Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Woscester 30cdi Greenstar system boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
M

matthew20

Hi I have a Worcester bosch 30cdi greenstar system boiler when i turn the heating on the flow pipe becomes hot the flame light is on ,flue fan on , pump running after about 5mins the flame led turns off and the pump stops, have tried the reset button
 
hi, sounds like the boiler is over heating, does your hot water work ok?
 
Have you got enough pressure in the boiler should be set about 1 - 1.5 bar
 
it did loose about 0.2bar and while it was working about a week ago it was discharging water through the pressure relief
 
If you are regulary refiling the system, It could be a faulty pressure relief valve, or a faulty expansion vessel, or the expansion vessel needs recharging.
 
Last edited:
i only topped it up once and twisted the valve which stopped it discharging
 
No pressure remains constant flame led turns off U6 is displayed on led screen
 
have checked the pump it is not jammed or sticking but there is power going to it and its not running (only runs for about 5mins when boiler starts)
 
Could be a motorised valve faulty, not sure what the U6 code means, when hot water is on do you get the same fault code
 
Very strange it has now started to work again is there sensors on the flow and return pipes ?
Does the display on the from indicate the temp of the flow ?
 
if it has started to work again, it does sound like a overheat problem, see if the boiler runs with heating and hot water on, make sure the hot water tank is cold. If the boiler continues to works but the radiators are not heating up, it is very possible that the motorised is stuck on hot water, therefore when the demand for heating is on, the boiler will over heat as there is no where for the water to go.
 
CDi's display U when its over 99 degrees. U1 U2 U3 etc. Defo overheating. Not circulating for some reason mate
 
Status
Not open for further replies.

Similar plumbing topics

Or elec bills as it would be running...
Replies
9
Views
598
J
In a simular situation to yourself, partners...
Replies
2
Views
855
I understand, thanks for letting me know.
Replies
4
Views
464
I’m guessing the installer didn’t have a...
Replies
3
Views
437
thanks.... yes, so my diagram and wording is...
2 3
Replies
55
Views
2K
Back
Top