Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss W-plan pump run on in the Boilers area at Plumbers Forums

You sure your drawing is correct 100% as your boiler requires a perm live and a switch live ?

You sure the red wires arnt perm lives ?
 
I THINK I have re-drawn it correctly "as-is".....without programmer connections etc.

IF correct I agree there's no way the diverter can be operating....
how about IF any of the cyl stat connections are reversed.....
appreciate thats a lot of IF's but I havent been able to get over there yet

View attachment 94764

That looks correct to me, when you do get there suggest turning both roomstat and cylinderstat to a high setting, when pipe B? to the cylinder coil gets hot about a foot from the diverter valve (and pipe A remains cold, turn roomstat to a low setting (no call) then turn down the cylinderstat, check that pipe A remains cold during boiler overrun.
 
Easy way to fix the issue is to get a battery prog room stat eg eph cp4b then move the cylinder satisfied wire and pair it with the prog room stat live and diverter switch eg brown

And then marry up all the switch wires eg boiler switch, pump live, cylinder stat call and prog room stat switch live
 
ah....apologies for not clarifying... the roomstat we have IS a battery powered one

Easy switch over then just moving some wires etc
 
....which, surely is the setup I have as in #25 ???

No as your drawing there’s no connection between the room stat and the boiler unless you’ve miss labelled the pump as the boiler switch live ?

I suspect you’ve got your perm and switch lives mixed up

Eg yellow going to the boiler perm live to the wirings centre and the red coming from the boiler / pump switch live etc
 
OK, so I missed out the fused spur supply...... maybe this is how it SHOULD be...... Screenshot 2024-07-31 150122.jpg
 

Attachments

  • Screenshot 2024-07-31 150122.jpg
    Screenshot 2024-07-31 150122.jpg
    121.4 KB · Views: 16
Just a quick look but roomstat & cylinder stats are switching the boiler live , they should be switching a SL on the boiler & the boiler should have a permanet Live to allow it to request/do a pump overrun when both the HW & the room stats are both satisfied?.
 
Not sure this is the exact correct model, but likely similar
Mains from the FCU connects to the boiler at one block.
There is a separate connection block to accommodate a live (out) supply to eg thermostat , a switched live (in) from eg thermostat, a neutral etc etc as below simple example.

Ls is live supply (out). Lr is switched live (control in)

So the Boiler L in the diagram above (post #34 yellow and grey wires) should actually be Lr in the boiler. Hopefully it is like that already.

IMG_0672.jpeg
 
Last edited:
right.....having gone through all the connections it appears that on the cylinder stat, C & 1 were reversed....the stat is actually marked 1,2,3 rather that C,1,2 which might explain it
I have corrected this and re-drawn the actual installation as it is, I also fitted a new Drayton home battery operated programmable thermostat just to eliminate that
When I tried it yesterday it all seemed OK but was later advised that after the water had been on the rads were still getting hot at the top - suggesting a short run rather than being on all the time
The diverter valve is new and moves and seals OK
1.jpg




2.jpg
 
Last edited:
As far as I can see, the only difference the reversal of C and 1 would make, is that the diverter valve would be permanently powered once the cylinder stat is satisfied, irrespective of whether timer is on or off.
Having corrected the C/1 swap, the diverter is no longer powered once the timer is off.
So I hope residual boiler heat won't now be continually pumped around the rads as before, but it seems there's still something of that effect?

