While safety check/servicing a Glow-worm BBU today I discovered there was no fused spare to isolate the boiler. The customer was recording his favourite program, and requested I didn't switch off the electric, so I switched off the demand for heating and water at the programmer. I proceeded and took the risk. I checked the boiler with my voltstick and confirmed it was dead. I disconnected the gas connection at the 3 way gas tap and received a nasty elecrtic shock. After picking myself up from the recoil, I tested the boiler with my voltstick and the entire boiler was live!. Sod the tv program, I insisted on isolating the electric supply at the fusebox. Out of curiosity I reconnected the gas pipe, restored the electric supply and tested the boiler again...... No voltage, it was dead. Does this mean the equipotential bonding is not present some where? Needless to say the gas pipe is bonded at the meter having checked it during the TT. I continued the my work with the power off. I did notice that the 240v supply to the boiler had what appeared to be a connection taped with insulation tape. I intend writing a report about this to the letting agent. Can anyone throw some light on why the boiler was live with the gas bipe dosconnected and yet no breakers had tripped? I need some ammunition for my report. Thanks in advance