esteemed
Plumber
Messages
1,002
Following on from the recent thread: "should i have a room thermostat with my combi boiler. "

Where it was made clear that this is required under the building regs when replacing a boiler, what else must be updated.

When you read the Domestic Building Compliance Guide 2010 ( Planning Portal - Building Services Compliance Guides )

If you take the interpretation that when replacing Gas fired boilers, you need to include for section 5 page 23, (i.e. a room thermostat) then how much else do you also need to change?

What says you do not need to upgrade the zones to section 1,2,3,4 or 6 ?
How do you differentiate? or where are the guides to what does and doesn't need to be updated?
Wher do you stop?

The comments on the thread that triggered this also claim that you need to provide interlock, - then what excludes the requirments to include more than one zone if the property is >150m2 ?

That then triggers the next question - with all the boiler replacements (straight swap) done under ECO, why weren't room stats required to be installed as well if they weren't there already?
 
Reading another thread eleswher they suggest that only the requirment for boiler interlock needs to be met (obviosly normal TRV's won't provide that) presumably that could be met by a zone valve (if one is fitted..)

So who's right? And where do you get that fact / interpretation from?
 
in a word........
the customers £

Nope, we walk from customers if they won't take professional advice, as we know what problems it leads to down the road.
 
So no-one knows?
 
It the customer don't want a room stat I would just note it in the log book offered but declined.

It ends with how much they want to pay. As with all other upgrades I only recommend if I think they have the money for it.
mr cheap combi swap will under cut you on every job in the land leaving you quoting building regs while he counts his wad.
 
Last edited by a moderator:
One of the klan on here emailed Government department some time ago for guidance & a definitive answer to this & received a good reply which I kept (as I teach the Part L), it is at work so will post it up tomorrow.
I think it should be a minimum of TRV's on all rads & towel rads except the room with the thermostat to provide the interlock for any boiler change.
 
Trv are recommended , interlock is required there are no choices on this time and temp interlock is mandatory . Also if in unheated space pipes must be lagged. - spoken to LABC a few times. You install a new boiler you have to meet building regs - they are above gas safe, gas safe is only there to comply with building regs. If your an illegal installer you are supposed to be chased by building control as GS don't have remit.

If over 150 must be zoned with separate interlock. ( only on new installs and or where significant changes to pipework / system) like for like isn't included in this as mandatory requirement just recommendation.
 
Thanks, I was trying to find what MUST be done under Building Regs, as opposed to what is the best to do:)

We will always try to do the best, however the challenge is sometimes, you've got what you've got...
Because of the scale of the cost of the replacement work that we do, and the changes to they way the new system should be used, the client will usually adopt any recommendations (within reason) that we make.

@Chris Watkins, much appreciated that would be awesome.
 
That wont pay bills. We need money to survive...
Any body that will sell themselves just for money really needs to take a long hard look at their life in my opinion !
I could live in my van and survive on next to nothing before I sell myself and my beliefs !
 
One of the klan on here emailed Government department some time ago for guidance & a definitive answer to this & received a good reply which I kept (as I teach the Part L), it is at work so will post it up tomorrow.
I think it should be a minimum of TRV's on all rads & towel rads except the room with the thermostat to provide the interlock for any boiler change.

I think Chris is right, partly because he is ALWAYS right!
There are a number of old threads on this.
AND i remember asking the very same question about 2 years ago - asking where the answer was in official black and white.
I'm sure Chris will come back on this and I will also try to dig up the reference.
 
...You install a new boiler you have to meet building regs - they are above gas safe, gas safe is only there to comply with building regs. If your an illegal installer you are supposed to be chased by building control as GS don't have remit.

...
This isn't how I would explain the difference between GS and LABC - they are disrinct bodies with different remits created because of totally different legislation.

illegal installers are NOT chased by BC
and
GS is NOT there to comply with Building Regs

LABC - we know what they do - monitor & enforce building regs.
Building regs include stuff about heating, insulation, ventilation etc - so we need to know about them.

GS are set up under the Health & Safety Executive - to do with monitoring & enforcing that bit of the Health and safety legislation that we know and love - the Gas Installation & Use Safety Regs.

GSR do have an important role in catching illegal gas insrallers - they are the first people to report illegal installers to. GSR exist under the HSE it is the HSE who may investigate and actually do the prosecution.

In recent years under BUilding regs MANY competent persons schemes were set up - so that installers (eg. windows, electrics, gas heating, oil heating) could self certify that their work complies with building regs.
This means that the the Building Control officer does not need to inspect it.

GSR simply administer a self cert competant persons scheme for us when we install boilers, but this is separate to their main function and the reason they were set up - which is to administer registration of people competent to WORK on gas under Gas Regs.
 
