Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Zoned central heating problem in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
dont ideals come with built in by-passes? If valves are on returns are they the right way>?
 
Hi Fred I've never put them on the return if they are on the return what's to stop the heat on the flow going where it wants Evan with one return it only creeps up getting the nearest rad warm you must have linked them somewhere is a new build might have put a downstairs rad in upstairs loop or other way round easy mistake to do
 
Hi Fred I've never put them on the return if they are on the return what's to stop the heat on the flow going where it wants Evan with one return it only creeps up getting the nearest rad warm you must have linked them somewhere is a new build might have put a downstairs rad in upstairs loop or other way round easy mistake to do

Rob,


I agree, you need to put the barrier on the hottest pipe work which is the flow, hells-bells Fred this is 50 posts now you should be able to fit a heating system yourself, albeit push fit plastic. When your plumber comes around, show him the posts here, there are some little nuggets of information.

Tony
 
Hi Guys,

Just had my heating sorted after a short 4 months wait! just glad we've had a nice summer. Anyway just thought I would update you on what the issues were.

1st no by-pass circuit installed.
2nd zone valves on return instead of flow.
3rd 2 flow pipes fitted (1 to each zone) but only 1 return for both zones.

Pleased to say that the chap today knew what he was doing and has put it all right. Thanks for all your advice, looks like everyone on he was correct in one way or another.

cheers fellas
 
Hi Guys,

Just had my heating sorted after a short 4 months wait! just glad we've had a nice summer. Anyway just thought I would update you on what the issues were.

1st no by-pass circuit installed.
2nd zone valves on return instead of flow.
3rd 2 flow pipes fitted (1 to each zone) but only 1 return for both zones.

Pleased to say that the chap today knew what he was doing and has put it all right. Thanks for all your advice, looks like everyone on he was correct in one way or another.

cheers fellas

Nice to here you got some one in to put right
 
Status
Not open for further replies.

Similar plumbing topics

In the end decided to follow Chuck’s advice...
Replies
11
Views
679
Replies
0
Views
448
I have a home with an oil boiler in a garage...
Replies
0
Views
637
Sometimes the connection point of the cylinder...
Replies
3
Views
559
That's a fair better idea or costly mistakes...
Replies
5
Views
1K
Back
Top