tamz
It was never allowed to be installed like that.
This is what it says in the BS
Where two or more vertical fanned draught chimney configurations
terminate in close proximity at the same height, they shall be separated
by at least 300 mm. Where any one vertical outlet is more than 300 mm
above the other, then they shall be separated by at least 1 500 mm.
Where any vertical fanned draught chimney configuration outlets is
within 2 000 mm measured horizontally of an opening window, then it
shall be at least 300 mm above the opening.
This is what it says in the BS
Where two or more vertical fanned draught chimney configurations
terminate in close proximity at the same height, they shall be separated
by at least 300 mm. Where any one vertical outlet is more than 300 mm
above the other, then they shall be separated by at least 1 500 mm.
Where any vertical fanned draught chimney configuration outlets is
within 2 000 mm measured horizontally of an opening window, then it
shall be at least 300 mm above the opening.