Well done for finding that wiring feature!
 
yes....but if the diverter valve IS / WAS being held open that would explain the residual heat around the rads whilst the pump was over-running......it is only a small house with small rads
I will do another check in case I have missed something but, with it operating as it should, there's no way the residual heat CAN circulate around the rads is there.......unless the pump pressure is keeping the valve open but that is unlikely
"feature" indeed :rolleyes:
 
yes....but if the diverter valve IS / WAS being held open that would explain the residual heat around the rads whilst the pump was over-running......it is only a small house with small rads
Yes absolutely!
I will do another check in case I have missed something but, with it operating as it should, there's no way the residual heat CAN circulate around the rads is there.......unless the pump pressure is keeping the valve open but that is unlikely
"feature" indeed :rolleyes:
I don't think you've missed anything! Now the diverter should return to hot water position when the programmer/thermostat are off, so hopefully no spurious heating any longer 🏅.
I was just slightly surprised by the report that rads were still getting hot at the top after water heating, as the diverter surely shouldn't operate if heating isn't called for 🤔
 
So was I 😅......it is possible that I have mis-wired it again as even I got confused with the C/1/2 and 1/2/3 labelling and have also swapped the colours around to try and simplify (!!!!) things
 
So was I 😅......it is possible that I have mis-wired it again as even I got confused with the C/1/2 and 1/2/3 labelling and have also swapped the colours around to try and simplify (!!!!) things
What is the cylinder stat exact make and model?.

Did you do the basic test of feeling pipe A (should be cold/cool) when HW calling and boiler firing and should remain cold/cool on pump overrun.
 
not sure of exact make but it had the terminals marked 1-2-3 .... looks identical to this one (attached)
....yes, at least whilst the HW was on the pipe seemed to remain cool
will check again when I can get over there....again :rolleyes:
 

Attachments

  • cyl stat.pdf
    951.8 KB · Views: 19
I wondered about that...... but I think the printed version is correct....
so C & 1 are connected when it is calling for heat i.e. when the water temp is lower than the set point
when it is satisfied contacts C & 2 will connect as per my diagrams
...it all depends on what they are calling normal.... in my opinion, normal is whan everything is satisfied co normally open would be C & 1
 
Last edited:
I wondered about that...... but I think the printed version is correct....
so C & 1 are connected when it is calling for heat i.e. when the water temp is lower than the set point
Looks that way to me, so, in the installed stat. 1&2, (where 1 is "C" & 2 is "1") are made when the water temp is < the SP, I would turn up the stat fully and check for continuity between 1&2.
when it is satisfied contacts C & 2 will connect as per my diagrams
...it all depends on what they are calling normal.... in my opinion, normal is whan everything is satisfied co normally open would be C & 1
then turn the stat fully down and check for continuity between 1&3.

Also check that pipe A remains cold on the pump overrun, if so, the only other explaination I can think of is some form of reverse circulation.
 
Apologies again for the delay in response.......I have been pretty much laid up for 8 weeks with sciatic pain :rolleyes: but its finally easing.....

I have just re-checked EVERYTHING
The system IS wired as per my latest diagram in post #38
The cylinder stat operates correctly with continuity between C & 1 calling and C & 2 satisfied
The connector block wiring is all correct as per diagram
The diverter valve doesnt seem to be leaking or bleeding to the rads circuit in its' closed / normal position, it ONLY moves when the roomstat is calling for heat and returns to normal position when the roomstat is satisfied
The pipe from the diverter to the rads ONLY gets hot when it should
The pump overruns for approx 5 minutes during which time, with the roomstat satisfied, no heat (correctly) goes through the rads
With the HW satisfied and the roomstat calling, all the heat goes to the rads
With the roomstat calling, if I turn up the HW stat to calling the diverter valve closes and diverts all the heat to the HW
With the roomstat calling, if I turn it down to satisfied the diverter valve closes to its normal position (HW)

So, as far as I can see it is all physically, mechanically and electrically correct and functioning as it should......time, as they say will tell
 
Last edited:
Post #38 shows wire blue to C, brown to 1 and black to 2 (on the stat) but your stat is numbered 1,2&3? so what colour wires go to these numbers?.
 

Similar plumbing topics

  • Question
Its a very ingenious but devilishly cunning...
2
Replies
25
Views
3K
John Thank you for all your help, changed the...
Replies
13
Views
2K
One thing I might add. We too are in a similar...
Replies
2
Views
1K
Hi It seems like i have exatly same problem -...
Replies
2
Views
1K
Replies
0
Views
444
Back
Top