Last edited by a moderator:
As promised please find info below (sorry but can't remember who did all the hard work & should take the credit)
Right, time to put this one to bed once and for all...

I spoke to a Building Control officer at the local council and they advised me for a definite answer I need to speak to the Department for Communities and Local Government.

I emailed the following to someone at Department for Communities and Local Government who was there to give advice on Part L.

I have a question regarding Part L & Domestic Building Services Guide.

If a boiler is being replaced (like for like i.e natural gas fuelled for natural gas fuelled, in England) in a domestic dwelling what are the requirements for zoning the central heating system?

Is it right that if the boiler is being replaced that the central heating needs to be separated into two different zones (1 zone upstairs & 1 zone downstairs).

Thank you,

(not the whole email but you get the drift...)

I then received a reply (this is not the full email...) from them stating;


When simply replacing a boiler, there is no requirement to upgrade the whole heating system to meet current standards. In general it is only the component being replaced that needs to comply.

It is only heating systems in new dwellings and complete new heating systems (including pipework) in existing dwellings that should be provided with two heating zones - and then only if cost-effective. For example, there could be one room thermostat upstairs and one downstairs, or one could be in a lounge and the other in a home office.

There is further information in the Domestic Building Services Compliance Guide at www.planningportal.gov.uk/uploads/br/domestic_building_compliance_guide_2010.pdf - see for example Supplementary Information on page 24.

I hope this is helpful.

Best regards

So finally I have an answer. No zones needed on a boiler change... and only need to put zones in a new heating system if cost effective.

So basically no need to zone off new system either really (unless greater than 150m2).

I find it surprising that no one had a definite answer everyone kind of guessing (it is complicated I know).

Now I'm sure some people will be sitting there thinking "I knew that anyway" well - I didn't.

Thank you for your time and interest!

Read more: http://www.ukplumbersforums.co.uk/c...-new-replacement-systems-4.html#ixzz26GdUePV9
 
As promised please find info below (sorry but can't remember who did all the hard work & should take the credit)
Right, time to put this one to bed once and for all...

I spoke to a Building Control officer at the local council and they advised me for a definite answer I need to speak to the Department for Communities and Local Government.

I emailed the following to someone at Department for Communities and Local Government who was there to give advice on Part L.

I have a question regarding Part L & Domestic Building Services Guide.

If a boiler is being replaced (like for like i.e natural gas fuelled for natural gas fuelled, in England) in a domestic dwelling what are the requirements for zoning the central heating system?

Is it right that if the boiler is being replaced that the central heating needs to be separated into two different zones (1 zone upstairs & 1 zone downstairs).

Thank you,

(not the whole email but you get the drift...)

I then received a reply (this is not the full email...) from them stating;


When simply replacing a boiler, there is no requirement to upgrade the whole heating system to meet current standards. In general it is only the component being replaced that needs to comply.

It is only heating systems in new dwellings and complete new heating systems (including pipework) in existing dwellings that should be provided with two heating zones - and then only if cost-effective. For example, there could be one room thermostat upstairs and one downstairs, or one could be in a lounge and the other in a home office.

There is further information in the Domestic Building Services Compliance Guide at www.planningportal.gov.uk/uploads/br/domestic_building_compliance_guide_2010.pdf - see for example Supplementary Information on page 24.

I hope this is helpful.

Best regards

So finally I have an answer. No zones needed on a boiler change... and only need to put zones in a new heating system if cost effective.

So basically no need to zone off new system either really (unless greater than 150m2).

I find it surprising that no one had a definite answer everyone kind of guessing (it is complicated I know).

Now I'm sure some people will be sitting there thinking "I knew that anyway" well - I didn't.

Thank you for your time and interest!

Read more: http://www.ukplumbersforums.co.uk/c...-new-replacement-systems-4.html#ixzz26GdUePV9


That's pretty much what I was taught and have always followed.

Single component change, no requirement to comply, Significant change/upgrade to system, must comply. However, if custard refuses to pay for upgrades to ensure compliance, then record the fact that I recommended it, and take their money with impunity.
 
Any body that will sell themselves just for money really needs to take a long hard look at their life in my opinion !
I could live in my van and survive on next to nothing before I sell myself and my beliefs !

I know I couldn't live in my van, no thanks.

I would sell myself and beliefs to keep a roof over my family and some.
 
Last edited by a moderator:
That's pretty much what I was taught and have always followed.

Single component change, no requirement to comply, Significant change/upgrade to system, must comply. However, if custard refuses to pay for upgrades to ensure compliance, then record the fact that I recommended it, and take their money with impunity.

