Nico

Gas Engineer
Messages
79
This may be a bit of a daft question but seem to be having issues with 4 Atag xl110 when running on low fire and believe there could be an issue with the flue but when check-in Mis I noticed it says flue gas outlets under pressured and flue gas outlets over pressured. What is the difference in these configurations? Cheers
 
are you commercial ?
 
whats the issue on low fire?
 
whats the issue on low fire?
The O2 percentage is meant to be between 5-7% there is 4 boilers back to back going onto a common flue header but when running on low fire the percentage was 12% when trying to adjust the offset on gas valve when I was getting to roughly 10% the CO ppm was flying through the roof. These are newly installed boilers but have used existing class 1 flue
 
What was the high fire stats
 
Have you tried firing one boiler at a time on low ?
 
How long are the flue and is there a secondary flue fan fitted ?
 
Is could I would find out the max flue run on the Atags should be in the manual and then go from there

If you can’t find it phone tech up there a good bunch but commercial only so need to know what your talking about
 

Similar plumbing topics

  • Question
Let them supply and fit , then it’s their...
Replies
3
Views
672
C
I’m not posting here to agree to do/looking...
Replies
1
Views
847
E
It sounds like that needs to be sealed from...
Replies
3
Views
1K
it already IS (and always has been) a W-plan...
2 3 4
Replies
77
Views
3K
I've been a heating engineer for over 15years...
Replies
5
Views
1K
Back
Top