Y plan rads heating up when hot water on | Bathroom Advice | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Y plan rads heating up when hot water on in the Bathroom Advice area at Plumbers Forums

Subby

Plumbers Arms member
Plumber
Gas Engineer
Messages
445
Hi all. I have a problem with the rads heating up when there is call for hot water only on a small 5 radiator y plan system with regular boiler, grundfos alpha 2l pump , nest 3rd gen stat and drayton 3 port.
When the thermostat calls for heat the valve switches over, boiler fires and pump runs, the rads start to heat up a little , it does not appear that the 3 port valve is passing as the heating pipe at the valve stays cool. Is there some other way that heat could be leaking to the rads? The rads are piped up with 10mm.
 
Thanks I think his problem is zone valve passing, my problem appears to be "reverse circulation" as the cylinder return is not the last tee before the boiler.
I am trying to get my head around this reverse circulation.
Am I right in thinking if the cylinder return is not the last tee, then hot water flows through the coil, down the cylinder return, then through the return of a radiator further down the line out through the flow and then around the other rads through the flow pipes, out the returns back to the boiler . Is this what is happening?
Why does this only happen if the cylinder return is not the last tee?
As a side note, Are bi directional trvs a bad idea on this type of system as they allow the water to flow backwards through the radiator?
Just trying to make sense of it
 
If you are confident the valve is working as it should you could try fitting a non return valve just after the return connection from the cylinder where it tees back in the common return back to the boiler , this would stop heat creeping down the return pipework and warming the radiators when the hotwater is heating cheers kop
 

Similar plumbing topics

Sometimes the connection point of the cylinder...
Replies
3
Views
549
thanks.... yes, so my diagram and wording is...
2 3
Replies
55
Views
2K
Looks that way, a multimeter would tell alot...
Replies
8
Views
862
John Thank you for all your help, changed the...
Replies
13
Views
2K
    • Like
I'm inclined to adopt the occam's razor...
2
Replies
34
Views
7K
Back
Top