Looks alright to me, your roughest job is always your own home anyway.
Also looks like the others are radiator by radiator, whereas it seems like only Honeywell and Danfoss allows you to combine radiators into rooms / zones..
DHW DCW labelled incorrectly as return shown as DCW. No back flow protection that I can see. Flue not pointed, gas pipework under supported and asking for damage. Drain off in a considerate location. No Aav??
LLH well supported with no Aav
Couldn't see where system water coming from?
Manifold looked ok? Was bypass facing right way? Drain off on primary side of LLH missing?
Around twin head looked messy. Frost control?
Gas sleeve not pointed or sealed, earth? Supply looks a bit narrow for 100kw?
Probably missed all sorts.
DHW DCW labelled incorrectly as return shown as DCW. No back flow protection that I can see. Flue not pointed, gas pipework under supported and asking for damage. Drain off in a considerate location. No Aav??
LLH well supported with no Aav
Couldn't see where system water coming from?
Manifold looked ok? Was bypass facing right way? Drain off on primary side of LLH missing?
Around twin head looked messy. Frost control?
Gas sleeve not pointed or sealed, earth? Supply looks a bit narrow for 100kw?
Probably missed all sorts.
All these extra controls are well and good, but will the custs want to pay the extra? I don't think so. Then there's the reliability which is carp on most of these wireless products.
Never dump by prv! The fkr never reseals, drain off at lowest point it's a.basic! Perhaps some lock Sheilds then? Or ones that require a hex key. But who's going in the plant room? Care taker? . No provision for balancing on returns either? Assume each cir is more than one emitter?
Blow it off and replace prv. ££££ though!
Ermi,
The process for replacing the air bubble in a Megaflow entails manually opening the PRV, it's a standard procedure that you may need to do twice a year,
they don't leak after, its good gear.
Tony
but that's half way up the cylinder and its not filled with sludge!!!
What do you size the rads on? If upstairs is off then the rads downstairs will be undersized taking into account the unheated space above, or the rads will be sized in that manner and be over sized when upstairs is heated?