Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Where oh where is this air coming from? in the Air Sourced Heat Pumps area at Plumbers Forums

Status
Not open for further replies.

Ric2013

Plumbers Arms member
Plumber
Messages
3,916
Solutions
1
Help please.

My heating system at home is hardly an urgent issue. That said, I've had to admit defeat on how on earth air is getting in! Any ideas welcome.

The original pipework on this system was a bit messy and there were some redundant runs, but basically sound as far as I can see. There were points where the flow from the boiler to the vent dropped below horizontal, but I think I have got rid of these. Air has been a problem for some time, and a year ago I removed some of the bad and obsolete pipework and re-plumbed it in a more rational way. This has helped to some degree.

There is no evidence of leakage on the system that I have seen.

The boiler is 25' horizontal distance from the close coupled vent arrangement. System is a Y plan with heat only boiler on ground floor, horizontal(ish) primary runs in first floor void to close coupled vent arrangement and 3 port valve in airing cupboard on first floor. The heating and DHW returns merge just before the Magnaclean, and I have fitted the Magnaclean above this confluence so that the Magnaclean is accessible and so it acts as the highest point on the return (doubling as an air vent point).

Boiler (Potterton Netaheat Profile 40e) kettles badly, and probably needs descaling. Every time I run the boiler, there is air in the Magnaclean which I bleed out. There is air in the Magnaclean even if I leave the system to cool before bleeding the air, so that rules out it being steam. The air does not appear to be hydrogen. The air is only present if the system has been run. System was refilled with fresh inhibitor 3 months ago (after trying out the efficacy of MC3 cleaner) and has been bled several times a week since, so this surely must be new air, not residual from filling! Quantity is probably about a teaspoon of air for every time I heat the cylinder up.

I'm clutching at straws now. Could the possible bubbles of steam passing the vent be somehow dragging in air? Could they be dragging in air through a micro-weep somewhere hidden? Could the boiler heat exchanger be letting in air somehow if a seal is defective? Could the compression unions on the boiler tails be letting in air?

I spend £300 a year on gas, so the idea of buying a new efficient boiler and replumbing the entire system has limited appeal. I'm not so much worried about curing the problem as understanding what is wrong... but curing the problem would be nice.

Thank you if you are still reading :)

Ric

DSCI0017.JPG


DSCI0020.JPG


DSCI0021.JPG
 
Last edited:
I found the original Fernox back in the day to be exellent on open vented systems, often with little corrosion present after many years. But the modern Fernox seems different.
What puzzles me is the 4 litre Fernox is not the same as the concentrate.
 
I found the original Fernox back in the day to be exellent on open vented systems, often with little corrosion present after many years. But the modern Fernox seems different.
What puzzles me is the 4 litre Fernox is not the same as the concentrate.

Watering it down mate
 
I recently tried the 'nail through a piece of pipe in a small jar of water' test[...].

I assume that's to test the effect of dissimilar metals too?

I must say I took a water sample from a customer's system recently, having drained to add a new radiator, and did the plain nail in a jar test, just using the system water undiluted and, in spite of 2l Sentinel to 13 radiators, the nails, in 10 days, are not quite as bright as when new.

But better than whatever inhibitor the RGI had used two months prior, His let the nail go a dark orange and pitted in three weeks and seemed to encourage slime to grow in the F&E (which I had thoroughly cleaned prior to his installation). I was trying to show the customer what inhibitor did, but it didn't really work as a demonstration. When refilling, I asked the RGI which inhibitor he had used so I could refill with the same and he said, 'Oh, "Range" boilers don't mind. Just use any good-quality inhibitor.' I took this as an evasion, and let it slide.
 
I assume that's to test the effect of dissimilar metals too?

It's to model the Galvanic corrosion that occurs in heating systems. I suppose one should include some aluminium in the mix these days but this was the quick and dirty test the scientists that developed Fernox used to decide which formulations were worth investigating further.

To demonstrate the effect of the protector, you need to use a second pot with tap water as a control. With a nail through 10mm of 15mm Cu tube there'll be a noticeable amount of rust after 24 hours.

The RGI should have specified the inhibitor used on the Benchmark statement for the boiler. If you've drained and refilled with something else don't forget to update the docs and any labels on the system.
 
The RGI should have specified the inhibitor used on the Benchmark statement for the boiler. If you've drained and refilled with something else don't forget to update the docs and any labels on the system.

Yes, he wrote '1l'. No mention of the brand. And he left the lid and the lagging off the F&E. I wasn't impressed, especially since I was the one that got him the contract to fit that boiler in the first place. I left the Benchmark as he had left it, stuck a Sentinel label on the boiler casing, and wrote '2 litres' on the label.

Did you observe how much the height of the level in the expansion tank rose and fell between the system being cold and the system being hot?

I've had a go today at checking the water level in the F&E. It rises from 5.5" to 5.6" over a 17 x 11.5" tank. I make this 0.56pt, or 318ml, compared with 358ml in the cold feed run, if we assume the pipe contains 130ml/m.