It is this bit that is a bit grey (gray? I never know which)
Replace boiler you must put in TVRS and stat - they used to be optional then became complusory 2010 BR.
Reg has posted many times a link that shows the installer must comply with BR or face heafty fine.
I asked GSR technical line and they also said it is not optional to comply.
It is NOT customer choice.
BUT
of course many other installers don't comply - offer a far cheaper job and we lose work to them.

It's not fair! STamps feet!
 
It is this bit that is a bit grey (gray? I never know which)
Replace boiler you must put in TVRS and stat - they used to be optional then became complusory 2010 BR.
Reg has posted many times a link that shows the installer must comply with BR or face heafty fine.
I asked GSR technical line and they also said it is not optional to comply.
It is NOT customer choice.
BUT
of course many other installers don't comply - offer a far cheaper job and we lose work to them.

It's not fair! STamps feet!

Really?!

I was under the impression - seriously - that you cannot force someone to upgrade to comply with Building Regs.

Have you got a link to the relevant regs please?
 
I think Chris is right, partly because he is ALWAYS right!
There are a number of old threads on this.
AND i remember asking the very same question about 2 years ago - asking where the answer was in official black and white.
I'm sure Chris will come back on this and I will also try to dig up the reference.
Thank you kind lady but sadly can confirm that I am most certainly NOT always right.
& A Big Thank you to "rodders" who did all the leg work (emailing) to find the info in the first place, that I have just re-posted.

There seems to be a lot of so called professionals on here who need any excuse not to do what is required (by the Law) & justify their actions with "well if I don't someone else will" & then "I will loose the work". We call this "the race to the bottom" & it is an easy one to win!!!! It will result in plumbing professional sleeping around & sometimes in their vans LOL. There is always someone who will do it for less than you, look at the domestic house bathroom scene, people are working for nothing to gain NVQ, compete with that!!
We need to maintain professional standard & it is the responsibility of us all, of course it would be a lot easier to do this if we had an effective policeman & some prosecutions to remind all of what the Law requires.
 
Last edited:
Thank you kind lady but sadly can confirm that I am most certainly NOT always right.
& A Big Thank you to "rodders" who did all the leg work (emailing) to find the info in the first place, that I have just re-posted.

There seems to be a lot of so called professionals on here who need any excuse not to do what is required & justify their actions with "well if I don't someone else will" & then I will loss the work. We call this "the race to the bottom" & it is an easy one to win!!!! It will result in plumbing professional sleeping around & sometimes in their vans LOL. There is always someone who will do it for less than you, look at the house bathroom scene people are working for nothing to gain NVQ, compete with that!!
We need to maintain professional standard & it is the responsibility of us all, of course it would be a lot easier to do this if we had an effective policeman & some prosecutions to remind all of the Law.
You normally know within a few minutes of meeting a client what type of job they are looking for and many times I have listened politely but already knew there was not a hope I want to do their work !
Am not saying I was the best but have always wanted to try my best, how some can sleep at night I really do wonder. I learnt early on it is not just about money and all this nonsense about keeping a roof over your head we are not in a third world country but we have somehow lost our way and put money in front of all else !
 
Really?!

I was under the impression - seriously - that you cannot force someone to upgrade to comply with Building Regs.

Have you got a link to the relevant regs please?

Using same principle would u upon custards request use 39 year old flue liner or connect a new boiler to an old flue and just record it as ncs? Yeh carry on plumbing.
 
Using same principle would u upon custards request use 39 year old flue liner or connect a new boiler to an old flue and just record it as ncs? Yeh carry on plumbing.

No of course not and that's a very silly analogy to draw. You're better than that. Anything that risks life and health is a no no. Energy efficiency or lack thereof is not going to kill anybody.

In any case I didn't say I disagreed with doing a proper job, far from it. I said that I thought, and was taught, that enforcement did not extend to forcibly imposing Part L Regs on people.
 
No of course not and that's a very silly analogy to draw. You're better than that. Anything that risks life and health is a no no. Energy efficiency or lack thereof is not going to kill anybody.
Or it might kill us all, with the predicted sea rises & climatic changes Masood, just hope I go before.
 
i think a customers ability to pay should be a factor when work is decided upon. If you had an old dear who's boiler went down in the middle of winter and only had a very limited budget then i would fit what she can afford.
 
Status
Not open for further replies.

Similar plumbing topics

I need someone to replace my boiler, I am...
Replies
0
Views
480
There must be many installations that are in...
Replies
7
Views
921
    • Like
Great summary and well done for getting it...
Replies
1
Views
2K
  • Question
Many thanks for the reply @Timmy D thats a...
Replies
5
Views
906
Back
Top