The pipe run from the close-coupled tee to the tank is about 1.25m vertical and then 1.5m across the loft joists, giving a total of 2.75m.

So, while the expansion is not quite as great as the quantity in the cold feed, it isn't far off, and I can see that air could potentially get into the system this way, particularly when central heating is warming up a far greater quantity of water than the small amount in the primaries, boiler, and cylinder coil.
 
Last edited:
The noise is tiny bubbles of steam being created in hot crevices at the HX surface, moving out into the relatively cool bulk water in the HX and then collapsing as the steam condenses.

This is how I've always had kettling explained to me. However, in the case of my system, you hear air/steam bubbles running the full length of the primaries. Sometimes they even are enough to be dragged back into the pump. Can steam possibly remain as steam for this distance? It's 25' (8m) horizontal in 22mm...
 
This is how I've always had kettling explained to me. However, in the case of my system, you hear air/steam bubbles running the full length of the primaries. Sometimes they even are enough to be dragged back into the pump. Can steam possibly remain as steam for this distance? It's 25' (8m) horizontal in 22mm...

They can't be steam, unless your flow temperature is above 100°C, which I assume you would have mentioned if it were the case. The boiler is one place where dissolved air is likely to come out of solution because that's where it's heated. The pump is another because that's where there'll be turbulance and cavitation.

From your description of the noise, however, I suspect the long horizontal run may have a slight downhill gradient and be partially air locked as a result. Imagine the pipe half full of air. Is this possible? If so it could take a very long time to bleed all the air out of a few ml at a time.
 
The horizontal run used to dive down under the airing cupboard just before the pump arrangement, thus airlocking much of the run. I changed that, but, yes, there may be other problem areas.

What I don't understand is, if it isn't steam, why does this air running noise not happen at all until the boiler starts to kettle?
 
Yes, he wrote '1l'. No mention of the brand. And he left the lid and the lagging off the F&E. I wasn't impressed, especially since I was the one that got him the contract to fit that boiler in the first place. I left the Benchmark as he had left it, stuck a Sentinel label on the boiler casing, and wrote '2 litres' on the label.

At least that's sorted now.

So, while the expansion is not quite as great as the quantity in the cold feed, it isn't far off, and I can see that air could potentially get into the system this way, particularly when central heating is warming up a far greater quantity of water than the small amount in the primaries, boiler, and cylinder coil.

It's not impossible, but I'm not convinced that with this mechanism is getting enough transfer of aerated water down into the system to explain the amount of air that you are getting out.

The 1.25 m head is lower than I'd guessed. (You might like to check the pump is okay with an inlet pressure this low.)

Has the system always needed air bleeding from it, or did it only start after you drained it for some reason? (I'm thinking that there may be a partial airlock acting as a reservoir of air.)
 
The system saw a lot of fills and drain last year, so I can't be certain, but in general, the radiators have not been quick to fill with air. They probably get bled each autumn: I lose track.

What used to happen (long-term issue) is that the air would run around the system, get caught under the airing cupboard where there was a pass-under on the flow under another pipe and then every now and then there would be a GLUG sound and then a load of air would get to the H arrangement. Most would go up the vent, but some would get into the pump which would then make an airy sound.

My response was to re-design all the pipework in the 12x10 landing-room, remove several radiators (who needs a radiator in a draughty porch or in a loft?), remove a run that ran all the way around the landing for no apparent reason before going to a bedroom radiator, add a radiator in a drying cupboard, drop the pump a few inches to see if that helped, replace the lounge radiators with underfloor heating (on the same zone as everything else but done for technical and practical reasons), design the return to ensure reverse circulation was impossible, and put a Magnaclean on the highest point of the return to act as an air-vent point, and as a filter.

The GLUG sound no longer happens and the air seems to be finding its way into the vent. It is no longer usual for the pump to get air in it. Everything seems to be working as it should. The only exception is the running air sound and this small quantity in the Magnaclean (only with a hot system).

Even if the pump were able to cavitate as the water temperature increased, as you say, the resultant steam could not survive for long. Though, at 75°C, it should be okay at a 0.5m head inlet pressure, according to Grundfos data, the only risk being cavitation.
 
Last edited:
Thanks to all those who commented and for the advice given. Considering that this system has been problematic for at least the last 10 years, and my various modifications have improved the various failings without yet solving this air problem completely, I knew it was never going to be easy.

I think Shaun's suggestion, to seal the system, might solve a lot of problems (or find the leaks!) but otherwise it remains a head-scratcher as I've tried to check if the vent was drawing air as suggested and it seems not to, and I've tried to see if this is only air coming out of solution and we think it mostly isn't. I will try the air separator though.

If everyone is agreed that kettled steam CANNOT survive long in water at 75°C, then the gasses running up and down must be air and are is probably getting in at a joint near the boiler, or from the boiler H Ex itself (I hope not).

If no one has any further suggestions, I'll try to update this thread when I get around to the next stage in investigations.

Thanks again.
 
Honestly one of the most interesting threads I have read! Next time I come home from work and tell the Mrs I feel knackered & she replies "work is easier than having the kids"I will show her this thread good luck mate would be interested to how you get on
 
Just an update. The system seems still to have some air, though not quite as much. Interestingly, since the boiler is running (on and off) for central heating for most of the day, but only fires for DHW in the morning, the problem seems less severe than when it was firing for DHW only.

From this, it seems reasonable to speculate that this is another nail in the coffin of the idea that the problem could be due to air being absorbed into the F&E water and then coming in via the feed pipe, as the volume of water in 3 radiators and the UFH is much higher than just in the cylinder coil. If the problem were air absorbed via the F&E, I would expect it to be worse during the CH season?
 
It could be pulling in air on the vacuum side of the circulating pump, past the washer. I had one like that a few years ago where I found the most minute of weeps on the pump valve. It had fibre washers and I changed them to rubber and the air ingress problem went away.

Just an idea!
 
It could be pulling in air on the vacuum side of the circulating pump, past the washer. I had one like that a few years ago where I found the most minute of weeps on the pump valve. It had fibre washers and I changed them to rubber and the air ingress problem went away.

Just an idea!
That would be the logical explanation - only part of the system that is under vacuum.
 
That would be the logical explanation - only part of the system that is under vacuum.

I have been able to replicate this fault for the college apprentices I support. I used clear hoses and rigged them up to a circulating pump. I then scratched a fibre washer with my pocket knife and installed it on the vacuum side of the pump. We could see a steady stream of minute bubbles being pulled into the hose.
 
Silly thoughts is there still some contaminant / or chemical reaction thats only happening somewhere with high temperature ?
( Still like sound of small surge caused / intermittent temp dependant vacuum leak ..somewhere )
 
Hi, thanks Stigster. It was a rubber washer but wasn't all that tight. Took it out, and put it back after a clean and a smear of "Hylomar". Will report back in a few days.

zzz - I don't follow what you mean in your comments in brackets. Can you elaborate please?
 
Sorry if anyone has already said this but there seems to be no bypass after the pump? Pump shouldnt be set on 3. Boiler stat shutting on and off correctly?? If you shut heating off can you hear motorized valve shutting down...no air heard by pump and vent/coldfeed??
 
.... I don't follow what you mean in your comments in brackets....
a) May happen at pump surge start-up
b) Be a slow steady process during certain conditions.
A vacuum is forming and drawing air occasionally, would have to be at a point of lower pressure / or speed change (size changes) .. like some-one elses scratched fibre washer -demo . A minuscule leak that may depend on expansion / contraction
 
Sorry if anyone has already said this but there seems to be no bypass after the pump? Pump shouldnt be set on 3. Boiler stat shutting on and off correctly?? If you shut heating off can you hear motorized valve shutting down...no air heard by pump and vent/coldfeed??
At present there is no official bypass, but the boiler can only fire when the UFH is running - the radiators come on at the same time (no separate zone as such: 'wrong', I know). Before there was UFH, the room served by the UFH has rads on manual valves and the air situation was no better. Y plan, so always somewhere for pump over-run to go.

Pump is on proportional pressure curve 3, not speed 3. The 3 pp curves are not that different each from the other.

Boiler cycles correctly, albeit with quite a high hysterisis. I think the gas rate is too high (but not by much), but last RGI to work here refused to set it down for me on the grounds that it would most likely cause the diaphragm in the gas valve to fail for not much gain.

Y plan, so motorised valve stays in CH mode until call for DHW.

After I removed the pump, air could be heard travelling up the vent. In normal use, with boiler kettling, you do hear the occasional bubble running up the vent, and sometimes a bubble manages to get pulled into the pump.
 
Last edited:
a) May happen at pump surge start-up
b) Be a slow steady process during certain conditions.
A vacuum is forming and drawing air occasionally, would have to be at a point of lower pressure / or speed change (size changes) .. like some-one elses scratched fibre washer -demo . A minuscule leak that may depend on expansion / contraction
I think we can rule out pump surge on start up to be the problem as the air seems to be only when there is heat/ boiler kettling UNLESS there is a miniscule leak that develops when the system is hot. (Also I would rule it out due to having semi plugged the vent in earlier experiment (see above) and confirm it would not appear to be sucking in air).
I'm wondering whether the steam bubbles collapsing in the flow could be causing a vacuum where the boiler is connected up with compression fittings, or if the boiler heat exchanger itself could have a miniscule leak with the same effect? Potterton (Netaheat) Profile 40e...
 
Last edited:
Status
Not open for further replies.

Similar plumbing topics

  • Question
It could well be, the OP will soon hopefully...
2
Replies
35
Views
2K
  • Question
Thanks very much for all the advice John, it's...
Replies
13
Views
903
  • Question
But they don’t drain the system so can still...
Replies
3
Views
326
  • Question
Hi Ric - thanks you so much for taking time to...
Replies
4
Views
1K
  • Question
You’re a genius, thank you! Held my thumb over...
Replies
2
Views
886
Back
Top